[Nut-upsuser] EVER ECO PRO AVR CDS force shutdown not wirking
Marek Czerski
m.czerski at ap-tech.pl
Thu Aug 3 19:59:58 BST 2023
Hi all,
Debian bookworm (all updates installed)
NUT 2.8.0-7 deb installed from http://deb.debian.org/debian
UPS usbhid 2e51:0000 EVER ECO PRO AVR CDS
upsc output:
battery.capacity: 100
battery.charge: 100
battery.runtime: 17911
battery.runtime.low: 100
battery.type: 18
battery.voltage: 26
device.mfr: EVER
device.model: ECO PRO AVR CDS
device.serial: 800200074230430520353859
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 1
driver.parameter.port: auto
driver.parameter.synchronous: auto
driver.version: 2.8.0
driver.version.data: Ever HID 0.1
driver.version.internal: 0.47
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
experimental.battery.batteryid: 1
experimental.battery.chargerid: 1
experimental.battery.input_flowid: 1
experimental.battery.input_id: 1
experimental.battery.output_flowid: 2
experimental.battery.output_id: 1
experimental.battery.systemid: 1
experimental.control.audible_alarm: 1
experimental.outlet.1.present: yes
experimental.outlet.1.system_id: 1
experimental.outlet.1.undefined: 0
experimental.powerconverter.input_flow_id: 1
experimental.powerconverter.input_id: 1
experimental.powerconverter.output_flowid: 3
experimental.powerconverter.output_id: 1
experimental.powerconverter.powerconverterid: 1
experimental.powersummary.capacity_granularity_1: 1
experimental.powersummary.capacity_granularity_2: 1
experimental.powersummary.capacity_mode: 2
experimental.powersummary.flow_id: 3
experimental.powersummary.rechargeable: 1
experimental.statistics.autonomous_operation_time: 193
experimental.statistics.discharge_counter: 9
experimental.statistics.mains_loss_counter: 26
experimental.statistics.mains_operation_time: 190
experimental.statistics.overload_counter: 1
experimental.statistics.overload_operation_time: 0
experimental.statistics.rising_AVR_trigger_counter: 1
experimental.statistics.short_circuit_counter: 2
experimental.status.alarms:
experimental.status.messages:
experimental.status.workmode: ONLINE
experimental.ups.flow_id: 1
input.frequency: 50
input.voltage: 222
outlet.1.id: 1
outlet.1.switchable: no
output.current: 0
output.frequency: 50
output.frequency.nominal: 50
output.voltage: 230
output.voltage.nominal: 230
powerfactor: 0
ups.delay.shutdown: 20
ups.load: 0
ups.mfr: EVER
ups.model: ECO PRO AVR CDS
ups.power: 0
ups.power.nominal: 1000
ups.productid: 0000
ups.realpower: 0
ups.realpower.nominal: 650
ups.serial: 800200074230430520353859
ups.status: OL
ups.timer.shutdown: -1
ups.vendorid: 2e51
while testing FSD (sudo upsmon -c fsd) UPS is not shutting down. All seems to work correctly, just ups is not shutting down.
/lib/systemd/system-shutdown/nutshutdown:
#!/bin/sh
if (/sbin/upsmon -K)
then
echo "Killing the power, bye!"
/sbin/upsdrvctl shutdown
sleep 120
# uh oh... the UPS power-off failed
# you probably want to reboot here so you don't get stuck!
# *** see also the section on power races in the FAQ! ***
fi
I also tested direct shutdown command to the UPS:
sudo systemctl stop nut-driver at ups.service
sudo /lib/nut/usbhid-ups -a ups -k -D -D -D
and the output of the last command:
Network UPS Tools - Generic HID driver 0.47 (2.8.0)
USB communication driver (libusb 1.0) 0.43
0.000000 [D1] debug level is '3'
0.000707 [D2] Initializing an USB-connected UPS with library libusb-1.0.26 (API: 0x1000109) (NUT subdriver name='USB communication driver (libusb 1.0)' ver='0.43')
0.000713 [D1] upsdrv_initups (non-SHUT)...
0.003404 [D2] Checking device 1 of 6 (0B95/1790)
0.003419 [D1] Failed to open device (0B95/1790), skipping: Access denied (insufficient permissions)
0.003423 [D2] Checking device 2 of 6 (1D6B/0003)
0.003428 [D1] Failed to open device (1D6B/0003), skipping: Access denied (insufficient permissions)
0.003431 [D2] Checking device 3 of 6 (2E51/0000)
0.005003 [D2] - VendorID: 2e51
0.005009 [D2] - ProductID: 0000
0.005012 [D2] - Manufacturer: EVER
0.005015 [D2] - Product: ECO PRO AVR CDS
0.005017 [D2] - Serial Number: 800200074230430520353859
0.005020 [D2] - Bus: 001
0.005023 [D2] - Device: unknown
0.005025 [D2] - Device release number: 0100
0.005028 [D2] Trying to match device
0.005031 [D2] match_function_subdriver (non-SHUT mode): matching a device...
0.005036 [D3] match_function_regex: matching a device...
0.005041 [D2] Device matches
0.005044 [D2] Reading first configuration descriptor
0.005049 [D3] libusb_kernel_driver_active() returned 0
0.005059 [D2] Claimed interface 0 successfully
0.005063 [D3] nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
0.005231 [D3] HID descriptor, method 1: (9 bytes) => 09 21 00 01 00 01 22 37 06
0.005237 [D3] HID descriptor length (method 1) 1591
0.005242 [D3] HID descriptor, method 2: (9 bytes) => 09 21 00 01 00 01 22 37 06
0.005245 [D3] HID descriptor length (method 2) 1591
0.005248 [D2] HID descriptor length 1591
0.007506 [D2] Report Descriptor size = 1591
0.007523 [D3] Report Descriptor: (1591 bytes) => 05 84 09 04 a1 01 09 1e a1 00 85 01 75
0.007528 [D3] 08 95 01 15 00 25 7f 65 00 55 00 09 1f b1 03 85 02 75 10 95 01 15 00 26 2c
0.007533 [D3] 01 67 21 d1 f0 00 55 07 09 40 b1 03 85 03 75 08 15 00 25 64 66 01 f0 55 00
0.007538 [D3] 09 42 b1 03 c0 09 1e a1 00 85 04 75 08 95 01 15 00 25 7f 65 00 55 00 09 1f
0.007543 [D3] b1 03 85 05 75 10 95 01 15 00 25 64 67 21 d1 f0 00 55 07 09 40 b1 03 c0 09
0.007548 [D3] 1e a1 00 85 06 75 08 95 01 15 00 25 7f 65 00 55 00 09 1f b1 03 85 07 75 10
0.007554 [D3] 95 01 15 00 26 2c 01 67 21 d1 f0 00 55 07 09 40 b1 03 85 08 75 08 95 01 15
0.007561 [D3] 00 25 64 66 01 f0 55 00 09 42 b1 03 85 09 75 10 95 01 15 00 26 88 13 66 21
0.007566 [D3] d1 55 07 09 43 b1 03 85 0a 75 10 09 44 b1 03 c0 09 10 a1 00 85 0b 75 08 95
0.007571 [D3] 01 15 00 25 7f 65 00 55 00 09 11 b1 03 09 1a a1 00 85 0c 75 08 95 01 15 00
0.007576 [D3] 25 7f 09 1b b1 03 85 0d 09 1f 75 08 b1 03 c0 09 14 a1 00 85 0e 75 08 95 01
0.007582 [D3] 15 00 25 7f 09 15 b1 03 c0 09 1c a1 00 85 0f 75 08 95 01 15 00 25 7f 09 1d
0.007588 [D3] b1 03 85 10 75 08 09 1f b1 03 c0 09 12 a1 00 85 11 75 08 95 01 15 00 25 7f
0.007594 [D3] 09 13 b1 03 c0 c0 09 16 a1 00 85 12 75 08 95 01 15 00 25 7f 09 17 b1 03 09
0.007600 [D3] 1a a1 00 85 13 75 08 95 01 15 00 25 7f 09 1b b1 03 85 14 09 1f b1 03 85 15
0.007605 [D3] 75 10 95 01 15 00 26 2c 01 67 21 d1 f0 00 55 07 09 30 b1 83 09 30 81 83 85
0.007611 [D3] 16 09 53 b1 83 85 17 09 54 b1 83 85 18 26 8a 02 66 01 f0 55 0f 09 32 b1 83
0.007617 [D3] 09 32 81 83 c0 09 1a a1 00 85 19 75 08 95 01 15 00 25 7f 65 00 55 00 09 1b
0.007623 [D3] b1 03 85 1a 09 1f b1 03 85 1b 75 10 95 01 15 00 26 e8 03 67 21 d1 f0 00 55
0.007628 [D3] 06 09 30 b1 83 09 30 81 83 c0 09 1c a1 00 85 1c 65 00 55 00 75 08 95 01 15
0.007634 [D3] 00 25 7f 09 1d b1 03 85 1d 09 1f b1 03 85 1e 26 ff 00 09 35 b1 83 09 35 81
0.007639 [D3] 83 85 1f 75 10 95 01 15 00 26 2c 01 67 21 d1 f0 00 55 07 09 30 b1 83 09 30
0.007645 [D3] 81 83 85 20 26 f4 01 67 01 00 10 00 55 0e 09 31 b1 83 09 31 81 83 85 21 75
0.007652 [D3] 10 95 01 15 00 26 8a 02 66 01 f0 55 0f 09 32 b1 83 09 32 81 83 85 22 75 10
0.007656 [D3] 95 01 15 00 26 40 1f 66 21 d1 55 07 09 33 b1 83 09 33 81 83 85 23 09 34 b1
0.007661 [D3] 83 09 34 81 83 c0 c0 09 18 a1 00 85 24 75 08 95 01 15 00 25 7f 65 00 55 00
0.007667 [D3] 09 19 b1 03 09 20 a1 00 09 21 85 25 b1 03 09 02 a1 02 15 00 25 01 85 26 75
0.007672 [D3] 01 95 08 09 60 09 6c 09 00 09 00 09 00 09 00 09 00 09 00 b1 83 09 60 09 6c
0.007678 [D3] 09 00 09 00 09 00 09 00 09 00 09 00 81 83 c0 c0 c0 09 24 a1 00 85 2f 75 08
0.007683 [D3] 95 01 15 00 25 7f 65 00 55 00 09 25 b1 03 85 30 09 1f b1 03 85 31 25 03 0b
0.007689 [D3] 2c 00 85 00 b1 03 85 32 25 01 0b 8b 00 85 00 b1 03 85 33 25 64 0b 83 00 85
0.007695 [D3] 00 b1 03 85 34 0b 67 00 85 00 b1 03 85 35 0b 8d 00 85 00 b1 03 85 3e 0b 8e
0.007701 [D3] 00 85 00 b1 03 85 36 0b 66 00 85 00 b1 83 0b 66 00 85 00 81 83 85 37 75 10
0.007707 [D3] 95 01 15 00 27 ff ff 00 00 66 01 10 55 00 0b 68 00 85 00 b1 83 0b 68 00 85
0.007714 [D3] 00 81 83 85 38 0b 2a 00 85 00 b1 02 85 39 75 08 95 01 65 00 55 00 15 00 25
0.007721 [D3] 7f 0b 89 00 85 00 b1 03 85 3a 26 ff 00 09 35 b1 83 85 3b 75 10 95 01 15 ff
0.007727 [D3] 26 40 38 66 01 10 55 00 09 57 b1 82 85 3c 75 10 95 01 15 00 26 e8 03 67 21
0.007733 [D3] d1 f0 00 55 06 09 30 b1 83 09 02 a1 02 85 3d 75 01 95 10 15 00 25 01 65 00
0.007740 [D3] 55 00 0b d0 00 85 00 0b 45 00 85 00 0b 44 00 85 00 0b 42 00 85 00 0b 43 00
0.007746 [D3] 85 00 0b 4b 00 85 00 0b d1 00 85 00 09 65 09 62 09 69 09 6e 09 00 09 00 09
0.007752 [D3] 72 09 73 09 61 b1 83 0b d0 00 85 00 0b 45 00 85 00 0b 44 00 85 00 0b 42 00
0.007759 [D3] 85 00 0b 43 00 85 00 0b 4b 00 85 00 0b d1 00 85 00 09 65 09 62 09 69 09 6e
0.007771 [D3] 09 00 09 00 09 72 09 73 09 61 81 83 c0 c0 06 00 ff a1 00 85 46 75 10 95 01
0.007778 [D3] 15 00 27 ff ff 00 00 65 00 55 00 09 10 b1 03 85 47 95 02 09 24 09 25 b1 03
0.007784 [D3] 85 48 95 02 09 26 09 27 b1 03 85 49 95 02 09 28 09 29 b1 03 09 90 a1 02 85
0.007789 [D3] 4a 75 01 95 10 15 00 25 01 09 91 09 00 09 93 09 94 09 00 09 96 09 97 09 00
0.007799 [D3] 09 00 09 00 09 00 09 00 09 00 09 00 09 00 09 00 b1 03 c0 09 16 a1 02 85 4b
0.007805 [D3] 75 01 95 10 15 00 25 01 09 17 09 18 09 19 09 00 09 00 09 00 09 1d 09 00 09
0.007812 [D3] 00 09 20 09 00 09 00 09 00 09 2a 09 00 09 00 b1 03 c0 09 30 a1 02 85 4c 75
0.007818 [D3] 01 95 10 15 00 25 01 09 31 09 32 09 00 09 00 09 35 09 00 09 37 09 38 09 00
0.007824 [D3] 09 00 09 00 09 00 09 00 09 00 09 00 09 00 b1 03 c0 85 4f 75 10 95 01 25 64
0.007830 [D3] 55 00 65 00 09 42 b1 83 09 50 a1 02 85 54 75 01 95 08 15 00 25 01 09 54 09
0.007837 [D3] 00 09 00 09 00 09 00 09 00 09 00 09 00 b1 02 c0 85 55 15 00 26 f4 01 67 21
0.007843 [D3] d1 f0 00 55 07 75 10 95 01 09 60 b1 02 85 56 09 98 b1 02 85 57 09 99 b1 02
0.007849 [D3] 85 58 26 e8 03 66 01 f0 55 0f 75 10 95 01 09 63 b1 02 85 59 09 64 b1 02 85
0.007854 [D3] 5a 15 00 26 f4 01 67 21 d1 f0 00 55 09 75 10 95 01 09 9a b1 02 85 c8 75 10
0.007859 [D3] 95 01 15 00 27 ff ff 00 00 65 00 55 00 09 69 b1 83 85 ca 09 6b b1 83 85 cb
0.007865 [D3] 09 6c b1 83 85 cc 09 6d b1 83 85 cd 09 6e b1 83 85 cf 09 70 b1 83 85 d0 09
0.007870 [D3] 71 b1 83 85 d1 09 72 b1 83 85 d2 15 00 27 ff ff 00 00 65 00 55 00 75 10 95
0.007876 [D3] 1e 09 9b 09 9c 09 9b 09 9c 09 9b 09 9c 09 9b 09 9c 09 9b 09 9c 09 9b 09 9c
0.007881 [D3] 09 9b 09 9c 09 9b 09 9c 09 9b 09 9c 09 9b 09 9c 09 9b 09 9c 09 9b 09 9c 09
0.007887 [D3] 9b 09 9c 09 9b 09 9c 09 9b 09 9c b1 83 c0 06 00 ff 09 9d a1 01 85 fd 09 9e
0.007893 [D3] 15 00 26 ff 00 75 08 95 78 b1 81 c0 09 9f a1 01 85 fe 09 a0 15 00 26 ff 00
0.007898 [D3] 75 08 95 3e b1 81 c0 09 9f a1 01 85 ff 09 a0 15 00 26 ff 00 75 08 95 0b b1
0.007902 [D3] 80 c0 c0
0.008013 Using subdriver: Ever HID 0.1
0.008018 [D1] 222 HID objects found
0.008192 [D3] Report[get]: (2 bytes) => 01 01
0.008203 [D1] Path: UPS.Flow.FlowID, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
0.008435 [D3] Report[get]: (3 bytes) => 02 e6 00
0.008445 [D1] Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x02, Offset: 0, Size: 16, Value: 230
0.008569 [D3] Report[get]: (2 bytes) => 03 32
0.008576 [D1] Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 50
0.008696 [D3] Report[get]: (2 bytes) => 04 02
0.008702 [D1] Path: UPS.Flow.FlowID, Type: Feature, ReportID: 0x04, Offset: 0, Size: 8, Value: 2
0.008822 [D3] Report[get]: (3 bytes) => 05 18 00
0.008829 [D1] Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x05, Offset: 0, Size: 16, Value: 24
0.008944 [D3] Report[get]: (2 bytes) => 06 03
0.008950 [D1] Path: UPS.Flow.FlowID, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 3
0.009069 [D3] Report[get]: (3 bytes) => 07 e6 00
0.009074 [D1] Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x07, Offset: 0, Size: 16, Value: 230
0.009191 [D3] Report[get]: (2 bytes) => 08 32
0.009196 [D1] Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x08, Offset: 0, Size: 8, Value: 50
0.009315 [D3] Report[get]: (3 bytes) => 09 e8 03
0.009320 [D1] Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 1000
0.009438 [D3] Report[get]: (3 bytes) => 0a 8a 02
0.009444 [D1] Path: UPS.Flow.ConfigActivePower, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 16, Value: 650
0.009603 [D3] Report[get]: (2 bytes) => 0b 01
0.009611 [D1] Path: UPS.BatterySystem.BatterySystemID, Type: Feature, ReportID: 0x0b, Offset: 0, Size: 8, Value: 1
0.009772 [D3] Report[get]: (2 bytes) => 0c 01
0.009782 [D1] Path: UPS.BatterySystem.Input.InputID, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 1
0.009965 [D3] Report[get]: (2 bytes) => 0d 01
0.009976 [D1] Path: UPS.BatterySystem.Input.FlowID, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 8, Value: 1
0.010102 [D3] Report[get]: (2 bytes) => 0e 01
0.010110 [D1] Path: UPS.BatterySystem.Charger.ChargerID, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 1
0.010231 [D3] Report[get]: (2 bytes) => 0f 01
0.010237 [D1] Path: UPS.BatterySystem.Output.OutputID, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 1
0.010399 [D3] Report[get]: (2 bytes) => 10 02
0.010405 [D1] Path: UPS.BatterySystem.Output.FlowID, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 2
0.010526 [D3] Report[get]: (2 bytes) => 11 01
0.010532 [D1] Path: UPS.BatterySystem.Battery.BatteryID, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 1
0.010653 [D3] Report[get]: (2 bytes) => 12 01
0.010659 [D1] Path: UPS.PowerConverter.PowerConverterID, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 1
0.010804 [D3] Report[get]: (2 bytes) => 13 01
0.010810 [D1] Path: UPS.PowerConverter.Input.InputID, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1
0.010953 [D3] Report[get]: (2 bytes) => 14 01
0.010959 [D1] Path: UPS.PowerConverter.Input.FlowID, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 1
0.011104 [D3] Report[get]: (3 bytes) => 15 de 00
0.011111 [D1] Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 222
0.011114 [D3] Report[buf]: (3 bytes) => 15 de 00
0.011119 [D1] Path: UPS.PowerConverter.Input.Voltage, Type: Input, ReportID: 0x15, Offset: 0, Size: 16, Value: 222
0.011240 [D3] Report[get]: (3 bytes) => 16 b8 00
0.011246 [D1] Path: UPS.PowerConverter.Input.LowVoltageTransfer, Type: Feature, ReportID: 0x16, Offset: 0, Size: 16, Value: 184
0.011392 [D3] Report[get]: (3 bytes) => 17 fd 00
0.011398 [D1] Path: UPS.PowerConverter.Input.HighVoltageTransfer, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 253
0.011517 [D3] Report[get]: (3 bytes) => 18 f7 01
0.011524 [D1] Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 50.3
0.011529 [D3] Report[buf]: (3 bytes) => 18 f7 01
0.011534 [D1] Path: UPS.PowerConverter.Input.Frequency, Type: Input, ReportID: 0x18, Offset: 0, Size: 16, Value: 50.3
0.011653 [D3] Report[get]: (2 bytes) => 19 02
0.011658 [D1] Path: UPS.PowerConverter.Input.InputID, Type: Feature, ReportID: 0x19, Offset: 0, Size: 8, Value: 2
0.011777 [D3] Report[get]: (2 bytes) => 1a 02
0.011783 [D1] Path: UPS.PowerConverter.Input.FlowID, Type: Feature, ReportID: 0x1a, Offset: 0, Size: 8, Value: 2
0.011903 [D3] Report[get]: (3 bytes) => 1b 07 01
0.011909 [D1] Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 16, Value: 26.3
0.011913 [D3] Report[buf]: (3 bytes) => 1b 07 01
0.011917 [D1] Path: UPS.PowerConverter.Input.Voltage, Type: Input, ReportID: 0x1b, Offset: 0, Size: 16, Value: 26.3
0.012036 [D3] Report[get]: (2 bytes) => 1c 01
0.012042 [D1] Path: UPS.PowerConverter.Output.OutputID, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 8, Value: 1
0.012162 [D3] Report[get]: (2 bytes) => 1d 03
0.012168 [D1] Path: UPS.PowerConverter.Output.FlowID, Type: Feature, ReportID: 0x1d, Offset: 0, Size: 8, Value: 3
0.012286 [D3] Report[get]: (2 bytes) => 1e 00
0.012292 [D1] Path: UPS.PowerConverter.Output.PercentLoad, Type: Feature, ReportID: 0x1e, Offset: 0, Size: 8, Value: 0
0.012297 [D3] Report[buf]: (2 bytes) => 1e 00
0.012302 [D1] Path: UPS.PowerConverter.Output.PercentLoad, Type: Input, ReportID: 0x1e, Offset: 0, Size: 8, Value: 0
0.012430 [D3] Report[get]: (3 bytes) => 1f df 00
0.012437 [D1] Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 16, Value: 223
0.012443 [D3] Report[buf]: (3 bytes) => 1f df 00
0.012448 [D1] Path: UPS.PowerConverter.Output.Voltage, Type: Input, ReportID: 0x1f, Offset: 0, Size: 16, Value: 223
0.012571 [D3] Report[get]: (3 bytes) => 20 00 00
0.012577 [D1] Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 0
0.012583 [D3] Report[buf]: (3 bytes) => 20 00 00
0.012588 [D1] Path: UPS.PowerConverter.Output.Current, Type: Input, ReportID: 0x20, Offset: 0, Size: 16, Value: 0
0.012708 [D3] Report[get]: (3 bytes) => 21 f7 01
0.012714 [D1] Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x21, Offset: 0, Size: 16, Value: 50.3
0.012719 [D3] Report[buf]: (3 bytes) => 21 f7 01
0.012725 [D1] Path: UPS.PowerConverter.Output.Frequency, Type: Input, ReportID: 0x21, Offset: 0, Size: 16, Value: 50.3
0.012855 [D3] Report[get]: (3 bytes) => 22 00 00
0.012865 [D1] Path: UPS.PowerConverter.Output.ApparentPower, Type: Feature, ReportID: 0x22, Offset: 0, Size: 16, Value: 0
0.012871 [D3] Report[buf]: (3 bytes) => 22 00 00
0.012877 [D1] Path: UPS.PowerConverter.Output.ApparentPower, Type: Input, ReportID: 0x22, Offset: 0, Size: 16, Value: 0
0.013001 [D3] Report[get]: (3 bytes) => 23 00 00
0.013007 [D1] Path: UPS.PowerConverter.Output.ActivePower, Type: Feature, ReportID: 0x23, Offset: 0, Size: 16, Value: 0
0.013011 [D3] Report[buf]: (3 bytes) => 23 00 00
0.013015 [D1] Path: UPS.PowerConverter.Output.ActivePower, Type: Input, ReportID: 0x23, Offset: 0, Size: 16, Value: 0
0.013146 [D3] Report[get]: (2 bytes) => 24 01
0.013154 [D1] Path: UPS.OutletSystem.OutletSystemID, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1
0.013277 [D3] Report[get]: (2 bytes) => 25 01
0.013284 [D1] Path: UPS.OutletSystem.Outlet.OutletID, Type: Feature, ReportID: 0x25, Offset: 0, Size: 8, Value: 1
0.013430 [D3] Report[get]: (2 bytes) => 26 01
0.013437 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Present, Type: Feature, ReportID: 0x26, Offset: 0, Size: 1, Value: 1
0.013441 [D3] Report[buf]: (2 bytes) => 26 01
0.013447 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Switchable, Type: Feature, ReportID: 0x26, Offset: 1, Size: 1, Value: 0
0.013452 [D3] Report[buf]: (2 bytes) => 26 01
0.013458 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Feature, ReportID: 0x26, Offset: 2, Size: 1, Value: 0
0.013463 [D3] Report[buf]: (2 bytes) => 26 01
0.013469 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Feature, ReportID: 0x26, Offset: 3, Size: 1, Value: 0
0.013474 [D3] Report[buf]: (2 bytes) => 26 01
0.013479 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Feature, ReportID: 0x26, Offset: 4, Size: 1, Value: 0
0.013484 [D3] Report[buf]: (2 bytes) => 26 01
0.013490 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Feature, ReportID: 0x26, Offset: 5, Size: 1, Value: 0
0.013494 [D3] Report[buf]: (2 bytes) => 26 01
0.013500 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Feature, ReportID: 0x26, Offset: 6, Size: 1, Value: 0
0.013503 [D3] Report[buf]: (2 bytes) => 26 01
0.013508 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Feature, ReportID: 0x26, Offset: 7, Size: 1, Value: 0
0.013511 [D3] Report[buf]: (2 bytes) => 26 01
0.013516 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Present, Type: Input, ReportID: 0x26, Offset: 0, Size: 1, Value: 1
0.013521 [D3] Report[buf]: (2 bytes) => 26 01
0.013526 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Switchable, Type: Input, ReportID: 0x26, Offset: 1, Size: 1, Value: 0
0.013531 [D3] Report[buf]: (2 bytes) => 26 01
0.013537 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Input, ReportID: 0x26, Offset: 2, Size: 1, Value: 0
0.013541 [D3] Report[buf]: (2 bytes) => 26 01
0.013545 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Input, ReportID: 0x26, Offset: 3, Size: 1, Value: 0
0.013549 [D3] Report[buf]: (2 bytes) => 26 01
0.013554 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Input, ReportID: 0x26, Offset: 4, Size: 1, Value: 0
0.013558 [D3] Report[buf]: (2 bytes) => 26 01
0.013613 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Input, ReportID: 0x26, Offset: 5, Size: 1, Value: 0
0.013619 [D3] Report[buf]: (2 bytes) => 26 01
0.013626 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Input, ReportID: 0x26, Offset: 6, Size: 1, Value: 0
0.013631 [D3] Report[buf]: (2 bytes) => 26 01
0.013636 [D1] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Input, ReportID: 0x26, Offset: 7, Size: 1, Value: 0
0.013819 [D3] Report[get]: (2 bytes) => 2f 01
0.013838 [D1] Path: UPS.PowerSummary.PowerSummaryID, Type: Feature, ReportID: 0x2f, Offset: 0, Size: 8, Value: 1
0.014040 [D3] Report[get]: (2 bytes) => 30 03
0.014047 [D1] Path: UPS.PowerSummary.FlowID, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 3
0.014169 [D3] Report[get]: (2 bytes) => 31 02
0.014179 [D1] Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x31, Offset: 0, Size: 8, Value: 2
0.014308 [D3] Report[get]: (2 bytes) => 32 01
0.014325 [D1] Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x32, Offset: 0, Size: 8, Value: 1
0.014467 [D3] Report[get]: (2 bytes) => 33 64
0.014478 [D1] Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8, Value: 100
0.014649 [D3] Report[get]: (2 bytes) => 34 64
0.014663 [D1] Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
0.014819 [D3] Report[get]: (2 bytes) => 35 01
0.014826 [D1] Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, ReportID: 0x35, Offset: 0, Size: 8, Value: 1
0.014957 [D3] Report[get]: (2 bytes) => 3e 01
0.014966 [D1] Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, ReportID: 0x3e, Offset: 0, Size: 8, Value: 1
0.015131 [D3] Report[get]: (2 bytes) => 36 64
0.015141 [D1] Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 100
0.015158 [D3] Report[buf]: (2 bytes) => 36 64
0.015176 [D1] Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x36, Offset: 0, Size: 8, Value: 100
0.015300 [D3] Report[get]: (3 bytes) => 37 f7 45
0.015308 [D1] Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x37, Offset: 0, Size: 16, Value: 17911
0.015361 [D3] Report[buf]: (3 bytes) => 37 f7 45
0.015372 [D1] Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x37, Offset: 0, Size: 16, Value: 17911
0.015508 [D3] Report[get]: (3 bytes) => 38 64 00
0.015515 [D1] Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, ReportID: 0x38, Offset: 0, Size: 16, Value: 100
0.015685 [D3] Report[get]: (2 bytes) => 39 12
0.015693 [D1] Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x39, Offset: 0, Size: 8, Value: 18
0.015868 [D3] Report[get]: (2 bytes) => 3a 00
0.015876 [D1] Path: UPS.PowerSummary.PercentLoad, Type: Feature, ReportID: 0x3a, Offset: 0, Size: 8, Value: 0
0.016048 [D3] Report[get]: (3 bytes) => 3b ff ff
0.016056 [D1] Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x3b, Offset: 0, Size: 16, Value: -1
0.016182 [D3] Report[get]: (3 bytes) => 3c 07 01
0.016189 [D1] Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x3c, Offset: 0, Size: 16, Value: 26.3
0.016311 [D3] Report[get]: (3 bytes) => 3d 41 80
0.016319 [D1] Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x3d, Offset: 0, Size: 1, Value: 1
0.016327 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016336 [D1] Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x3d, Offset: 1, Size: 1, Value: 0
0.016344 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016350 [D1] Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x3d, Offset: 2, Size: 1, Value: 0
0.016354 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016363 [D1] Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x3d, Offset: 3, Size: 1, Value: 0
0.016369 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016377 [D1] Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x3d, Offset: 4, Size: 1, Value: 0
0.016384 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016390 [D1] Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x3d, Offset: 5, Size: 1, Value: 0
0.016397 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016403 [D1] Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x3d, Offset: 6, Size: 1, Value: 1
0.016409 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016414 [D1] Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x3d, Offset: 7, Size: 1, Value: 0
0.016419 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016426 [D1] Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x3d, Offset: 8, Size: 1, Value: 0
0.016432 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016439 [D1] Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x3d, Offset: 9, Size: 1, Value: 0
0.016447 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016456 [D1] Path: UPS.PowerSummary.PresentStatus.Boost, Type: Feature, ReportID: 0x3d, Offset: 10, Size: 1, Value: 0
0.016463 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016469 [D1] Path: UPS.PowerSummary.PresentStatus.Undefined, Type: Feature, ReportID: 0x3d, Offset: 11, Size: 1, Value: 0
0.016476 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016482 [D1] Path: UPS.PowerSummary.PresentStatus.Undefined, Type: Feature, ReportID: 0x3d, Offset: 12, Size: 1, Value: 0
0.016488 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016495 [D1] Path: UPS.PowerSummary.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x3d, Offset: 13, Size: 1, Value: 0
0.016501 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016507 [D1] Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x3d, Offset: 14, Size: 1, Value: 0
0.016512 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016520 [D1] Path: UPS.PowerSummary.PresentStatus.Good, Type: Feature, ReportID: 0x3d, Offset: 15, Size: 1, Value: 1
0.016526 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016535 [D1] Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x3d, Offset: 0, Size: 1, Value: 1
0.016542 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016550 [D1] Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x3d, Offset: 1, Size: 1, Value: 0
0.016557 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016563 [D1] Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x3d, Offset: 2, Size: 1, Value: 0
0.016571 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016577 [D1] Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x3d, Offset: 3, Size: 1, Value: 0
0.016584 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016591 [D1] Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, ReportID: 0x3d, Offset: 4, Size: 1, Value: 0
0.016599 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016605 [D1] Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x3d, Offset: 5, Size: 1, Value: 0
0.016613 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016619 [D1] Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Input, ReportID: 0x3d, Offset: 6, Size: 1, Value: 1
0.016624 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016632 [D1] Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, ReportID: 0x3d, Offset: 7, Size: 1, Value: 0
0.016639 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016646 [D1] Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x3d, Offset: 8, Size: 1, Value: 0
0.016653 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016658 [D1] Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x3d, Offset: 9, Size: 1, Value: 0
0.016664 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016669 [D1] Path: UPS.PowerSummary.PresentStatus.Boost, Type: Input, ReportID: 0x3d, Offset: 10, Size: 1, Value: 0
0.016675 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016681 [D1] Path: UPS.PowerSummary.PresentStatus.Undefined, Type: Input, ReportID: 0x3d, Offset: 11, Size: 1, Value: 0
0.016687 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016695 [D1] Path: UPS.PowerSummary.PresentStatus.Undefined, Type: Input, ReportID: 0x3d, Offset: 12, Size: 1, Value: 0
0.016702 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016710 [D1] Path: UPS.PowerSummary.PresentStatus.AwaitingPower, Type: Input, ReportID: 0x3d, Offset: 13, Size: 1, Value: 0
0.016717 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016725 [D1] Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, ReportID: 0x3d, Offset: 14, Size: 1, Value: 0
0.016732 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.016739 [D1] Path: UPS.PowerSummary.PresentStatus.Good, Type: Input, ReportID: 0x3d, Offset: 15, Size: 1, Value: 1
0.016861 [D3] Report[get]: (3 bytes) => 46 02 00
0.016868 [D1] Path: UPS.EVER1.EVER12, Type: Feature, ReportID: 0x46, Offset: 0, Size: 16, Value: 2
0.016992 [D3] Report[get]: (5 bytes) => 47 0a 10 01 11
0.017000 [D1] Path: UPS.EVER1.ff000024, Type: Feature, ReportID: 0x47, Offset: 0, Size: 16, Value: 4106
0.017008 [D3] Report[buf]: (5 bytes) => 47 0a 10 01 11
0.017013 [D1] Path: UPS.EVER1.ff000025, Type: Feature, ReportID: 0x47, Offset: 16, Size: 16, Value: 4353
0.017136 [D3] Report[get]: (5 bytes) => 48 01 01 01 01
0.017144 [D1] Path: UPS.EVER1.ff000026, Type: Feature, ReportID: 0x48, Offset: 0, Size: 16, Value: 257
0.017151 [D3] Report[buf]: (5 bytes) => 48 01 01 01 01
0.017158 [D1] Path: UPS.EVER1.ff000027, Type: Feature, ReportID: 0x48, Offset: 16, Size: 16, Value: 257
0.017280 [D3] Report[get]: (5 bytes) => 49 01 10 02 10
0.017286 [D1] Path: UPS.EVER1.ff000028, Type: Feature, ReportID: 0x49, Offset: 0, Size: 16, Value: 4097
0.017290 [D3] Report[buf]: (5 bytes) => 49 01 10 02 10
0.017295 [D1] Path: UPS.EVER1.ff000029, Type: Feature, ReportID: 0x49, Offset: 16, Size: 16, Value: 4098
0.017434 [D3] Report[get]: (3 bytes) => 4a 04 00
0.017443 [D1] Path: UPS.EVER1.EVER97.EVER98, Type: Feature, ReportID: 0x4a, Offset: 0, Size: 1, Value: 0
0.017450 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017457 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 1, Size: 1, Value: 0
0.017462 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017468 [D1] Path: UPS.EVER1.EVER97.EVER100, Type: Feature, ReportID: 0x4a, Offset: 2, Size: 1, Value: 1
0.017476 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017482 [D1] Path: UPS.EVER1.EVER97.EVER101, Type: Feature, ReportID: 0x4a, Offset: 3, Size: 1, Value: 0
0.017488 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017495 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 4, Size: 1, Value: 0
0.017500 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017508 [D1] Path: UPS.EVER1.EVER97.EVER103, Type: Feature, ReportID: 0x4a, Offset: 5, Size: 1, Value: 0
0.017513 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017521 [D1] Path: UPS.EVER1.EVER97.EVER104, Type: Feature, ReportID: 0x4a, Offset: 6, Size: 1, Value: 0
0.017528 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017535 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 7, Size: 1, Value: 0
0.017542 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017550 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 8, Size: 1, Value: 0
0.017557 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017565 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 9, Size: 1, Value: 0
0.017572 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017579 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 10, Size: 1, Value: 0
0.017585 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017590 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 11, Size: 1, Value: 0
0.017598 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017603 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 12, Size: 1, Value: 0
0.017611 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017619 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 13, Size: 1, Value: 0
0.017624 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017630 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 14, Size: 1, Value: 0
0.017635 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.017641 [D1] Path: UPS.EVER1.EVER97.EVER2, Type: Feature, ReportID: 0x4a, Offset: 15, Size: 1, Value: 0
0.017796 [D3] Report[get]: (3 bytes) => 4b 00 00
0.017802 [D1] Path: UPS.EVER1.EVER18.EVER19, Type: Feature, ReportID: 0x4b, Offset: 0, Size: 1, Value: 0
0.017806 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017811 [D1] Path: UPS.EVER1.EVER18.EVER20, Type: Feature, ReportID: 0x4b, Offset: 1, Size: 1, Value: 0
0.017815 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017819 [D1] Path: UPS.EVER1.EVER18.EVER21, Type: Feature, ReportID: 0x4b, Offset: 2, Size: 1, Value: 0
0.017823 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017828 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 3, Size: 1, Value: 0
0.017833 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017843 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 4, Size: 1, Value: 0
0.017847 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017852 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 5, Size: 1, Value: 0
0.017859 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017866 [D1] Path: UPS.EVER1.EVER18.EVER25, Type: Feature, ReportID: 0x4b, Offset: 6, Size: 1, Value: 0
0.017870 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017878 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 7, Size: 1, Value: 0
0.017886 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017892 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 8, Size: 1, Value: 0
0.017897 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017904 [D1] Path: UPS.EVER1.EVER18.EVER28, Type: Feature, ReportID: 0x4b, Offset: 9, Size: 1, Value: 0
0.017909 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017917 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 10, Size: 1, Value: 0
0.017924 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017930 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 11, Size: 1, Value: 0
0.017936 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017941 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 12, Size: 1, Value: 0
0.017947 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017954 [D1] Path: UPS.EVER1.EVER18.ff00002a, Type: Feature, ReportID: 0x4b, Offset: 13, Size: 1, Value: 0
0.017962 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017968 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 14, Size: 1, Value: 0
0.017974 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.017980 [D1] Path: UPS.EVER1.EVER18.EVER2, Type: Feature, ReportID: 0x4b, Offset: 15, Size: 1, Value: 0
0.018106 [D3] Report[get]: (3 bytes) => 4c 00 00
0.018113 [D1] Path: UPS.EVER1.EVER32.EVER33, Type: Feature, ReportID: 0x4c, Offset: 0, Size: 1, Value: 0
0.018120 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018126 [D1] Path: UPS.EVER1.EVER32.EVER34, Type: Feature, ReportID: 0x4c, Offset: 1, Size: 1, Value: 0
0.018131 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018138 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 2, Size: 1, Value: 0
0.018144 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018152 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 3, Size: 1, Value: 0
0.018159 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018166 [D1] Path: UPS.EVER1.EVER32.EVER37, Type: Feature, ReportID: 0x4c, Offset: 4, Size: 1, Value: 0
0.018174 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018179 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 5, Size: 1, Value: 0
0.018185 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018192 [D1] Path: UPS.EVER1.EVER32.EVER39, Type: Feature, ReportID: 0x4c, Offset: 6, Size: 1, Value: 0
0.018196 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018204 [D1] Path: UPS.EVER1.EVER32.EVER40, Type: Feature, ReportID: 0x4c, Offset: 7, Size: 1, Value: 0
0.018211 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018219 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 8, Size: 1, Value: 0
0.018226 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018233 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 9, Size: 1, Value: 0
0.018238 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018244 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 10, Size: 1, Value: 0
0.018248 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018254 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 11, Size: 1, Value: 0
0.018262 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018267 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 12, Size: 1, Value: 0
0.018275 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018280 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 13, Size: 1, Value: 0
0.018286 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018292 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 14, Size: 1, Value: 0
0.018296 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.018304 [D1] Path: UPS.EVER1.EVER32.EVER2, Type: Feature, ReportID: 0x4c, Offset: 15, Size: 1, Value: 0
0.018514 [D3] Report[get]: (3 bytes) => 4f 00 00
0.018521 [D1] Path: UPS.EVER1.EVER44, Type: Feature, ReportID: 0x4f, Offset: 0, Size: 16, Value: 0
0.018676 [D3] Report[get]: (2 bytes) => 54 01
0.018683 [D1] Path: UPS.EVER1.EVER49.EVER53, Type: Feature, ReportID: 0x54, Offset: 0, Size: 1, Value: 1
0.018689 [D3] Report[buf]: (2 bytes) => 54 01
0.018694 [D1] Path: UPS.EVER1.EVER49.EVER2, Type: Feature, ReportID: 0x54, Offset: 1, Size: 1, Value: 0
0.018699 [D3] Report[buf]: (2 bytes) => 54 01
0.018704 [D1] Path: UPS.EVER1.EVER49.EVER2, Type: Feature, ReportID: 0x54, Offset: 2, Size: 1, Value: 0
0.018709 [D3] Report[buf]: (2 bytes) => 54 01
0.018718 [D1] Path: UPS.EVER1.EVER49.EVER2, Type: Feature, ReportID: 0x54, Offset: 3, Size: 1, Value: 0
0.018724 [D3] Report[buf]: (2 bytes) => 54 01
0.018728 [D1] Path: UPS.EVER1.EVER49.EVER2, Type: Feature, ReportID: 0x54, Offset: 4, Size: 1, Value: 0
0.018734 [D3] Report[buf]: (2 bytes) => 54 01
0.018741 [D1] Path: UPS.EVER1.EVER49.EVER2, Type: Feature, ReportID: 0x54, Offset: 5, Size: 1, Value: 0
0.018747 [D3] Report[buf]: (2 bytes) => 54 01
0.018754 [D1] Path: UPS.EVER1.EVER49.EVER2, Type: Feature, ReportID: 0x54, Offset: 6, Size: 1, Value: 0
0.018759 [D3] Report[buf]: (2 bytes) => 54 01
0.018766 [D1] Path: UPS.EVER1.EVER49.EVER2, Type: Feature, ReportID: 0x54, Offset: 7, Size: 1, Value: 0
0.018921 [D3] Report[get]: (3 bytes) => 55 e6 00
0.018929 [D1] Path: UPS.EVER1.EVER54, Type: Feature, ReportID: 0x55, Offset: 0, Size: 16, Value: 230
0.019055 [D3] Report[get]: (3 bytes) => 56 b8 00
0.019064 [D1] Path: UPS.EVER1.ff000098, Type: Feature, ReportID: 0x56, Offset: 0, Size: 16, Value: 184
0.019186 [D3] Report[get]: (3 bytes) => 57 fd 00
0.019192 [D1] Path: UPS.EVER1.ff000099, Type: Feature, ReportID: 0x57, Offset: 0, Size: 16, Value: 253
0.019310 [D3] Report[get]: (3 bytes) => 58 2d 00
0.019316 [D1] Path: UPS.EVER1.EVER57, Type: Feature, ReportID: 0x58, Offset: 0, Size: 16, Value: 4.5
0.019439 [D3] Report[get]: (3 bytes) => 59 37 00
0.019445 [D1] Path: UPS.EVER1.EVER58, Type: Feature, ReportID: 0x59, Offset: 0, Size: 16, Value: 5.5
0.019570 [D3] Report[get]: (3 bytes) => 5a c8 00
0.019578 [D1] Path: UPS.EVER1.ff00009a, Type: Feature, ReportID: 0x5a, Offset: 0, Size: 16, Value: 2e-12
0.019701 [D3] Report[get]: (3 bytes) => c8 1a 00
0.019708 [D1] Path: UPS.EVER1.EVER62, Type: Feature, ReportID: 0xc8, Offset: 0, Size: 16, Value: 26
0.019833 [D3] Report[get]: (3 bytes) => ca 01 00
0.019839 [D1] Path: UPS.EVER1.EVER64, Type: Feature, ReportID: 0xca, Offset: 0, Size: 16, Value: 1
0.019963 [D3] Report[get]: (3 bytes) => cb 01 00
0.019971 [D1] Path: UPS.EVER1.EVER65, Type: Feature, ReportID: 0xcb, Offset: 0, Size: 16, Value: 1
0.020093 [D3] Report[get]: (3 bytes) => cc 02 00
0.020099 [D1] Path: UPS.EVER1.EVER66, Type: Feature, ReportID: 0xcc, Offset: 0, Size: 16, Value: 2
0.020293 [D3] Report[get]: (3 bytes) => cd 09 00
0.020300 [D1] Path: UPS.EVER1.EVER67, Type: Feature, ReportID: 0xcd, Offset: 0, Size: 16, Value: 9
0.020435 [D3] Report[get]: (3 bytes) => cf be 00
0.020447 [D1] Path: UPS.EVER1.EVER69, Type: Feature, ReportID: 0xcf, Offset: 0, Size: 16, Value: 190
0.020574 [D3] Report[get]: (3 bytes) => d0 c1 00
0.020581 [D1] Path: UPS.EVER1.EVER70, Type: Feature, ReportID: 0xd0, Offset: 0, Size: 16, Value: 193
0.020705 [D3] Report[get]: (3 bytes) => d1 00 00
0.020713 [D1] Path: UPS.EVER1.EVER71, Type: Feature, ReportID: 0xd1, Offset: 0, Size: 16, Value: 0
0.020897 [D3] Report[get]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.020909 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.020917 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 0, Size: 16, Value: 0
0.020928 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.020967 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.020979 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 16, Size: 16, Value: 65535
0.020986 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.020992 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021034 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 32, Size: 16, Value: 220
0.021044 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021081 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021092 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 48, Size: 16, Value: 240
0.021099 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021142 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021153 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 64, Size: 16, Value: 240
0.021163 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021200 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021211 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 80, Size: 16, Value: 264
0.021218 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021228 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021266 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 96, Size: 16, Value: 168
0.021276 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021288 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021325 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 112, Size: 16, Value: 210
0.021337 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021346 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021384 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 128, Size: 16, Value: 184
0.021395 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021405 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021442 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 144, Size: 16, Value: 210
0.021453 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021463 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021484 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 160, Size: 16, Value: 45
0.021516 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021526 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021563 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 176, Size: 16, Value: 49
0.021574 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021584 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021620 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 192, Size: 16, Value: 51
0.021631 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021641 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021678 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 208, Size: 16, Value: 55
0.021689 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021698 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021735 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 224, Size: 16, Value: 0
0.021746 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021755 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021792 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 240, Size: 16, Value: 65535
0.021803 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021813 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021849 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 0, Size: 16, Value: 0
0.021860 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021870 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021906 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 16, Size: 16, Value: 65535
0.021917 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021927 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.021964 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 32, Size: 16, Value: 220
0.021975 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.021985 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022022 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 48, Size: 16, Value: 240
0.022032 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022042 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022079 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 64, Size: 16, Value: 240
0.022090 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022100 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022136 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 80, Size: 16, Value: 264
0.022147 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022157 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022194 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 96, Size: 16, Value: 168
0.022205 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022214 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022251 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 112, Size: 16, Value: 210
0.022262 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022272 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022309 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 128, Size: 16, Value: 184
0.022320 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022327 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022333 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 144, Size: 16, Value: 210
0.022376 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022384 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022405 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 160, Size: 16, Value: 45
0.022450 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022462 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022468 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 176, Size: 16, Value: 49
0.022475 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022481 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022486 [D1] Path: UPS.EVER1.ff00009b, Type: Feature, ReportID: 0xd2, Offset: 192, Size: 16, Value: 51
0.022491 [D3] Report[buf]: (33 bytes) => d2 00 00 ff ff dc 00 f0 00 f0 00 08 01 a8 00 d2
0.022497 [D3] 00 b8 00 d2 00 2d 00 31 00 33 00 37 00 00 00 ff ff
0.022504 [D1] Path: UPS.EVER1.ff00009c, Type: Feature, ReportID: 0xd2, Offset: 208, Size: 16, Value: 55
0.022679 [D3] Report[get]: (33 bytes) => fd cc 0f 03 00 03 00 00 00 00 00 00 00 00 00 00
0.022690 [D3] 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0.022700 [D1] Path: UPS.ff00009d.ff00009e, Type: Feature, ReportID: 0xfd, Offset: 0, Size: 8, Value: 204
0.022874 [D3] Report[get]: (33 bytes) => fe d3 00 d3 00 8c 00 76 16 bb 00 00 00 04 00 00
0.022883 [D3] 00 00 00 0f 00 01 00 40 38 00 00 00 00 00 00 00 00
0.022890 [D1] Path: UPS.ff00009f.ff0000a0, Type: Feature, ReportID: 0xfe, Offset: 0, Size: 8, Value: 211
0.023025 [D3] Report[get]: (12 bytes) => ff 00 00 00 00 00 00 00 00 00 00 00
0.023034 [D1] Path: UPS.ff00009f.ff0000a0, Type: Feature, ReportID: 0xff, Offset: 0, Size: 8, Value: 0
0.023047 [D2] Report descriptor retrieved (Reportlen = 1591)
0.023051 [D2] Found HID device
0.023058 [D1] Detected a UPS: EVER/ECO PRO AVR CDS
0.023072 [D3] Report[buf]: (2 bytes) => 11 01
0.023078 [D2] Path: UPS.BatterySystem.Battery.BatteryID, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 1
0.023088 [D3] Report[buf]: (2 bytes) => 0b 01
0.023094 [D2] Path: UPS.BatterySystem.BatterySystemID, Type: Feature, ReportID: 0x0b, Offset: 0, Size: 8, Value: 1
0.023106 [D3] Report[buf]: (2 bytes) => 0e 01
0.023112 [D2] Path: UPS.BatterySystem.Charger.ChargerID, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 1
0.023121 [D3] Report[buf]: (2 bytes) => 0d 01
0.023125 [D2] Path: UPS.BatterySystem.Input.FlowID, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 8, Value: 1
0.023134 [D3] Report[buf]: (2 bytes) => 0c 01
0.023140 [D2] Path: UPS.BatterySystem.Input.InputID, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 1
0.023151 [D3] Report[buf]: (2 bytes) => 10 02
0.023176 [D2] Path: UPS.BatterySystem.Output.FlowID, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 2
0.023207 [D3] Report[buf]: (2 bytes) => 0f 01
0.023213 [D2] Path: UPS.BatterySystem.Output.OutputID, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 1
0.023260 [D3] Report[buf]: (3 bytes) => 4f 00 00
0.023267 [D2] Path: UPS.EVER1.EVER44, Type: Feature, ReportID: 0x4f, Offset: 0, Size: 16, Value: 0
0.023292 [D3] Report[buf]: (2 bytes) => 54 01
0.023298 [D2] Path: UPS.EVER1.EVER49.EVER53, Type: Feature, ReportID: 0x54, Offset: 0, Size: 1, Value: 1
0.023306 [D3] Report[buf]: (3 bytes) => 55 e6 00
0.023318 [D2] Path: UPS.EVER1.EVER54, Type: Feature, ReportID: 0x55, Offset: 0, Size: 16, Value: 230
0.023344 [D3] Report[buf]: (3 bytes) => c8 1a 00
0.023348 [D2] Path: UPS.EVER1.EVER62, Type: Feature, ReportID: 0xc8, Offset: 0, Size: 16, Value: 26
0.023371 [D3] Report[buf]: (3 bytes) => ca 01 00
0.023381 [D2] Path: UPS.EVER1.EVER64, Type: Feature, ReportID: 0xca, Offset: 0, Size: 16, Value: 1
0.023390 [D3] Report[buf]: (3 bytes) => cb 01 00
0.023395 [D2] Path: UPS.EVER1.EVER65, Type: Feature, ReportID: 0xcb, Offset: 0, Size: 16, Value: 1
0.023404 [D3] Report[buf]: (3 bytes) => cc 02 00
0.023409 [D2] Path: UPS.EVER1.EVER66, Type: Feature, ReportID: 0xcc, Offset: 0, Size: 16, Value: 2
0.023421 [D3] Report[buf]: (3 bytes) => cd 09 00
0.023425 [D2] Path: UPS.EVER1.EVER67, Type: Feature, ReportID: 0xcd, Offset: 0, Size: 16, Value: 9
0.023437 [D3] Report[buf]: (3 bytes) => cf be 00
0.023442 [D2] Path: UPS.EVER1.EVER69, Type: Feature, ReportID: 0xcf, Offset: 0, Size: 16, Value: 190
0.023450 [D3] Report[buf]: (3 bytes) => d0 c1 00
0.023456 [D2] Path: UPS.EVER1.EVER70, Type: Feature, ReportID: 0xd0, Offset: 0, Size: 16, Value: 193
0.023466 [D3] Report[buf]: (3 bytes) => d1 00 00
0.023471 [D2] Path: UPS.EVER1.EVER71, Type: Feature, ReportID: 0xd1, Offset: 0, Size: 16, Value: 0
0.023528 [D3] Report[buf]: (3 bytes) => 0a 8a 02
0.023533 [D2] Path: UPS.Flow.ConfigActivePower, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 16, Value: 650
0.023543 [D3] Report[buf]: (3 bytes) => 09 e8 03
0.023548 [D2] Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 1000
0.023561 [D3] Report[buf]: (2 bytes) => 03 32
0.023567 [D2] Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 50
0.023578 [D3] Report[buf]: (3 bytes) => 02 e6 00
0.023584 [D2] Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x02, Offset: 0, Size: 16, Value: 230
0.023594 [D3] Report[buf]: (2 bytes) => 01 01
0.023601 [D2] Path: UPS.Flow.FlowID, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
0.023612 [D3] Report[buf]: (2 bytes) => 25 01
0.023619 [D2] Path: UPS.OutletSystem.Outlet.OutletID, Type: Feature, ReportID: 0x25, Offset: 0, Size: 8, Value: 1
0.023633 [D3] Report[buf]: (2 bytes) => 26 01
0.023639 [D2] Path: UPS.OutletSystem.Outlet.PresentStatus.Present, Type: Feature, ReportID: 0x26, Offset: 0, Size: 1, Value: 1
0.023652 [D3] Report[buf]: (2 bytes) => 26 01
0.023658 [D2] Path: UPS.OutletSystem.Outlet.PresentStatus.Switchable, Type: Feature, ReportID: 0x26, Offset: 1, Size: 1, Value: 0
0.023676 [D3] Report[buf]: (2 bytes) => 26 01
0.023682 [D2] Path: UPS.OutletSystem.Outlet.PresentStatus.Undefined, Type: Feature, ReportID: 0x26, Offset: 2, Size: 1, Value: 0
0.023707 [D3] Report[buf]: (2 bytes) => 24 01
0.023716 [D2] Path: UPS.OutletSystem.OutletSystemID, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1
0.023755 [D3] Report[buf]: (2 bytes) => 14 01
0.023767 [D2] Path: UPS.PowerConverter.Input.FlowID, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 1
0.023778 [D3] Report[buf]: (3 bytes) => 18 f7 01
0.023786 [D2] Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 50.3
0.023799 [D3] Report[buf]: (2 bytes) => 13 01
0.023805 [D2] Path: UPS.PowerConverter.Input.InputID, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1
0.023816 [D3] Report[buf]: (3 bytes) => 15 de 00
0.023822 [D2] Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 222
0.023836 [D3] Report[buf]: (3 bytes) => 23 00 00
0.023841 [D2] Path: UPS.PowerConverter.Output.ActivePower, Type: Feature, ReportID: 0x23, Offset: 0, Size: 16, Value: 0
0.023860 [D3] Report[buf]: (3 bytes) => 22 00 00
0.023877 [D2] Path: UPS.PowerConverter.Output.ApparentPower, Type: Feature, ReportID: 0x22, Offset: 0, Size: 16, Value: 0
0.023906 [D3] Report[buf]: (3 bytes) => 20 00 00
0.023927 [D2] Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 0
0.023947 [D3] Report[buf]: (2 bytes) => 1d 03
0.023952 [D2] Path: UPS.PowerConverter.Output.FlowID, Type: Feature, ReportID: 0x1d, Offset: 0, Size: 8, Value: 3
0.023963 [D3] Report[buf]: (3 bytes) => 21 f7 01
0.023969 [D2] Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x21, Offset: 0, Size: 16, Value: 50.3
0.023982 [D3] Report[buf]: (2 bytes) => 1c 01
0.023987 [D2] Path: UPS.PowerConverter.Output.OutputID, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 8, Value: 1
0.024005 [D3] Report[buf]: (2 bytes) => 1e 00
0.024022 [D2] Path: UPS.PowerConverter.Output.PercentLoad, Type: Feature, ReportID: 0x1e, Offset: 0, Size: 8, Value: 0
0.024053 [D3] Report[buf]: (2 bytes) => 12 01
0.024074 [D2] Path: UPS.PowerConverter.PowerConverterID, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 1
0.024085 [D3] Report[buf]: (2 bytes) => 35 01
0.024091 [D2] Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, ReportID: 0x35, Offset: 0, Size: 8, Value: 1
0.024105 [D3] Report[buf]: (2 bytes) => 3e 01
0.024109 [D2] Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, ReportID: 0x3e, Offset: 0, Size: 8, Value: 1
0.024122 [D3] Report[buf]: (2 bytes) => 31 02
0.024127 [D2] Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x31, Offset: 0, Size: 8, Value: 2
0.024146 [D3] Report[buf]: (2 bytes) => 33 64
0.024153 [D2] Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8, Value: 100
0.024164 [D3] Report[buf]: (2 bytes) => 30 03
0.024170 [D2] Path: UPS.PowerSummary.FlowID, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 3
0.024183 [D3] Report[buf]: (2 bytes) => 39 12
0.024188 [D2] Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x39, Offset: 0, Size: 8, Value: 18
0.024206 [D3] Report[buf]: (2 bytes) => 32 01
0.024211 [D2] Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x32, Offset: 0, Size: 8, Value: 1
0.024230 [D3] Report[buf]: (2 bytes) => 36 64
0.024252 [D2] Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 100
0.024282 [D3] Report[buf]: (3 bytes) => 38 64 00
0.024299 [D2] Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, ReportID: 0x38, Offset: 0, Size: 16, Value: 100
0.024311 [D3] Report[buf]: (3 bytes) => 37 f7 45
0.024317 [D2] Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x37, Offset: 0, Size: 16, Value: 17911
0.024327 [D3] Report[buf]: (3 bytes) => 3c 07 01
0.024333 [D2] Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x3c, Offset: 0, Size: 16, Value: 26.3
0.024345 [D3] Report[buf]: (3 bytes) => 3b ff ff
0.024350 [D2] Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x3b, Offset: 0, Size: 16, Value: -1
0.024363 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.024369 [D2] Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x3d, Offset: 0, Size: 1, Value: 1
0.024382 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.024387 [D2] Path: UPS.PowerSummary.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x3d, Offset: 13, Size: 1, Value: 0
0.024406 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.024423 [D2] Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x3d, Offset: 6, Size: 1, Value: 1
0.024450 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.024472 [D2] Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x3d, Offset: 14, Size: 1, Value: 0
0.024483 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.024490 [D2] Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x3d, Offset: 1, Size: 1, Value: 0
0.024502 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.024508 [D2] Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x3d, Offset: 5, Size: 1, Value: 0
0.024516 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.024521 [D2] Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x3d, Offset: 7, Size: 1, Value: 0
0.024534 [D3] Report[buf]: (3 bytes) => 3d 41 80
0.024538 [D2] Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x3d, Offset: 9, Size: 1, Value: 0
0.024545 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.024549 [D2] Path: UPS.EVER1.EVER18.EVER19, Type: Feature, ReportID: 0x4b, Offset: 0, Size: 1, Value: 0
0.024556 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.024560 [D2] Path: UPS.EVER1.EVER18.EVER20, Type: Feature, ReportID: 0x4b, Offset: 1, Size: 1, Value: 0
0.024566 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.024570 [D2] Path: UPS.EVER1.EVER18.EVER21, Type: Feature, ReportID: 0x4b, Offset: 2, Size: 1, Value: 0
0.024579 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.024583 [D2] Path: UPS.EVER1.EVER18.EVER25, Type: Feature, ReportID: 0x4b, Offset: 6, Size: 1, Value: 0
0.024589 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.024593 [D2] Path: UPS.EVER1.EVER18.EVER28, Type: Feature, ReportID: 0x4b, Offset: 9, Size: 1, Value: 0
0.024600 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.024604 [D2] Path: UPS.EVER1.EVER32.EVER33, Type: Feature, ReportID: 0x4c, Offset: 0, Size: 1, Value: 0
0.024611 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.024615 [D2] Path: UPS.EVER1.EVER32.EVER40, Type: Feature, ReportID: 0x4c, Offset: 7, Size: 1, Value: 0
0.024626 [D3] Report[buf]: (3 bytes) => 4a 04 00
0.024630 [D2] Path: UPS.EVER1.EVER97.EVER98, Type: Feature, ReportID: 0x4a, Offset: 0, Size: 1, Value: 0
0.024638 [D3] Report[buf]: (3 bytes) => 4b 00 00
0.024643 [D2] Path: UPS.EVER1.EVER18.EVER28, Type: Feature, ReportID: 0x4b, Offset: 9, Size: 1, Value: 0
0.024651 [D3] Report[buf]: (3 bytes) => 4c 00 00
0.024655 [D2] Path: UPS.EVER1.EVER32.EVER33, Type: Feature, ReportID: 0x4c, Offset: 0, Size: 1, Value: 0
0.024663 [D3] Report[buf]: (3 bytes) => 3b ff ff
0.024668 [D2] Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x3b, Offset: 0, Size: 16, Value: -1
0.024673 [D3] Adding command 'load.off.delay' using Path 'UPS.PowerSummary.DelayBeforeShutdown'
0.024681 [D3] Report[buf]: (3 bytes) => 3b ff ff
0.024685 [D2] Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x3b, Offset: 0, Size: 16, Value: -1
0.024689 [D3] Adding command 'shutdown.return' using Path 'UPS.PowerSummary.DelayBeforeShutdown'
0.024696 [D2] find_nut_info: unknown info type: load.on.delay
0.024702 [D2] find_nut_info: unknown info type: load.on.delay
0.024706 Initiating UPS shutdown
0.024710 [D1] upsdrv_shutdown...
0.024714 [D1] instcmd(shutdown.return, [NULL])
0.024719 [D3] instcmd: using Path 'UPS.PowerSummary.DelayBeforeShutdown'
0.024845 [D3] Report[set]: (3 bytes) => 3b 14 00
0.024850 [D3] instcmd: SUCCEED
0.024855 [D1] upsdrv_cleanup...
To me it looks like everything is ok on the OS side ... is that a problem with UPS itself ? What can I check more ?