I left this line uncommented in powercom-hid.c for battery voltage:
{ "battery.voltage", 0, 0, "UPS.Battery.Voltage", NULL, "%.2f", 0, NULL },
and got some data different from the input voltage values
The Powercom support staff gave the following response to my question:
Dear Alex,
First of all , thank you for purchasing PCM MRT-3000 ups.
Regarding of your question, see our reply in below
==> Please take your data with below rules :
• DEX : 5378
• HEX : 1502 (Low : 15 / High : 02)
• Battery one cell voltage : [High + (Low/100)] : 2.21
• Battery voltage : 2.21 * 6 * 6 = 79.56 Vol (1 package with 6 cells / MRT has 6 packages)
Best regards
Sandy Chang, Powercom Taiwan HQ
-----Original Message-----
From: Alex Rydzewski [mailto:arydzewski at elyland.net]
Sent: Thursday, January 12, 2023 5:47 PM
To:pcm.eu at upspowercom.com
Subject: MRT-3000 USB battery.voltage
Hello!
I have the MRT-3000 UPS and try to get real battery voltage through USB.
USB protocol reference has specify for battery.voltage:
report id | Usage | Usage Name | Data Access | Length
26 0X8430 Battery Voltage R/O 3 Byte
But I get for this position the next data:
0.544555 [D4] Entering libusb_get_report
0.549533 [D3] Report[get]: (3 bytes) => 1a 02 15
0.549550 [D5] PhyMax = 0, PhyMin = 0, LogMax = 9216, LogMin = 2304
0.549561 [D5] Unit = 00000000, UnitExp = 0
0.549569 [D5] Exponent = 0
0.549576 [D5] hid_lookup_path: 00840004 -> UPS
0.549583 [D5] hid_lookup_path: 00840012 -> Battery
0.549591 [D5] hid_lookup_path: 00840030 -> Voltage
0.549603 [D1] Path: UPS.Battery.Voltage, Type: Feature,
ReportID: 0x1a, Offset: 0, Size: 16, Value: 5378
Suggest me, please, how I can interpret the battery.voltage value "5378? How I can get real battery.voltage data?
Perhaps it is possible implement this algorithm to "nut" project for a
UPS like this?
On 10.01.23 19:14, Jim Klimov wrote:
> I suppose that should have read "correct battery.voltage" ;)
>
> Not sure really - this is the standard endpoint for that info, so
> firmware is broken for USB HID power device support.
>
> If you start the driver with higher debug verbosity, it prints the
> reports from USB. If you can decipher those (online tools exist but I
> don't have a link handy), maybe some other field (possibly with an
> untranslated hex name) conveys data that looks like what you need.
>
> Jim
>
> On Tue, Jan 10, 2023, 18:09 Alex Rydzewski <arydzewski at elyland.net> wrote:
>
> Thank You for your attention, Jim!
> I compiled and ran the 2.8.0 version with this part uncomment
> * { "battery.voltage", 0, 0, "UPS.PowerSummary.Voltage", NULL,
> "%.2f", 0, NULL },
> * { "battery.voltage", 0, 0, "UPS.Battery.Voltage", NULL,
> "%.2f", 0, NULL },
> * { "battery.voltage.nominal", 0, 0,
> "UPS.PowerSummary.ConfigVoltage", NULL, "%.0f", HU_FLAG_STATIC,
> NULL },
> * { "battery.voltage.nominal", 0, 0,
> "UPS.Battery.ConfigVoltage", NULL, "%.0f", HU_FLAG_STATIC, NULL },
> from powercom-hid.c, and it is so, it is duplicates for
> output.voltage.
>
> Is there anything I can do to find the correct output.voltage?
>
> On 10.01.23 14:12, Jim Klimov wrote:
>> Hello,
>>
>> One thing that pops out in your report is that NUT 2.7.2 is
>> used, which is pretty old now. If you have a chance to install
>> 2.8.0 or newer (custom build of current git master) to confirm if
>> the problem is still there, it could be helpful.
>>
>> Other than that, current source says at
>> https://github.com/networkupstools/nut/blob/1deab1638322e9e64a0cf3200dadc93dbe3a3f41/drivers/powercom-hid.c#L362-L368
>> that "battery.voltage" is served in USB reports, but is not
>> useful (same as output voltage). Nearby, "battery.runtime" and
>> "battery.mfr.date" do come from USB reports, but per
>> https://github.com/networkupstools/nut/issues/1644 the latter was
>> previously wrongly reported as "battery.date" (for replacement).
>> Note that generally fixes are based on user reports about devices
>> which misbehaved; if a vendor has multiple devices with different
>> behaviors (including bug fixes in newer firmwares) it can get
>> messy and need some more elaborate fixes :-\
>>
>> Something in your question does ring a bell - please revise
>> https://github.com/networkupstools/nut/issues?q=label%3APowercom
>> <https://github.com/networkupstools/nut/issues?q=+label%3APowercom>
>> and/or https://github.com/networkupstools/nut/issues?q=powercom
>> to see if that was discussed earlier in more detail.
>>
>> Hope this helps,
>> Jim Klimov
>>
>>
>> On Tue, Jan 10, 2023 at 11:42 AM Alex Rydzewski
>> <arydzewski at elyland.net> wrote:
>>
>> Hello!
>>
>> I have not been able to get the battery.voltage data from the
>> Powercom
>> Macan MRT-3000, although there is data in the log that does
>> not match
>> the value I see on the device's display. Please tell me how I
>> can
>> control this. And please tell me, if possible, how to get the
>> absolute
>> value of the load on this device.
>> Debug log is attached
>>
>> ~ # upsc 004-0D9F-000
>> Init SSL without certificate database
>> battery.charge: 100
>> battery.charge.low: 10
>> battery.charge.warning: 30
>> battery.date: 2014/01/15 I'm not sure that it is
>> right
>> battery.runtime: 800 Is this data from the
>> device or
>> from the driver?
>> battery.type: PbAc
>> battery.voltage.high: 81.60
>> battery.voltage.low: 63.60
>> battery.voltage.nominal: 75.60
>> device.mfr: POWERCOM Co.,LTD
>> device.model: HID UPS Battery
>> device.serial: 004-0D9F-000
>> device.type: ups
>> driver.name <http://driver.name>: usbhid-ups
>> driver.version: 2.7.2
>> driver.version.data: PowerCOM HID 0.4
>> driver.version.internal: 0.38
>> ...
>>
>> --
>> З найкращими побажаннями, Олександр Ридзевський |With best
>> regards, Mr. Alexander Rydzewski, |С наилучшими
>> пожеланиями, Александр Рыдзевский
>> Системний та мережевий інженер, Elyland ltd. |System and
>> Network Engineer at Elyland ltd. |Системный и сетевой
>> инженер, Elyland ltd.
>>
> --
> З найкращими побажаннями, Олександр Ридзевський |With best regards, Mr. Alexander Rydzewski, |С наилучшими пожеланиями, Александр Рыдзевский
> Системний та мережевий інженер, Elyland ltd. |System and Network Engineer at Elyland ltd. |Системный и сетевой инженер, Elyland ltd.
>
--
З найкращими побажаннями, Олександр Ридзевський |With best regards, Mr. Alexander Rydzewski, |С наилучшими пожеланиями, Александр Рыдзевский
Системний та мережевий інженер, Elyland ltd. |System and Network Engineer at Elyland ltd. |Системный и сетевой инженер, Elyland ltd.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20230113/898fa250/attachment.htm>
More information about the Nut-upsuser
mailing list