I suppose, this approach may be apply to some other data from that UPS.
I could check another values and ask powercom support for other data
items to explain interpretation, if it will help.
On 13.01.23 14:22, Greg Troxel wrote:
> That makes sense to me. The field needs to be split into bytes. The
> low byte is the integer part of voltags, and the high part is units of
> 10 mV. And this is per cell.
>
> Probably the unit is measuring the total and then dividing by 36. But
> volts per cell will have the same interpretation for varying cell
> counts, so it's a nice representation.
--