Correct - the faulty system uses the older packaged NUT. The working setup in FreeBSD (actually XigmaNAS v12.3.0.4.9848) uses NUT v2021.12.09, which I am guessing is whatever they pulled from Github on that date.
Unfortunately, I can only verify that the faulty one (Linux) uses libusb-0.1 and cannot find anything on the libusb for the working FreeBSD. Looking at the changelog for NUT, it seems though that libusb-1.0 were not merged into main NUT codebase until 2022.01.12. So I would guess it is still on libusb-0.1.
I took a look at the parameters for usbhid-ups. It seems the most relevant ones would be pollreq, pollonly, interruptonly, interruptsize. Is the strategy here just trial and error since the error log is not showing anything? However, the config used between the two systems are identical so would it still be relevant?
________________________________
From: Jim Klimov <jimklimov+nut at gmail.com>
Sent: February 11, 2022 12:31 AM
To: Gary <digimon0327 at msn.com>
Cc: Arnaud Quette via Nut-upsuser <nut-upsuser at alioth-lists.debian.net>
Subject: Re: [Nut-upsuser] usbhid-ups becomes unresponsive after extended period
So just to clarify - the faulty system uses the older packaged NUT (in Linux) and the newer build of master (in FreeBSD) works better?
Does the newer one also use libusb-1.0 dependency (vs. 0.1 likely for packaged one), is the custom build that new? It may be that some transport deficiencies were fixed in that, or in NUT over the years.
For that older setup, probably there are some timeout settings to tell the driver to reconnect somehow, but can't remember ATM. Also different systems varied with success of active polling vs interrupt delivery, so "pollonly" (and freq) options can help.
On Wed, Feb 9, 2022, 03:56 Gary via Nut-upsuser <nut-upsuser at alioth-lists.debian.net<mailto:nut-upsuser at alioth-lists.debian.net>> wrote:
OS name and version: Ubuntu 20.04.3 LTS
NUT Version: 2.7.4 (installed via apt-get)
USB communication driver: 0.33
Subdriver: APC HID 0.96
Device: APC Back-UPS 550
The usbhid-ups driver seems to stop responding/serving data to upsd after running it for a few hours. It works initially when starting the NUT service but would stop working after a while. It would start working again for a bit if I restart it (sudo upsdrvctl start)
In my syslog, I would get these error messages once it stops working.
Feb  8 15:20:43 internal upsmon[25307]: UPS [ups1 at localhost]: connect failed: Connection failure: Connection timed out
Feb  8 15:20:43 internal upsmon[25307]: UPS ups1 at localhost is unavailable
Reading the log, the upshid-ups log stops updating after a while. For example, in this log, it would keep updating until 8282 seconds but nothing appears in the log afterwards. The command I use to capture the log is:
/usr/lib/nut/usbhid-ups -DDDDD -a ups1 > /var/log/usbhid_log 2>&1 &
Log file:
https://drive.google.com/file/d/11LwtnUoF7TweNDxMrIG8ZAxNTlzKwpy7/view?usp=sharing
The troubleshooting steps I have done include:
- Works without issue: Connecting to a different VM (but on same hardware, cable port, usb passthrough) running FreeBSD 12.3 and NUT 2.7.4.1
--- So it doesn't seem to be an issue with hardware, cable, or VM passthrough issue
The setup:
- APC Back-UPS connected via USB to USB port on machine, passthrough via ESXi to guest VM
Greatly appreciate any insights.
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser at alioth-lists.debian.net<mailto:Nut-upsuser at alioth-lists.debian.net>
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20220215/7033a420/attachment-0001.htm>
    
    
More information about the Nut-upsuser
mailing list