[Nut-upsuser] PR to test for users of Qx devices (blazer and nutdrv_qx)
Jim Klimov
jimklimov+nut at gmail.com
Wed Sep 13 21:36:34 BST 2023
Thanks!
So, comparing this with the January report -- there are no substantial
changes in device discovery process and the collected info.
However, the 10K seems to actually report most of the data which we have
to "guesstimate" in other cases.
Hoping somebody else with QX devices would chime in then :)
Jim
On Wed, Sep 13, 2023 at 3:26 PM d tbsky <tbskyd at gmail.com> wrote:
> jim Klimov <jimklimov+nut at gmail.com>
> >
> > Hello all,
> >
> > Had another hard look at the PR for QX device voltage/charge/runtime
> fixes for some broken use-cases (AND hoping to not introduce problems for
> cases that were not broken), and hopefully found and rolled back the change
> which in fact introduced the strangeness found in our winter round of
> tests. Then the year was busy...
> >
> > As before, the context for this is:
> > * issue https://github.com/networkupstools/nut/issues/1279
> > * PR https://github.com/networkupstools/nut/pull/1652
> > * PR source git branch (code to build for tests)
> https://github.com/jimklimov/nut/tree/issue-1279
> > *
> https://github.com/networkupstools/nut/wiki/Building-NUT-for-in%E2%80%90place-upgrades-or-non%E2%80%90disruptive-tests
> suggests how to quickly build and
>
> Hi:
> one of our voltronic ups caught fire last year. so we abandoned
> them and bought APC. now I have only one 10KV ups to test. It's sad
> because I like nutdrv_qx driver. APC microlink is too bad since nut
> doesn't support it. there is only modbus with apcupsd driver.
>
> BTW I saw an APC ups discussion at nut-upsdev about "SRVS1KI"(can
> not reply, not subscribed to that list) . I have that easy-ups series.
> nut can support them well with apcsmart driver. normally we should
> attach it via serial cable. if you attach the ups with usb cable, you
> will see "XR21V1410" which is a usb-serial converter. linux kernel
> 5.15 seems include the driver. or you will need to compile the
> driver(xr_usb_serial_common) yourself and get "/dev/ttyXRUSB0" to use
> as an serial port. I do that because we lost serial cable at a remote
> site and forced to use the usb cable.
>
> > ./nutdrv_qx -a ftups -u root -DDDDDD -d1
> Network UPS Tools - Generic Q* USB/Serial driver 0.35
> (2.8.0-2359-g6c0032e52)
> USB communication driver (libusb 1.0) 0.45
> 0.000000 [D1] Network UPS Tools version 2.8.0-2359-g6c0032e52
> (release/snapshot of 2.8.0.1) built with gcc (GCC) 11.3.1 20221121
> (Red Hat 11.3.1-4) and configured with flags: --enable-Wcolor
> --enable-keep_nut_report_featu
> re --with-all=auto --with-cgi=auto
> --with-serial=auto --with-dev=auto --with-doc=skip
> --with-nut_monitor=auto --with-pynut=auto
> --disable-force-nut-version-header --enable-check-NIT
> --enable-maintainer-mode
> 0.000011 [D1] debug level is '6'
> 0.000014 [D5] send_to_all: SETINFO driver.debug "6"
> 0.000018 [D5] send_to_all: SETFLAGS driver.debug RW NUMBER
> 0.000815 [D1] Succeeded to become_user(root): now UID=0 GID=0
> 0.000822 [D5] send_to_all: SETINFO device.type "ups"
> 0.000825 [D5] send_to_all: SETINFO driver.state "init.device"
> 0.000827 [D1] upsdrv_initups...
> 0.003147 [D2] Checking device 1 of 11 (8087/8000)
> 0.057855 [D2] - VendorID: 8087
> 0.057861 [D2] - ProductID: 8000
> 0.057862 [D2] - Manufacturer: unknown
> 0.057864 [D2] - Product: unknown
> 0.057865 [D2] - Serial Number: unknown
> 0.057867 [D2] - Bus: 002
> 0.057868 [D2] - Device: 002
> 0.057870 [D2] - Device release number: 0005
> 0.057873 [D2] Trying to match device
> 0.057875 [D3] match_function_regex: matching a device...
> 0.057888 [D2] Device does not match - skipping
> 0.071830 [D2] Checking device 2 of 11 (1D6B/0002)
> 0.078881 [D2] - VendorID: 1d6b
> 0.078885 [D2] - ProductID: 0002
> 0.078887 [D2] - Manufacturer: Linux 5.14.0-162.23.1.el9_1.x86_64
> ehci_hcd
> 0.078888 [D2] - Product: EHCI Host Controller
> 0.078890 [D2] - Serial Number: 0000:00:1d.0
> 0.078891 [D2] - Bus: 002
> 0.078893 [D2] - Device: 001
> 0.078894 [D2] - Device release number: 0514
> 0.078897 [D2] Trying to match device
> 0.078898 [D3] match_function_regex: matching a device...
> 0.078912 [D2] Device does not match - skipping
> 0.091359 [D2] Checking device 3 of 11 (8087/8008)
> 0.145626 [D2] - VendorID: 8087
> 0.145635 [D2] - ProductID: 8008
> 0.145637 [D2] - Manufacturer: unknown
> 0.145638 [D2] - Product: unknown
> 0.145640 [D2] - Serial Number: unknown
> 0.145641 [D2] - Bus: 001
> 0.145643 [D2] - Device: 002
> 0.145645 [D2] - Device release number: 0005
> 0.145648 [D2] Trying to match device
> 0.145661 [D3] match_function_regex: matching a device...
> 0.145664 [D2] Device does not match - skipping
> 0.159837 [D2] Checking device 4 of 11 (1D6B/0002)
> 0.166862 [D2] - VendorID: 1d6b
> 0.166867 [D2] - ProductID: 0002
> 0.166868 [D2] - Manufacturer: Linux 5.14.0-162.23.1.el9_1.x86_64
> ehci_hcd
> 0.166870 [D2] - Product: EHCI Host Controller
> 0.166871 [D2] - Serial Number: 0000:00:1a.0
> 0.166873 [D2] - Bus: 001
> 0.166874 [D2] - Device: 001
> 0.166876 [D2] - Device release number: 0514
> 0.166878 [D2] Trying to match device
> 0.166880 [D3] match_function_regex: matching a device...
> 0.166894 [D2] Device does not match - skipping
> 0.179366 [D2] Checking device 5 of 11 (1D6B/0003)
> 0.200847 [D2] - VendorID: 1d6b
> 0.200851 [D2] - ProductID: 0003
> 0.200853 [D2] - Manufacturer: Linux 5.14.0-162.23.1.el9_1.x86_64
> xhci-hcd
> 0.200854 [D2] - Product: xHCI Host Controller
> 0.200856 [D2] - Serial Number: 0000:00:14.0
> 0.200857 [D2] - Bus: 004
> 0.200858 [D2] - Device: 001
> 0.200860 [D2] - Device release number: 0514
> 0.200862 [D2] Trying to match device
> 0.200864 [D3] match_function_regex: matching a device...
> 0.200877 [D2] Device does not match - skipping
> 0.200931 [D2] Checking device 6 of 11 (9966/0202)
> 0.202237 [D2] - VendorID: 9966
> 0.202254 [D2] - ProductID: 0202
> 0.202256 [D2] - Manufacturer: PSTEK
> 0.202268 [D2] - Product: PSTEK Combo KVM 8/16 V:2.00
> 0.202269 [D2] - Serial Number: unknown
> 0.202271 [D2] - Bus: 003
> 0.202272 [D2] - Device: 003
> 0.202274 [D2] - Device release number: 0000
> 0.202275 [D2] Trying to match device
> 0.202276 [D3] match_function_regex: matching a device...
> 0.202279 [D2] Device does not match - skipping
> 0.202300 [D2] Checking device 7 of 11 (0557/2419)
> 0.202309 [D2] - VendorID: 0557
> 0.202327 [D2] - ProductID: 2419
> 0.202329 [D2] - Manufacturer: unknown
> 0.202331 [D2] - Product: unknown
> 0.202334 [D2] - Serial Number: unknown
> 0.202346 [D2] - Bus: 003
> 0.202348 [D2] - Device: 004
> 0.202350 [D2] - Device release number: 0100
> 0.202353 [D2] Trying to match device
> 0.202365 [D3] match_function_regex: matching a device...
> 0.202367 [D2] Device does not match - skipping
> 0.202371 [D2] Checking device 8 of 11 (0557/7000)
> 0.202377 [D2] - VendorID: 0557
> 0.202379 [D2] - ProductID: 7000
> 0.202380 [D2] - Manufacturer: unknown
> 0.202382 [D2] - Product: unknown
> 0.202384 [D2] - Serial Number: unknown
> 0.202386 [D2] - Bus: 003
> 0.202389 [D2] - Device: 002
> 0.202391 [D2] - Device release number: 0000
> 0.202393 [D2] Trying to match device
> 0.202395 [D3] match_function_regex: matching a device...
> 0.202398 [D2] Device does not match - skipping
> 0.202402 [D2] Checking device 9 of 11 (0665/5161)
> 0.204923 [D1] nut_libusb_open get iManufacturer failed, retrying...
> 0.207280 [D1] nut_libusb_open get iManufacturer failed, retrying...
> 0.209669 [D1] nut_libusb_open get iManufacturer failed, retrying...
> 0.212022 [D1] nut_libusb_open get iProduct failed, retrying...
> 0.214338 [D1] nut_libusb_open get iProduct failed, retrying...
> 0.216830 [D1] nut_libusb_open get iProduct failed, retrying...
> 0.216846 [D2] - VendorID: 0665
> 0.216847 [D2] - ProductID: 5161
> 0.216849 [D2] - Manufacturer: unknown
> 0.216850 [D2] - Product: unknown
> 0.216852 [D2] - Serial Number: unknown
> 0.216864 [D2] - Bus: 003
> 0.216866 [D2] - Device: 006
> 0.216868 [D2] - Device release number: 0001
> 0.216870 [D2] Trying to match device
> 0.216872 [D3] match_function_regex: matching a device...
> 0.216885 [D2] Device matches
> 0.216886 [D2] Reading first configuration descriptor
> 0.216896 [D3] libusb_kernel_driver_active() returned 0: Success
> 0.216926 [D2] Claimed interface 0 successfully
> 0.216929 [D3] nut_usb_set_altinterface: skipped
> libusb_set_interface_alt_setting(udev, 0, 0)
> 0.216946 [D5] send_to_all: SETINFO ups.vendorid "0665"
> 0.216950 [D5] send_to_all: SETINFO ups.productid "5161"
> 0.218318 [D3] send: QGS
> 0.278886 [D5] read [ 0]: (8 bytes) => 28 32 32 31 2e 33 20 35
> 0.310887 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 31 39 2e
> 0.342884 [D5] read [ 16]: (8 bytes) => 35 20 35 39 2e 39 20 30
> 0.382879 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
> 0.414887 [D5] read [ 32]: (8 bytes) => 20 33 36 32 2e 33 20 33
> 0.454888 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
> 0.486869 [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
> 0.518892 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
> 0.558896 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
> 0.574889 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
> 0.574909 [D3] read: (221.3 59.9 219.5 59.9 002.8 007 362.3
> 361.8 272.9 ---.- 022.9 100000000010
> 0.574928 [D5] send_to_all: SETINFO input.voltage "221.3"
> 0.576176 [D3] send: QPI
> 0.622874 [D5] read [ 0]: (8 bytes) => 28 50 49 30 32 0d 00 00
> 0.622880 [D3] read: (PI02
> 0.622937 [D5] send_to_all: SETINFO ups.firmware.aux "P02"
> 0.622940 Using protocol: Voltronic 0.08
> 0.622942 [D5] send_to_all: SETINFO driver.state "init.quiet"
> 0.622956 [D5] send_to_all: SETINFO driver.version
> "2.8.0-2359-g6c0032e52"
> 0.622959 [D5] send_to_all: SETINFO driver.version.internal "0.35"
> 0.622963 [D5] send_to_all: SETINFO driver.name "nutdrv_qx"
> 0.622965 [D5] send_to_all: SETINFO driver.state "init.info"
> 0.622967 [D1] upsdrv_initinfo...
> 0.622980 [D5] send_to_all: SETINFO driver.version.data "Voltronic
> 0.08"
> 0.624104 [D3] send: QRI
> 0.678874 [D5] read [ 0]: (8 bytes) => 28 32 32 30 2e 30 20 30
> 0.718855 [D5] read [ 8]: (8 bytes) => 34 35 20 32 34 30 2e 30
> 0.742898 [D5] read [ 16]: (8 bytes) => 20 36 30 2e 30 0d 00 00
> 0.742910 [D3] read: (220.0 045 240.0 60.0
> 0.742946 [D5] send_to_all: SETINFO output.voltage.nominal "220.0"
> 0.742952 [D5] send_to_all: SETINFO output.current.nominal "45"
> 0.742958 [D5] send_to_all: SETINFO battery.voltage.nominal "240.0"
> 0.742964 [D5] send_to_all: SETINFO output.frequency.nominal "60.0"
> 0.744242 [D3] send: QMD
> 0.798887 [D5] read [ 0]: (8 bytes) => 28 23 23 23 23 23 23 23
> 0.838882 [D5] read [ 8]: (8 bytes) => 23 23 23 23 47 31 30 4b
> 0.870886 [D5] read [ 16]: (8 bytes) => 20 23 23 31 30 30 30 30
> 0.910884 [D5] read [ 24]: (8 bytes) => 20 38 30 20 31 2f 31 20
> 0.942903 [D5] read [ 32]: (8 bytes) => 32 33 30 20 32 33 30 20
> 0.974868 [D5] read [ 40]: (8 bytes) => 32 30 20 31 32 2e 30 0d
> 0.974873 [D3] read: (###########G10K ##10000 80 1/1 230 230 20 12.0
> 0.974882 [D5] send_to_all: SETINFO device.model "G10K"
> 0.974887 [D5] send_to_all: SETINFO ups.power.nominal "10000"
> 0.974893 [D5] send_to_all: SETINFO output.powerfactor "0.8"
> 0.974903 [D5] send_to_all: SETINFO input.phases "1"
> 0.974907 [D5] send_to_all: SETINFO output.phases "1"
> 0.974911 [D5] send_to_all: SETINFO input.voltage.nominal "230.0"
> 0.976111 [D3] send: F
> 1.022870 [D5] read [ 0]: (8 bytes) => 23 32 32 30 2e 30 20 30
> 1.062876 [D5] read [ 8]: (8 bytes) => 34 35 20 32 34 30 2e 30
> 1.086867 [D5] read [ 16]: (8 bytes) => 20 36 30 2e 30 0d 00 00
> 1.086872 [D3] read: #220.0 045 240.0 60.0
> 1.086881 [D5] send_to_all: SETINFO input.current.nominal "45.0"
> 1.086901 [D5] send_to_all: SETINFO input.frequency.nominal "60.0"
> 1.088234 [D3] send: QMF
> 1.134884 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
> 1.134903 [D3] read: (NAK
> 1.134905 [D2] qx_process_answer: query rejected by the UPS
> (device.mfr)
> 1.136185 [D3] send: QVFW
> 1.198873 [D5] read [ 0]: (8 bytes) => 28 56 45 52 46 57 3a 30
> 1.230865 [D5] read [ 8]: (8 bytes) => 30 30 37 37 2e 31 33 0d
> 1.230870 [D3] read: (VERFW:00077.13
> 1.230874 [D5] send_to_all: SETINFO ups.firmware "00077.13"
> 1.232171 [D3] send: QID
> 1.278886 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
> 1.278896 [D3] read: (NAK
> 1.278909 [D2] qx_process_answer: query rejected by the UPS
> (device.serial)
> 1.280047 [D3] send: I
> 1.326866 [D5] read [ 0]: (8 bytes) => 20 20 20 20 20 20 20 20
> 1.334901 [D5] read [ 8]: (8 bytes) => 0d 00 00 00 00 00 00 00
> 1.334906 [D3] read:
> 1.334908 [D2] qx_process_answer: short reply (device.mfr)
> 1.336115 [D3] send: QGS
> 1.390871 [D5] read [ 0]: (8 bytes) => 28 32 31 39 2e 35 20 35
> 1.430868 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 32 30 2e
> 1.462877 [D5] read [ 16]: (8 bytes) => 34 20 36 30 2e 30 20 30
> 1.502865 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
> 1.534867 [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
> 1.566867 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
> 1.606862 [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
> 1.638861 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
> 1.678883 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
> 1.694864 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
> 1.694884 [D3] read: (219.5 59.9 220.4 60.0 002.8 007 361.8
> 361.8 272.9 ---.- 022.9 100000000010
> 1.694914 [D5] send_to_all: SETINFO input.frequency "59.9"
> 1.694921 [D5] send_to_all: SETINFO output.voltage "220.4"
> 1.694926 [D5] send_to_all: SETINFO output.frequency "60.0"
> 1.694932 [D5] send_to_all: SETINFO output.current "2.8"
> 1.694936 [D5] send_to_all: SETINFO ups.load "7"
> 1.694940 [D5] send_to_all: SETINFO battery.voltage "272.9"
> 1.694945 [D5] send_to_all: SETINFO ups.temperature "22.9"
> 1.694962 [D5] send_to_all: SETINFO ups.type "online"
> 1.694967 [D5] update_status: OL
> 1.694970 [D5] update_status: !LB
> 1.694988 [D5] update_status: !CAL
> 1.695003 [D5] update_status: !FSD
> 1.695007 [D5] send_to_all: SETINFO ups.beeper.status "enabled"
> 1.696295 [D3] send: QMOD
> 1.734859 [D5] read [ 0]: (8 bytes) => 28 4c 0d 00 00 00 00 00
> 1.734878 [D3] read: (L
> 1.734891 [D5] update_status: OL
> 1.736229 [D3] send: QWS
> 1.790912 [D5] read [ 0]: (8 bytes) => 28 30 30 30 30 30 30 30
> 1.830878 [D5] read [ 8]: (8 bytes) => 30 30 30 30 30 30 30 30
> 1.862874 [D5] read [ 16]: (8 bytes) => 30 30 30 30 30 30 30 30
> 1.894869 [D5] read [ 24]: (8 bytes) => 30 30 30 30 30 30 30 30
> 1.934865 [D5] read [ 32]: (8 bytes) => 30 30 30 30 30 30 30 30
> 1.966853 [D5] read [ 40]: (8 bytes) => 30 30 30 30 30 30 30 30
> 2.006871 [D5] read [ 48]: (8 bytes) => 30 30 30 30 30 30 30 30
> 2.038858 [D5] read [ 56]: (8 bytes) => 30 30 30 30 30 30 30 30
> 2.046851 [D5] read [ 64]: (8 bytes) => 30 0d 30 30 30 30 30 30
> 2.046870 [D3] read:
> (0000000000000000000000000000000000000000000000000000000000000000
> 2.048166 [D3] send: QBV
> 2.102862 [D5] read [ 0]: (8 bytes) => 28 32 37 33 2e 32 20 32
> 2.142871 [D5] read [ 8]: (8 bytes) => 30 20 30 31 20 31 30 30
> 2.158875 [D5] read [ 16]: (8 bytes) => 20 30 31 30 0d 00 00 00
> 2.158880 [D3] read: (273.2 20 01 100 010
> 2.158886 battery_number: 20
> 2.158895 battery_number, settable range: 1..9
> 2.158904 [D5] send_to_all: SETINFO battery.packs "1"
> 2.158907 [D5] send_to_all: SETFLAGS battery.packs RW
> 2.158911 [D5] send_to_all: ADDRANGE battery.packs 1 99
> 2.158914 [D5] send_to_all: SETFLAGS battery.packs RW NUMBER
> 2.158919 [D5] send_to_all: SETINFO battery.charge "100"
> 2.158924 [D5] send_to_all: SETINFO battery.runtime "600"
> 2.160228 [D3] send: QLDL
> 2.206859 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
> 2.206874 [D3] read: (NAK
> 2.206880 [D2] qx_process_answer: query rejected by the UPS
> (output.power.minimum.percent)
> 2.206894 [D2] qx_process_answer: query rejected by the UPS
> (output.power.maximum.percent)
> 2.208167 [D3] send: QFLAG
> 2.270872 [D5] read [ 0]: (8 bytes) => 28 45 70 62 72 61 73 64
> 2.310890 [D5] read [ 8]: (8 bytes) => 74 69 44 6f 76 65 66 6a
> 2.318849 [D5] read [ 16]: (8 bytes) => 6d 0d 00 00 00 00 00 00
> 2.318867 [D3] read: (EpbrasdtiDovefjm
> 2.318910 [D5] send_to_all: SETINFO ups.start.auto "yes"
> 2.318915 [D5] send_to_all: SETFLAGS ups.start.auto RW
> 2.318928 [D5] send_to_all: ADDENUM ups.start.auto "no"
> 2.318930 [D5] send_to_all: ADDENUM ups.start.auto "yes"
> 2.318945 [D5] send_to_all: SETINFO battery.protection "yes"
> 2.318948 [D5] send_to_all: SETFLAGS battery.protection RW
> 2.318951 [D5] send_to_all: ADDENUM battery.protection "no"
> 2.318964 [D5] send_to_all: ADDENUM battery.protection "yes"
> 2.318969 [D4] ups_infoval_set: failed to preprocess value
> [battery.energysave: EpbrasdtiDovefjm]
> 2.318973 [D4] ups_infoval_set: failed to preprocess value
> [ups.start.battery: EpbrasdtiDovefjm]
> 2.318989 [D5] send_to_all: SETINFO outlet.0.switchable "no"
> 2.318992 [D5] send_to_all: SETFLAGS outlet.0.switchable RW
> 2.318994 [D5] send_to_all: ADDENUM outlet.0.switchable "no"
> 2.318996 [D5] send_to_all: ADDENUM outlet.0.switchable "yes"
> 2.319001 bypass_alarm: enabled
> 2.319020 battery_alarm: enabled
> 2.319036 bypass_when_off: disabled
> 2.319055 alarm_control: enabled
> 2.319060 converter_mode: disabled
> 2.319072 eco_mode: disabled
> 2.319075 battery_open_status_check: enabled
> 2.319078 bypass_forbidding: disabled
> 2.319083 [D4] ups_infoval_set: failed to preprocess value
> [site_fault_detection: EpbrasdtiDovefjm]
> 2.319087 [D4] ups_infoval_set: failed to preprocess value
> [advanced_eco_mode: EpbrasdtiDovefjm]
> 2.319091 [D4] ups_infoval_set: failed to preprocess value
> [constant_phase_angle: EpbrasdtiDovefjm]
> 2.319096 [D4] ups_infoval_set: failed to preprocess value
> [limited_runtime_on_battery: EpbrasdtiDovefjm]
> 2.319101 setvar(bypass_when_off, disabled)
> 2.319104 bypass_when_off is already disabled
> 2.319106 setvar: FAILED
> 2.320434 [D3] send: QHE
> 2.374864 [D5] read [ 0]: (8 bytes) => 28 32 33 31 20 32 30 39
> 2.382868 [D5] read [ 8]: (8 bytes) => 20 0d 00 00 00 00 00 00
> 2.382883 [D3] read: (231 209
> 2.382916 [D5] send_to_all: SETINFO input.transfer.high "231"
> 2.382929 [D5] send_to_all: SETFLAGS input.transfer.high RW
> 2.382932 [D5] send_to_all: ADDRANGE input.transfer.high 231 244
> 2.382934 [D5] send_to_all: SETFLAGS input.transfer.high RW NUMBER
> 2.382950 [D5] send_to_all: SETINFO input.transfer.low "209"
> 2.382953 [D5] send_to_all: SETFLAGS input.transfer.low RW
> 2.382955 [D5] send_to_all: ADDRANGE input.transfer.low 196 209
> 2.382957 [D5] send_to_all: SETFLAGS input.transfer.low RW NUMBER
> 2.382962 [D5] send_to_all: SETINFO input.transfer.low.min "196"
> 2.382966 [D5] send_to_all: SETINFO input.transfer.low.max "209"
> 2.382970 [D5] send_to_all: SETINFO input.transfer.high.min "231"
> 2.382975 [D5] send_to_all: SETINFO input.transfer.high.max "244"
> 2.384206 [D3] send: QFRE
> 2.430854 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
> 2.430859 [D3] read: (NAK
> 2.430861 [D2] qx_process_answer: query rejected by the UPS
> (input.frequency.high)
> 2.430864 [D2] qx_process_answer: query rejected by the UPS
> (input.frequency.low)
> 2.432092 [D3] send: QBYV
> 2.494864 [D5] read [ 0]: (8 bytes) => 28 32 36 34 20 31 31 30
> 2.502857 [D5] read [ 8]: (8 bytes) => 0d 00 00 00 00 00 00 00
> 2.502875 [D3] read: (264 110
> 2.502891 max_bypass_volt: 264
> 2.502896 max_bypass_volt, settable range: 231..276
> 2.502899 min_bypass_volt: 110
> 2.502903 min_bypass_volt, settable range: 110..209
> 2.504103 [D3] send: QBYF
> 2.566858 [D5] read [ 0]: (8 bytes) => 28 36 34 2e 30 20 35 36
> 2.574855 [D5] read [ 8]: (8 bytes) => 2e 30 0d 00 00 00 00 00
> 2.574870 [D3] read: (64.0 56.0
> 2.574876 max_bypass_freq: 64.0
> 2.574891 max_bypass_freq, settable range: 61.0..64.0
> 2.574895 min_bypass_freq: 56.0
> 2.574909 min_bypass_freq, settable range: 56.0..59.0
> 2.574915 [D2] setvar: nothing to do... [battery_number]
> 2.576110 [D3] send: RE0
> 2.798865 [D5] read [ 0]: (8 bytes) => 00 00 00 00 00 00 00 00
> 3.801004 [D3] read: Operation timed out (-7)
> 3.801025 [D4] qx_process: failed to preprocess answer
> [battery.voltage.low]
> 3.802276 [D3] send: QPD
> 3.846839 [D5] read [ 0]: (8 bytes) => 28 4e 41 4b 0d 00 00 00
> 3.846844 [D3] read: (NAK
> 3.846855 [D2] qx_process_answer: query rejected by the UPS
> (input_phase_angle)
> 3.846872 [D2] qx_process_answer: query rejected by the UPS
> (output_phase_angle)
> 3.848203 [D3] send: QPAR
> 3.894852 [D5] read [ 0]: (8 bytes) => 28 30 31 0d 00 00 00 00
> 3.894870 [D3] read: (01
> ] 3.894874 [D2] voltronic_parallel: non numerical value
> [voltronic_parallel: 01
> ] 3.894875 [D4] ups_infoval_set: failed to preprocess value
> [voltronic_parallel: 01
> 3.894883 [D5] send_to_all: ADDCMD load.off
> 3.894898 [D5] send_to_all: ADDCMD load.on
> 3.894900 [D5] send_to_all: ADDCMD shutdown.return
> 3.894902 [D5] send_to_all: ADDCMD shutdown.stayoff
> 3.894904 [D5] send_to_all: ADDCMD shutdown.stop
> 3.894916 [D5] send_to_all: ADDCMD test.battery.start
> 3.894918 [D5] send_to_all: ADDCMD test.battery.start.deep
> 3.894920 [D5] send_to_all: ADDCMD test.battery.start.quick
> 3.894922 [D5] send_to_all: ADDCMD test.battery.stop
> 3.894934 [D5] send_to_all: ADDCMD beeper.toggle
> 3.894937 [D5] send_to_all: ADDCMD beeper.enable
> 3.894940 [D5] send_to_all: ADDCMD beeper.disable
> 3.894942 [D5] send_to_all: ADDCMD bypass.start
> 3.894956 [D5] send_to_all: ADDCMD bypass.stop
> 3.894960 [D5] send_to_all: SETINFO ups.delay.start "180"
> 3.894963 [D5] send_to_all: SETFLAGS ups.delay.start RW
> 3.894978 [D5] send_to_all: ADDRANGE ups.delay.start 0 599940
> 3.894981 [D5] send_to_all: SETFLAGS ups.delay.start RW NUMBER
> 3.894983 [D5] send_to_all: SETINFO ups.delay.shutdown "30"
> 3.894985 [D5] send_to_all: SETFLAGS ups.delay.shutdown RW
> 3.894989 [D5] send_to_all: ADDRANGE ups.delay.shutdown 12 5940
> 3.895001 [D5] send_to_all: SETFLAGS ups.delay.shutdown RW NUMBER
> 3.895005 No values for battery high/low voltages
> 3.895010 [D5] send_to_all: SETINFO battery.voltage.low "208.00"
> 3.895023 [D5] send_to_all: SETINFO battery.voltage.high "260.00"
> 3.895026 Using 'guesstimation' (low: 208.000000, high: 260.000000)!
> 3.895037 setvar(ups.delay.start, 60)
> 3.895041 [D2] setvar: setting server side variable ups.delay.start
> 3.895044 [D5] send_to_all: SETINFO ups.delay.start "60"
> 3.895046 setvar: SUCCEED
> 3.895049 setvar(ups.delay.shutdown, 30)
> 3.895051 setvar: nothing to do... [ups.delay.shutdown]
> 3.895057 [D5] send_to_all: SETINFO driver.parameter.pollfreq "30"
> 3.895065 [D5] send_to_all: SETINFO driver.state "init.updateinfo"
> 3.895068 [D1] upsdrv_updateinfo...
> 3.895071 [D1] Quick update...
> 3.896659 [D3] send: QGS
> 3.950819 [D5] read [ 0]: (8 bytes) => 28 32 32 30 2e 34 20 35
> 3.990855 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 31 38 2e
> 4.022858 [D5] read [ 16]: (8 bytes) => 37 20 35 39 2e 39 20 30
> 4.062843 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
> 4.094844 [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
> 4.126840 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 33
> 4.166841 [D5] read [ 48]: (8 bytes) => 2e 32 20 2d 2d 2d 2e 2d
> 4.198838 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
> 4.238833 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
> 4.254852 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 33
> 4.254868 [D3] read: (220.4 59.9 218.7 59.9 002.8 007 361.8
> 361.8 273.2 ---.- 022.9 100000000010
> 4.254872 [D5] update_status: OL
> 4.254875 [D5] update_status: !LB
> 4.254879 [D5] update_status: !CAL
> 4.254896 [D5] update_status: !FSD
> 4.254918 [D5] send_to_all: SETINFO ups.status "OL"
> 4.254921 [D5] send_to_all: DATAOK
> 4.254924 [D5] send_to_all: SETINFO driver.state "init.quiet"
> 4.254938 [D5] send_to_all: SETINFO driver.parameter.pollinterval
> "10"
> 4.254941 [D5] send_to_all: SETINFO driver.parameter.synchronous
> "yes"
> 4.254943 Running as foreground process, not saving a PID file
> 4.254956 [D5] send_to_all: SETINFO driver.flag.allow_killpower "0"
> 4.254960 [D5] send_to_all: SETFLAGS driver.flag.allow_killpower RW
> NUMBER
> 4.254963 [D5] send_to_all: ADDCMD driver.killpower
> 4.254976 [D5] send_to_all: ADDCMD driver.reload
> 4.254979 [D5] send_to_all: ADDCMD driver.reload-or-exit
> 4.254981 [D5] send_to_all: ADDCMD driver.reload-or-error
> 4.254984 [D5] send_to_all: SETINFO driver.state "quiet"
> 4.254986 [D1] Driver initialization completed, beginning data
> dump (1 loops)
> 4.254990 [D5] send_to_all: SETINFO driver.state "updateinfo"
> 4.254993 [D1] upsdrv_updateinfo...
> 4.254995 [D1] Quick update...
> 4.256195 [D3] send: QGS
> 4.310837 [D5] read [ 0]: (8 bytes) => 28 32 31 39 2e 35 20 35
> 4.350846 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 31 39 2e
> 4.390858 [D5] read [ 16]: (8 bytes) => 35 20 36 30 2e 30 20 30
> 4.422834 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
> 4.454832 [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
> 4.494848 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
> 4.526837 [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
> 4.566835 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
> 4.598847 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
> 4.614849 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
> 4.614855 [D3] read: (219.5 59.9 219.5 60.0 002.8 007 361.8
> 361.8 272.9 ---.- 022.9 100000000010
> 4.614859 [D5] update_status: OL
> 4.614862 [D5] update_status: !LB
> 4.614866 [D5] update_status: !CAL
> 4.614883 [D5] update_status: !FSD
> 4.614903 [D5] send_to_all: SETINFO driver.state "quiet"
> 4.614906 [D5] send_to_all: SETINFO driver.state "updateinfo"
> 4.614908 [D1] upsdrv_updateinfo...
> 4.614911 [D1] Quick update...
> 4.616211 [D3] send: QGS
> 4.670846 [D5] read [ 0]: (8 bytes) => 28 32 32 31 2e 33 20 35
> 4.710831 [D5] read [ 8]: (8 bytes) => 39 2e 39 20 32 31 38 2e
> 4.742850 [D5] read [ 16]: (8 bytes) => 37 20 35 39 2e 39 20 30
> 4.782842 [D5] read [ 24]: (8 bytes) => 30 32 2e 38 20 30 30 37
> 4.814822 [D5] read [ 32]: (8 bytes) => 20 33 36 31 2e 38 20 33
> 4.846843 [D5] read [ 40]: (8 bytes) => 36 31 2e 38 20 32 37 32
> 4.886822 [D5] read [ 48]: (8 bytes) => 2e 39 20 2d 2d 2d 2e 2d
> 4.918833 [D5] read [ 56]: (8 bytes) => 20 30 32 32 2e 39 20 31
> 4.958839 [D5] read [ 64]: (8 bytes) => 30 30 30 30 30 30 30 30
> 4.974825 [D5] read [ 72]: (8 bytes) => 30 31 30 0d 20 32 37 32
> 4.974829 [D3] read: (221.3 59.9 218.7 59.9 002.8 007 361.8
> 361.8 272.9 ---.- 022.9 100000000010
> 4.974833 [D5] update_status: OL
> 4.974836 [D5] update_status: !LB
> 4.974839 [D5] update_status: !CAL
> 4.974855 [D5] update_status: !FSD
> 4.974864 [D5] send_to_all: SETINFO driver.state "quiet"
> 4.974878 [D5] send_to_all: SETINFO driver.state "dumping"
> 4.974881 [D3] Entering dstate_dump
> battery.charge: 100
> battery.packs: 1
> battery.protection: yes
> battery.runtime: 600
> battery.voltage: 272.9
> battery.voltage.high: 260.00
> battery.voltage.low: 208.00
> battery.voltage.nominal: 240.0
> device.model: G10K
> device.type: ups
> driver.debug: 6
> driver.flag.allow_killpower: 0
> driver.name: nutdrv_qx
> driver.parameter.bypass_when_off: disabled
> driver.parameter.offdelay: 30
> driver.parameter.ondelay: 60
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 10
> driver.parameter.port: auto
> driver.parameter.synchronous: yes
> driver.state: dumping
> driver.version: 2.8.0-2359-g6c0032e52
> driver.version.data: Voltronic 0.08
> driver.version.internal: 0.35
> driver.version.usb: libusb-1.0.26 (API: 0x1000109)
> input.current.nominal: 45.0
> input.frequency: 59.9
> input.frequency.nominal: 60.0
> input.phases: 1
> input.transfer.high: 231
> input.transfer.high.max: 244
> input.transfer.high.min: 231
> input.transfer.low: 209
> input.transfer.low.max: 209
> input.transfer.low.min: 196
> input.voltage: 221.3
> input.voltage.nominal: 230.0
> outlet.0.switchable: no
> output.current: 2.8
> output.current.nominal: 45
> output.frequency: 60.0
> output.frequency.nominal: 60.0
> output.phases: 1
> output.powerfactor: 0.8
> output.voltage: 220.4
> output.voltage.nominal: 220.0
> ups.beeper.status: enabled
> ups.delay.shutdown: 30
> ups.delay.start: 60
> ups.firmware: 00077.13
> ups.firmware.aux: P02
> ups.load: 7
> ups.power.nominal: 10000
> ups.productid: 5161
> ups.start.auto: yes
> ups.status: OL
> ups.temperature: 22.9
> ups.type: online
> ups.vendorid: 0665
> 4.975010 [D5] send_to_all: SETINFO driver.state "cleanup.upsdrv"
> 4.975014 [D1] upsdrv_cleanup...
> 4.975125 [D5] send_to_all: SETINFO driver.state "cleanup.exit
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20230913/159e341c/attachment-0001.htm>
More information about the Nut-upsuser
mailing list