[Nut-upsuser] NUT constantly reporting switching to battery
    Brandon Wright 
    skydive340 at gmail.com
       
    Thu Jan 13 15:09:05 GMT 2022
    
    
  
Hello,
I have an odd issue that I am trying to sort through, and looking for some
advice to narrow it down. I recently inherited a couple UPSs, one of which
is a TrippLite SU3000RTXR3U, which I replaced all batteries in last year. I
have hooked it up to two different NUT installations with this same
trouble. Even though the UPs itself is not indicating switching to battery
at all, and no alarms are happening, the monitoring tool is constantly
reporting that it is on battery and the back to on line. This cause a flood
of email alerts and other notifications. Using the Tripp Lite PowerAlert
software, there is never any notification of the unit switching to battery,
and self test reports are all clear. Output load on the UPS is sitting
around 12%, so should not be an issue with having a load higher than it is
rated for.
I have tried with two different installations. One was through my TrueNAS
installation, version 12.0-U7. The other was Rapbian Linux 11 (bullseye).
My NUT version is 2.7.4.
TrueNAS NUT is installed as a service by default, on the Linux box it was
installed via apt-get package.
In the debug log from the driver, I see that during the polling, it is
randomly getting a value of 0 for
"UPS.PowerSummary.PresentStatus.ACPresent".
*ups.conf:*
poll interval = 1
maxretry = 3
[rackups]
        driver = usbhid-ups
        port = auto
        desc = "Tripp Lite SU3000RTXR3U"
        vendorid = 09ae
        productid = 4003
*# ./usbhid-ups -DD -a ups*
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
   0.000000 debug level is '2'
   0.000512 upsdrv_initups...
   0.000880 Checking device (09AE/4003) (/dev/usb//dev/ugen0.4)
   0.295477 - VendorID: 09ae
   0.295511 - ProductID: 4003
   0.295517 - Manufacturer: Tripp Lite
   0.295522 - Product: TRIPP LITE UPS
   0.295527 - Serial Number: <Redacted>
   0.295532 - Bus: /dev/usb
   0.295538 - Device release number: 0000
   0.295543 Trying to match device
   0.295565 Device matches
   0.305439 HID descriptor length 1028
   0.351667 Report Descriptor size = 1028
   0.352039 Using subdriver: TrippLite HID 0.82
   0.352061 95 HID objects found
   0.359940 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28,
Offset: 0, Size: 8, Value: 6
   0.369830 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID:
0x29, Offset: 0, Size: 8, Value: 20
   0.379833 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID:
0x2b, Offset: 0, Size: 8, Value: 4
   0.389797 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature,
ReportID: 0x30, Offset: 0, Size: 8, Value: 120
   0.399803 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID:
0x31, Offset: 0, Size: 16, Value: 122.8
   0.409815 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.419801 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature,
ReportID: 0x2a, Offset: 0, Size: 8, Value: 10
   0.429964 Path: UPS.PowerSummary.iOEMInformation, Type: Feature,
ReportID: 0x62, Offset: 0, Size: 8, Value: 4
   0.439821 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID:
0x33, Offset: 0, Size: 8, Value: 2
   0.449793 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.449816 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.459817 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature,
ReportID: 0x3a, Offset: 0, Size: 8, Value: 25
   0.469798 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature,
ReportID: 0x37, Offset: 0, Size: 8, Value: 100
   0.479826 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID:
0x36, Offset: 0, Size: 8, Value: 100
   0.489796 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature,
ReportID: 0x38, Offset: 0, Size: 8, Value: 50
   0.499806 Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature,
ReportID: 0x3b, Offset: 0, Size: 8, Value: 1
   0.509801 Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature,
ReportID: 0x39, Offset: 0, Size: 8, Value: 1
   0.519703 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID:
0x2c, Offset: 0, Size: 8, Value: 1
   0.529542 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID:
0x35, Offset: 0, Size: 16, Value: 4222
   0.529565 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID:
0x35, Offset: 0, Size: 16, Value: 4222
   0.539558 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.539581 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   0.539603 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   0.539614 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   0.539624 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   0.539635 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   0.539645 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   0.539654 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   0.539664 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   0.539674 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.539684 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Feature, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   0.539694 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   0.539704 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   0.539714 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   0.539724 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   0.539734 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   0.539744 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   0.539753 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Feature, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   0.549556 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature,
ReportID: 0x04, Offset: 0, Size: 16, Value: 72
   0.559560 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature,
ReportID: 0x20, Offset: 0, Size: 16, Value: 81.6
   0.569418 Path:
UPS.BatterySystem.Battery.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0
   0.569442 Path: UPS.BatterySystem.Battery.PresentStatus.FullyCharged,
Type: Feature, ReportID: 0x23, Offset: 3, Size: 1, Value: 1
   0.569452 Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type:
Feature, ReportID: 0x23, Offset: 4, Size: 1, Value: 0
   0.569462 Path: UPS.BatterySystem.Battery.PresentStatus.Discharging,
Type: Feature, ReportID: 0x23, Offset: 5, Size: 1, Value: 0
   0.569472 Path: UPS.BatterySystem.Battery.PresentStatus.FullyDischarged,
Type: Feature, ReportID: 0x23, Offset: 6, Size: 1, Value: 0
   0.569482 Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement,
Type: Feature, ReportID: 0x23, Offset: 7, Size: 1, Value: 0
   0.579310 Path: UPS.BatterySystem.Battery.RemainingCapacity, Type:
Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 100
   0.589038 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10,
Offset: 0, Size: 8, Value: 1
   0.598958 Path: UPS.BatterySystem.Temperature, Type: Feature, ReportID:
0x1a, Offset: 0, Size: 16, Value: 296
   0.608842 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01,
Offset: 0, Size: 8, Value: 120
   0.618849 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02,
Offset: 0, Size: 8, Value: 60
   0.668359 libusb_get_report: Unknown error
   0.668382 Can't retrieve Report 55: Input/output error
   0.668391 Path: UPS.Flow.ffff0097, Type: Feature, ReportID: 0x55, Offset:
0, Size: 8
   0.678360 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID:
0x03, Offset: 0, Size: 16, Value: 3000
   0.688339 Path: UPS.PowerConverter.Input.Voltage, Type: Feature,
ReportID: 0x18, Offset: 0, Size: 16, Value: 122.8
   0.698342 Path: UPS.PowerConverter.Input.Frequency, Type: Feature,
ReportID: 0x19, Offset: 0, Size: 16, Value: 60
   0.708331 Path: UPS.PowerConverter.Output.Voltage, Type: Feature,
ReportID: 0x1b, Offset: 0, Size: 16, Value: 120
   0.718336 Path: UPS.PowerConverter.Output.Frequency, Type: Feature,
ReportID: 0x1c, Offset: 0, Size: 16, Value: 60
   0.728346 Path: UPS.PowerConverter.Output.Current, Type: Feature,
ReportID: 0x46, Offset: 0, Size: 16, Value: 3.1
   0.738339 Path: UPS.PowerConverter.Output.ActivePower, Type: Feature,
ReportID: 0x47, Offset: 0, Size: 16, Value: 288
   0.748338 Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type:
Feature, ReportID: 0x06, Offset: 0, Size: 16, Value: 65
   0.758360 Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type:
Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 138
   0.768335 Path: UPS.PowerConverter.Output.TLLowVoltageTransferMax, Type:
Feature, ReportID: 0x07, Offset: 0, Size: 16, Value: 70
   0.778350 Path: UPS.PowerConverter.Output.TLLowVoltageTransferMin, Type:
Feature, ReportID: 0x08, Offset: 0, Size: 16, Value: 65
   0.788336 Path: UPS.PowerConverter.Output.TLHighVoltageTransferMax, Type:
Feature, ReportID: 0x0a, Offset: 0, Size: 16, Value: 138
   0.798353 Path: UPS.PowerConverter.Output.TLHighVoltageTransferMin, Type:
Feature, ReportID: 0x0b, Offset: 0, Size: 16, Value: 133
   0.808330 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type:
Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
   0.808353 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature,
ReportID: 0x22, Offset: 1, Size: 1, Value: 0
   0.808363 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature,
ReportID: 0x22, Offset: 2, Size: 1, Value: 0
   0.808373 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature,
ReportID: 0x22, Offset: 4, Size: 1, Value: 0
   0.808383 Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature,
ReportID: 0x22, Offset: 5, Size: 1, Value: 1
   0.808393 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type:
Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
   0.808402 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type:
Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
   0.808412 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type:
Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
   0.818346 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   0.828331 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
   0.838342 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
   0.848337 Path: UPS.OutletSystem.Outlet.ActivePower, Type: Feature,
ReportID: 0x54, Offset: 0, Size: 16, Value: 288
   0.856257 Path: UPS.OutletSystem.Outlet.PercentLoad, Type: Feature,
ReportID: 0x1e, Offset: 0, Size: 8, Value: 12
   0.866091 Path: UPS.OutletSystem.Outlet.TLDelayBeforeStartup, Type:
Feature, ReportID: 0x16, Offset: 0, Size: 16, Value: 0
   0.875972 Path: UPS.OutletSystem.Outlet.ffff0081, Type: Feature,
ReportID: 0x41, Offset: 0, Size: 8, Value: 0
   0.885854 Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature,
ReportID: 0x51, Offset: 0, Size: 8, Value: 0
   0.895862 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.905866 Path: UPS.OutletSystem.Outlet.ffff0093, Type: Feature,
ReportID: 0x53, Offset: 0, Size: 8, Value: 0
   0.915885 Path: UPS.OutletSystem.Outlet.ffff0094, Type: Feature,
ReportID: 0x56, Offset: 0, Size: 8, Value: 1
   0.925888 Path: UPS.OutletSystem.Outlet.TLOutletsAvailableMask, Type:
Feature, ReportID: 0x67, Offset: 0, Size: 8, Value: 3
   0.935860 Path: UPS.OutletSystem.Outlet.TLOutletsStatusMask, Type:
Feature, ReportID: 0x68, Offset: 0, Size: 8, Value: 3
   0.945852 Path: UPS.OutletSystem.Outlet.ffff0098, Type: Feature,
ReportID: 0x69, Offset: 0, Size: 8, Value: 0
   0.996314 libusb_get_report: Unknown error
   0.996337 Can't retrieve Report 6a: Input/output error
   0.996346 Path: UPS.OutletSystem.Outlet.ffff0099, Type: Feature,
ReportID: 0x6a, Offset: 0, Size: 8
   1.046313 libusb_get_report: Unknown error
   1.046335 Can't retrieve Report 6b: Input/output error
   1.046344 Path: UPS.OutletSystem.Outlet.ffff009a, Type: Feature,
ReportID: 0x6b, Offset: 0, Size: 8
   1.056116 Path: UPS.TLCustom.[1].ffff0075, Type: Feature, ReportID: 0x0d,
Offset: 0, Size: 8, Value: 8
   1.065995 Path: UPS.TLCustom.[1].ffff0076, Type: Feature, ReportID: 0x0e,
Offset: 0, Size: 8, Value: 0
   1.075857 Path: UPS.TLCustom.[1].UPSFirmwareVersion, Type: Feature,
ReportID: 0x0f, Offset: 0, Size: 8, Value: 208
   1.085849 Path: UPS.TLCustom.[1].ffff009b, Type: Feature, ReportID: 0x42,
Offset: 0, Size: 8, Value: 0
   1.097175 Path: UPS.TLCustom.[1].ffff009c, Type: Feature, ReportID: 0x43,
Offset: 0, Size: 8, Value: 1
   1.105975 Path: UPS.TLCustom.[1].CommunicationProtocolVersion, Type:
Feature, ReportID: 0x6c, Offset: 0, Size: 16, Value: 16387
   1.106017 Report descriptor retrieved (Reportlen = 1028)
   1.106024 Found HID device
   1.106030 Detected a UPS: Tripp Lite      /TRIPP LITE UPS
   1.106113 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   1.106157 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature,
ReportID: 0x3a, Offset: 0, Size: 8, Value: 25
   1.106191 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature,
ReportID: 0x38, Offset: 0, Size: 8, Value: 50
   1.106222 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID:
0x35, Offset: 0, Size: 16, Value: 4222
   1.106247 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature,
ReportID: 0x04, Offset: 0, Size: 16, Value: 72
   1.106278 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature,
ReportID: 0x20, Offset: 0, Size: 16, Value: 81.6
   1.106310 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature,
ReportID: 0x2a, Offset: 0, Size: 8, Value: 10
   1.121628 Path: UPS.BatterySystem.Temperature, Type: Feature, ReportID:
0x1a, Offset: 0, Size: 16, Value: 296
   1.121711 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
   1.121744 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   1.121779 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
   1.121802 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10,
Offset: 0, Size: 8, Value: 1
   1.121823 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   1.121844 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID:
0x03, Offset: 0, Size: 16, Value: 3000
   1.121867 Path: UPS.OutletSystem.Outlet.ActivePower, Type: Feature,
ReportID: 0x54, Offset: 0, Size: 16, Value: 288
   1.121898 Path: UPS.OutletSystem.Outlet.PercentLoad, Type: Feature,
ReportID: 0x1e, Offset: 0, Size: 8, Value: 12
   1.121922 Path: UPS.TLCustom.[1].UPSFirmwareVersion, Type: Feature,
ReportID: 0x0f, Offset: 0, Size: 8, Value: 208
   1.121942 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   1.121964 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   1.121986 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Feature, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   1.122009 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   1.122032 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   1.122058 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   1.122086 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   1.122107 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   1.122129 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   1.122152 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Feature, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   1.122205 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type:
Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
   1.122225 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature,
ReportID: 0x22, Offset: 1, Size: 1, Value: 0
   1.122243 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature,
ReportID: 0x22, Offset: 2, Size: 1, Value: 0
   1.122273 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature,
ReportID: 0x22, Offset: 4, Size: 1, Value: 0
   1.122294 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type:
Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
   1.122312 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type:
Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
   1.122332 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type:
Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
   1.122352 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature,
ReportID: 0x30, Offset: 0, Size: 8, Value: 120
   1.122373 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID:
0x31, Offset: 0, Size: 16, Value: 122.8
   1.122403 Path: UPS.PowerConverter.Input.Frequency, Type: Feature,
ReportID: 0x19, Offset: 0, Size: 16, Value: 60
   1.122425 Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type:
Feature, ReportID: 0x06, Offset: 0, Size: 16, Value: 65
   1.122448 Path: UPS.PowerConverter.Output.TLLowVoltageTransferMax, Type:
Feature, ReportID: 0x07, Offset: 0, Size: 16, Value: 70
   1.122479 Path: UPS.PowerConverter.Output.TLLowVoltageTransferMin, Type:
Feature, ReportID: 0x08, Offset: 0, Size: 16, Value: 65
   1.122503 Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type:
Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 138
   1.122527 Path: UPS.PowerConverter.Output.TLHighVoltageTransferMax, Type:
Feature, ReportID: 0x0a, Offset: 0, Size: 16, Value: 138
   1.122549 Path: UPS.PowerConverter.Output.TLHighVoltageTransferMin, Type:
Feature, ReportID: 0x0b, Offset: 0, Size: 16, Value: 133
   1.122570 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01,
Offset: 0, Size: 8, Value: 120
   1.122589 Path: UPS.PowerConverter.Output.Voltage, Type: Feature,
ReportID: 0x1b, Offset: 0, Size: 16, Value: 120
   1.122619 Path: UPS.PowerConverter.Output.Current, Type: Feature,
ReportID: 0x46, Offset: 0, Size: 16, Value: 3.1
   1.122640 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02,
Offset: 0, Size: 8, Value: 60
   1.122661 Path: UPS.PowerConverter.Output.Frequency, Type: Feature,
ReportID: 0x1c, Offset: 0, Size: 16, Value: 60
   1.122682 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10,
Offset: 0, Size: 8, Value: 1
   1.122699 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10,
Offset: 0, Size: 8, Value: 1
   1.122716 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10,
Offset: 0, Size: 8, Value: 1
   1.122737 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   1.122757 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
   1.122775 Path: UPS.OutletSystem.Outlet.TLDelayBeforeStartup, Type:
Feature, ReportID: 0x16, Offset: 0, Size: 16, Value: 0
   1.122795 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   1.122815 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
   1.122832 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   1.122849 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   1.122867 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   1.122884 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   1.122902 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   1.122919 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   1.122936 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   1.122969 upsdrv_initinfo...
   1.122982 upsdrv_updateinfo...
   1.349376 Got 1 HID objects...
   1.349406 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   1.349415 Quick update...
   1.349424 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
   1.349435 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   1.349445 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
   1.349456 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   1.349465 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   1.349475 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   1.349485 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   1.349493 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   1.349502 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   1.349612 dstate_init: sock /var/db/nut/usbhid-ups-ups open on fd 6
   1.349648 upsdrv_updateinfo...
   1.536298 Got 1 HID objects...
   1.536330 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   1.536340 Quick update...
   1.536350 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
   1.536361 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   1.536372 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
   1.536383 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   1.536393 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   1.536402 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   1.536412 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   1.536421 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   1.536430 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   3.359261 upsdrv_updateinfo...
   3.362403 Got 9 HID objects...
   3.362433 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   3.362450 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   3.362463 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
   3.362475 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   3.362486 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
   3.362498 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   3.362509 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   3.362520 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   3.362532 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   3.362540 Quick update...
   3.372339 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
   3.382644 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   3.392571 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
   3.392600 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
   3.392610 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   3.392621 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
   3.392631 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   3.392640 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   3.392649 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   5.426452 upsdrv_updateinfo...
   5.543177 Got 1 HID objects...
   5.543207 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   5.543219 Quick update...
   5.553136 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
   5.563036 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   5.572900 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
   5.582768 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   5.582799 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   5.582809 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   5.582820 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   5.582830 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   5.582839 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   7.445986 upsdrv_updateinfo...
   7.552320 Got 9 HID objects...
   7.552351 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   7.552368 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   7.552380 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
   7.552392 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   7.552404 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
   7.552416 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   7.552426 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   7.552438 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   7.552458 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   7.552473 Quick update...
   7.562269 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
   7.572237 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   7.582238 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
   7.582263 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
   7.582273 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   7.582282 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
   7.582292 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   7.582301 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   7.582310 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   9.543976 upsdrv_updateinfo...
   9.559240 Got 1 HID objects...
   9.559270 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   9.559282 Quick update...
   9.569238 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
   9.579222 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
   9.589215 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
   9.599226 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   9.599250 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   9.599260 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   9.599271 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   9.599280 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   9.599290 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  11.566982 upsdrv_updateinfo...
  11.569235 Got 9 HID objects...
  11.569266 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  11.569283 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  11.569296 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  11.569308 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  11.569320 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  11.569338 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  11.569356 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  11.569375 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  11.569388 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  11.569396 Quick update...
  11.579362 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  11.589456 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  11.599454 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  11.599480 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  11.599491 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  11.599501 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  11.599511 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  11.599520 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  11.599529 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  13.631417 upsdrv_updateinfo...
  13.752266 Got 1 HID objects...
  13.752296 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
  13.752309 Quick update...
  13.762474 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  13.772464 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  13.782453 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  13.792452 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
  13.792477 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  13.792487 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
  13.792499 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  13.792509 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  13.792518 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  15.748057 upsdrv_updateinfo...
  15.756104 Got 9 HID objects...
  15.756135 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  15.756152 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  15.756165 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  15.756177 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  15.756188 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  15.756200 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  15.756211 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  15.756222 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  15.756233 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  15.756242 Quick update...
  15.766099 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  15.776051 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  15.785923 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  15.785949 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  15.785959 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  15.785968 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  15.785980 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  15.785989 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  15.785998 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  17.753938 upsdrv_updateinfo...
  17.945073 Got 1 HID objects...
  17.945104 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
  17.945116 Quick update...
  17.952970 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  17.961959 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  17.970958 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  17.978958 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
  17.978981 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  17.978991 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
  17.979003 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  17.979012 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  17.979021 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  19.763995 upsdrv_updateinfo...
  19.764373 Got 1 HID objects...
  19.764402 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
  19.764414 Quick update...
  19.772943 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  19.782939 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  19.792886 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  19.802894 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
  19.802917 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  19.802928 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
  19.802939 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  19.802948 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  19.802958 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  21.806950 upsdrv_updateinfo...
  21.900643 Got 9 HID objects...
  21.900676 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  21.900693 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  21.900706 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  21.900718 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  21.900730 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  21.900741 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  21.900753 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  21.900764 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  21.900775 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  21.900783 Quick update...
  21.909852 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  21.919830 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  21.929705 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  21.929729 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  21.929738 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  21.929748 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  21.929758 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  21.929767 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  21.929776 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  23.826222 upsdrv_updateinfo...
  23.875136 Got 1 HID objects...
  23.875167 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
  23.875179 Quick update...
  23.885270 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  23.895241 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  23.905236 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  23.915241 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
  23.915267 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  23.915277 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
  23.915289 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  23.915298 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  23.915307 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  25.949424 upsdrv_updateinfo...
  26.065981 Got 9 HID objects...
  26.066013 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  26.066030 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  26.066043 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  26.066054 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  26.066066 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  26.066077 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  26.066088 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  26.066100 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  26.066112 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  26.066120 Quick update...
  26.075898 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  26.085736 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  26.095597 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  26.095622 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  26.095632 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  26.095641 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  26.095651 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  26.095660 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  26.095669 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  28.068786 upsdrv_updateinfo...
  28.078159 Got 1 HID objects...
  28.078188 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
  28.078201 Quick update...
  28.088262 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  28.098246 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  28.108248 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  28.118240 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
  28.118264 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  28.118275 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
  28.118286 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  28.118295 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  28.118305 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  30.131462 upsdrv_updateinfo...
  30.258956 Got 9 HID objects...
  30.258988 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  30.259005 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  30.259017 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  30.259030 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  30.259041 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  30.259053 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  30.259064 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  30.259075 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  30.259087 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  30.259095 Quick update...
  30.268932 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  30.278923 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  30.288895 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  30.288919 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  30.288929 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  30.288938 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  30.288948 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  30.288957 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  30.288967 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  32.171461 upsdrv_updateinfo...
  32.261986 Got 1 HID objects...
  32.262016 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
  32.262028 Full update...
  32.262038 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
  32.271902 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature,
ReportID: 0x38, Offset: 0, Size: 8, Value: 50
  32.281869 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID:
0x35, Offset: 0, Size: 16, Value: 4176
  32.291870 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature,
ReportID: 0x20, Offset: 0, Size: 16, Value: 81.6
  32.301861 Path: UPS.BatterySystem.Temperature, Type: Feature, ReportID:
0x1a, Offset: 0, Size: 16, Value: 296
  32.311868 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  32.321867 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  32.331868 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  32.341860 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10,
Offset: 0, Size: 8, Value: 1
  32.351871 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
  32.361900 Path: UPS.OutletSystem.Outlet.ActivePower, Type: Feature,
ReportID: 0x54, Offset: 0, Size: 16, Value: 292
  32.371873 Path: UPS.OutletSystem.Outlet.PercentLoad, Type: Feature,
ReportID: 0x1e, Offset: 0, Size: 8, Value: 12
  32.381876 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
  32.391871 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  32.391896 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Feature, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  32.391907 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
  32.391916 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  32.391926 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
  32.391936 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  32.391945 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  32.391954 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  32.391964 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Feature, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  32.401893 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type:
Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
  32.401917 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature,
ReportID: 0x22, Offset: 1, Size: 1, Value: 0
  32.401927 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature,
ReportID: 0x22, Offset: 2, Size: 1, Value: 0
  32.401936 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature,
ReportID: 0x22, Offset: 4, Size: 1, Value: 0
  32.401945 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type:
Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
  32.401954 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type:
Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
  32.401963 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type:
Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
  32.411885 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID:
0x31, Offset: 0, Size: 16, Value: 122.8
  32.421865 Path: UPS.PowerConverter.Input.Frequency, Type: Feature,
ReportID: 0x19, Offset: 0, Size: 16, Value: 60
  32.431866 Path: UPS.PowerConverter.Output.Voltage, Type: Feature,
ReportID: 0x1b, Offset: 0, Size: 16, Value: 120
  32.441862 Path: UPS.PowerConverter.Output.Current, Type: Feature,
ReportID: 0x46, Offset: 0, Size: 16, Value: 3.1
  32.451869 Path: UPS.PowerConverter.Output.Frequency, Type: Feature,
ReportID: 0x1c, Offset: 0, Size: 16, Value: 60
  34.212879 upsdrv_updateinfo...
  34.452734 Got 9 HID objects...
  34.452774 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  34.452790 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  34.452803 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  34.452815 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  34.452826 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  34.452838 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  34.452850 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  34.452861 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  34.452872 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  34.452880 Quick update...
  34.462704 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  34.472611 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  34.482465 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  34.482489 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  34.482498 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  34.482508 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  34.482518 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  34.482527 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  34.482536 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  36.251466 upsdrv_updateinfo...
  36.272722 Got 1 HID objects...
  36.272752 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
  36.272765 Quick update...
  36.282676 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  36.292584 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  36.302441 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  36.312309 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
  36.312332 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  36.312342 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
  36.312353 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  36.312362 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  36.312372 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  38.324592 upsdrv_updateinfo...
  38.461074 Got 9 HID objects...
  38.461107 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  38.461123 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  38.461136 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  38.461148 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  38.461159 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  38.461172 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  38.461183 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  38.461194 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  38.461205 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  38.461214 Quick update...
  38.469551 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  38.479412 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  38.489280 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  38.489304 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  38.489314 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  38.489323 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  38.489333 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  38.489342 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  38.489351 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  40.368691 upsdrv_updateinfo...
  40.431863 Got 1 HID objects...
  40.431894 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
  40.431906 Quick update...
  40.441770 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  40.451748 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  40.461756 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  40.471750 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
  40.471773 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  40.471783 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
  40.471794 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  40.471803 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  40.471812 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  42.389570 upsdrv_updateinfo...
  42.442644 Got 9 HID objects...
  42.442676 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  42.442692 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  42.442705 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  42.442717 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  42.442729 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  42.442741 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  42.442752 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  42.442763 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  42.442775 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  42.442783 Quick update...
  42.452588 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 0
  42.462494 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1
  42.471641 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: -1
  42.471665 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 0
  42.471675 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  42.471684 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  42.471694 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 0
  42.471703 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  42.471713 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
-- 
Brandon Wright
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20220113/41e42363/attachment-0001.htm>
    
    
More information about the Nut-upsuser
mailing list