[Nut-upsuser] NUT and Eaton UPS produce a lot of error messages
Stefan Schumacher
stefanschumacheratwork at gmail.com
Fri Jan 19 16:02:09 GMT 2024
Jan 19 05:50:13 mars nut-monitor[849]: Signal 15: exiting
Jan 19 05:50:13 mars nut-monitor[849]: Network UPS Tools upsmon 2.8.0
Jan 19 05:50:13 mars systemd[1]: Stopping nut-monitor.service -
Network UPS Tools - power device monitor and shutdown controller...
Jan 19 05:50:13 mars systemd[1]: nut-monitor.service: Deactivated successfully.
Jan 19 05:50:13 mars systemd[1]: Stopped nut-monitor.service - Network
UPS Tools - power device monitor and shutdown controller.
Jan 19 05:50:17 mars nut-server[1303]: mainloop: Interrupted system call
Jan 19 05:50:17 mars nut-server[1303]: Signal 15: exiting
Jan 19 05:50:17 mars nut-server[1303]: Network UPS Tools upsd 2.8.0
Jan 19 05:50:17 mars systemd[1]: Stopping nut-server.service - Network
UPS Tools - power devices information server...
Jan 19 05:50:17 mars upsd[1303]: mainloop: Interrupted system call
Jan 19 05:50:17 mars upsd[1303]: Signal 15: exiting
Jan 19 05:50:17 mars systemd[1]: nut-server.service: Deactivated successfully.
Jan 19 05:50:17 mars systemd[1]: Stopped nut-server.service - Network
UPS Tools - power devices information server.
Jan 19 05:50:44 mars usbhid-ups[845]: WARNING: send_to_all: write 31
bytes to socket 11 failed (ret=-1), disconnecting: Broken pipe
Am Fr., 19. Jan. 2024 um 16:33 Uhr schrieb Matus UHLAR - fantomas
<uhlar at fantomas.sk>:
>
> On 19.01.24 16:20, Stefan Schumacher via Nut-upsuser wrote:
> >This morning at 9:50 the server stopped working unexpectedly - I was
> >still sleeping until 10:00, so no user intervention took place.
> >
> >Jan 19 05:50:17 mars nut-server[1303]: mainloop: Interrupted system call
> >Jan 19 05:50:17 mars nut-server[1303]: Signal 15: exiting
> >Jan 19 05:50:17 mars nut-server[1303]: Network UPS Tools upsd 2.8.0
> >Jan 19 05:50:17 mars systemd[1]: Stopping nut-server.service - Network
> >UPS Tools - power devices information server...
> >Jan 19 05:50:17 mars upsd[1303]: mainloop: Interrupted system call
> >Jan 19 05:50:17 mars upsd[1303]: Signal 15: exiting
> >Jan 19 05:50:17 mars systemd[1]: nut-server.service: Deactivated successfully.
> >Jan 19 05:50:17 mars systemd[1]: Stopped nut-server.service - Network
> >UPS Tools - power devices information server.
> >
> >I am considering returning the device to the online shop I bought. As
> >it is, it's nothing but trouble. Can you recommend a small UPS (1
> >Server) that is guaranteed to work flawlessly with NUT?
>
> perhaps Eaton Ellipse would be fine.
>
> The message above does not look like a problem of the UPS.
> Was there anything other in the logs, before the message above?
>
> >Am Fr., 19. Jan. 2024 um 10:54 Uhr schrieb Jim Klimov via Nut-upsuser
> ><nut-upsuser at alioth-lists.debian.net>:
> >>
> >> With recent NUT releases, driver disconnections should be contained in its own `nut-driver at eaton` instance (the `@upsname` part is derived from the `ups.conf` section name). One of the drivers failing and restarting is not a proper cause for the data server to recycle.
> >>
> >> Also, nowadays some (maybe not all) USB-capable drivers should try to reconnect without restarting. Note however, that in some NUT iterations it is possible that this feature misfires if the devices get re-enumerated and the driver tries to reuse results of original libusb discovery (e.g. some kernels add +1 to "device" number upon each reconnection, such as due to USB chip/hub reset, EMI causing protocol reset, or a device going to sleep and yanked back to work).
> >>
> >> In fact, recent work on master branch got `nut-scanner` to not suggest the `device` option by default to avoid such situations.
> >>
> >> Jim
> >>
> >>
> >> On Fri, Jan 19, 2024 at 9:36 AM Matus UHLAR - fantomas <uhlar at fantomas.sk> wrote:
> >>>
> >>> On 19.01.24 09:00, Jim Klimov via Nut-upsuser wrote:
> >>> >Well, from your logs it seems that at 05:17:03 your nut-server (upsd)
> >>> >restarted, so an upsmon reconnection attempt at 05:17:09 had an issue with
> >>> >that (config not all applied? strange a bit) but since 05:17:14 it is okay.
> >>> >
> >>> >Maybe a few too many banners shown from upsmon, while its same uptime seems
> >>> >to continue. Maybe someone should check on that, seems like a good and easy
> >>> >newcomer issue to learn the code, so PRs are welcome :D
> >>> >
> >>> >Messages about lack of "*.pid" files are okay, they should look less scary
> >>> >in newer releases of NUT. They confirm that there is no previous daemon
> >>> >with the same basic configuration currently running, so that your new
> >>> >instance might conflict with it or send it some signals intentionally - so
> >>> >it is just a new start in a clean environment with no competitors.
> >>> >
> >>> >It is a bit unfortunate that both syslog (upsd) and stderr (nut-server)
> >>> >messages land into the same systemd journal. It may be possible to add
> >>> >auto-detection of systemd and not-emit one of those streams then, or add an
> >>> >option for that to be quieter and better readable (some people can have a
> >>> >separate syslog setup anyway, maybe on a remote "sink" system, so just
> >>> >cutting one off always is not right).
> >>> >
> >>> >So one question that remains is the missing lines from previous lifetime in
> >>> >the short excerpt of upsd: why did it restart at that time? :)
> >>>
> >>> I also have Eaton UPS, just different model. It sometimes disconnects and
> >>> nut has to connect again. I guess this is what happened.
> >>>
> >>> I assume the disonnect message is not visible in "Systemctl status" message
> >>> because it does not belong to the current process but previous one.
> >>> Looking for syslog (/var/log/messages) or journal messages (journalctl) could
> >>> show that. I guess nothing bad happened there.
> >>>
> >>> >On Fri, Jan 19, 2024 at 6:13 AM Stefan Schumacher via Nut-upsuser <
> >>> >nut-upsuser at alioth-lists.debian.net> wrote:
> >>> >> I recently bought a small UPS by Eaton (Ellipse ECO 800) in order to
> >>> >> prevent my
> >>> >> btrfs-fileserver (running Debian 12 Bookworm 12.4 from shutting down
> >>> >> abruptly while writing
> >>> >> something important during a power loss. I am using the version
> >>> >> 2.8.0.7 provided by Debian.
> >>> >> I have found very gooddocumentation on how to set up the UPS and the
> >>> >> services on the server
> >>> >> connected to it. Unfortunately it's in German
> >>> >> (https://techbotch.org/blog/ups-setup/index.html) which is not a
> >>> >> problem for me but possibly for others trying to understand my set-up.
> >>> >>
> >>> >> I will now describe the steps I took and the configuration options I
> >>> >> set and then post the errors of nut-monitor and nut server. I hope
> >>> >> someone can help fix the underlying problem behind these error
> >>> >> messages.
> >>> >>
> >>> >> lsusb shows the UPS:
> >>> >> Bus 001 Device 003: ID 0463:ffff MGE UPS Systems UPS
> >>> >>
> >>> >> So I made this changes to ups.conf
> >>> >> [Eaton]
> >>> >> driver = usbhid-ups
> >>> >> port = auto
> >>> >> vendorid = 0463
> >>> >> pollfreq = 30
> >>> >>
> >>> >> In nut.conf I set mode=standalone.
> >>> >>
> >>> >> And finally I added these lines to upsd.users:
> >>> >> [upsmon]
> >>> >> password = XXXX
> >>> >> actions = SET
> >>> >> instcmds = ALL
> >>> >>
> >>> >> I did a live test, plugged the cord and waited until the server shut
> >>> >> down at 20%. Worked fine.
> >>> >> Upsc also works - I can query my UPS for specific parameters or show them
> >>> >> all.
> >>> >>
> >>> >> The problem is the dozens of errors the systemctl status messages
> >>> >> show. I bought the UPS to increase reliability and now I don't know if
> >>> >> the service is working in case of an emergency. How can I fix this ?
> >>> >>
> >>> >> ● nut-server.service - Network UPS Tools - power devices information server
> >>> >> Loaded: loaded (/lib/systemd/system/nut-server.service; enabled;
> >>> >> preset: enabled)
> >>> >> Active: active (running) since Fri 2024-01-19 05:17:03 CET; 5s ago
> >>> >> Main PID: 1303 (upsd)
> >>> >> Tasks: 1 (limit: 38253)
> >>> >> Memory: 640.0K
> >>> >> CPU: 3ms
> >>> >> CGroup: /system.slice/nut-server.service
> >>> >> └─1303 /lib/nut/upsd -F
> >>> >> Jan 19 05:17:03 servername nut-server[1303]: fopen /run/nut/upsd.pid:
> >>> >> No such file or directory
> >>> >> Jan 19 05:17:03 servername nut-server[1303]: Could not find PID file
> >>> >> '/run/nut/upsd.pid' to see if previous upsd instance is already
> >>> >> running!
> >>> >> Jan 19 05:17:03 servername nut-server[1303]: listening on 127.0.0.1 port
> >>> >> 3493
> >>> >> Jan 19 05:17:03 servername nut-server[1303]: listening on ::1 port 3493
> >>> >> Jan 19 05:17:03 servername upsd[1303]: listening on 127.0.0.1 port 3493
> >>> >> Jan 19 05:17:03 servername upsd[1303]: listening on ::1 port 3493
> >>> >> Jan 19 05:17:03 servername nut-server[1303]: Connected to UPS [Eaton]:
> >>> >> usbhid-ups-Eaton
> >>> >> Jan 19 05:17:03 servername upsd[1303]: Connected to UPS [Eaton]:
> >>> >> usbhid-ups-Eaton
> >>> >> Jan 19 05:17:03 servername upsd[1303]: Running as foreground process,
> >>> >> not saving a PID file
> >>> >> Jan 19 05:17:03 servername nut-server[1303]: Running as foreground
> >>> >> process, not saving a PID file
> >>> >>
> >>> >> ● nut-monitor.service - Network UPS Tools - power device monitor and
> >>> >> shutdown controller
> >>> >> Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled;
> >>> >> preset: enabled)
> >>> >> Active: active (running) since Fri 2024-01-19 03:37:28 CET; 1h 41min ago
> >>> >> Main PID: 847 (upsmon)
> >>> >> Tasks: 2 (limit: 38253)
> >>> >> Memory: 3.4M
> >>> >> CPU: 338ms
> >>> >> CGroup: /system.slice/nut-monitor.service
> >>> >> ├─847 /lib/nut/upsmon -F
> >>> >> └─849 /lib/nut/upsmon -F
> >>> >> Jan 19 03:43:08 servername nut-monitor[849]: UPS Eaton at localhost on
> >>> >> battery
> >>> >> Jan 19 03:43:09 servername nut-monitor[916]: Network UPS Tools upsmon 2.8.0
> >>> >> Jan 19 03:43:33 servername nut-monitor[849]: UPS Eaton at localhost on line
> >>> >> power
> >>> >> Jan 19 03:43:34 servername nut-monitor[920]: Network UPS Tools upsmon 2.8.0
> >>> >> Jan 19 05:17:04 servername nut-monitor[849]: Poll UPS
> >>> >> [Eaton at localhost] failed - Write error: Broken pipe
> >>> >> Jan 19 05:17:04 servername nut-monitor[849]: Communications with UPS
> >>> >> Eaton at localhost lost
> >>> >> Jan 19 05:17:04 servername nut-monitor[1305]: Network UPS Tools upsmon
> >>> >> 2.8.0
> >>> >> Jan 19 05:17:09 servername nut-monitor[849]: Login on UPS
> >>> >> [Eaton at localhost] failed - got [ERR ACCESS-DENIED]
> >>> >> Jan 19 05:17:14 servername nut-monitor[849]: Communications with UPS
> >>> >> Eaton at localhost established
> >>> >> Jan 19 05:17:14 servername nut-monitor[1312]: Network UPS Tools upsmon
> >>> >> 2.8.0
> >>>
> >>>
> >>> --
> >>> Matus UHLAR - fantomas, uhlar at fantomas.sk ; http://www.fantomas.sk/
> >>> Warning: I wish NOT to receive e-mail advertising to this address.
> >>> Varovanie: na tuto adresu chcem NEDOSTAVAT akukolvek reklamnu postu.
> >>> Spam = (S)tupid (P)eople's (A)dvertising (M)ethod
> >>>
> >>> _______________________________________________
> >>> Nut-upsuser mailing list
> >>> Nut-upsuser at alioth-lists.debian.net
> >>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
> >>
> >> _______________________________________________
> >> Nut-upsuser mailing list
> >> Nut-upsuser at alioth-lists.debian.net
> >> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
> >
> >_______________________________________________
> >Nut-upsuser mailing list
> >Nut-upsuser at alioth-lists.debian.net
> >https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>
> --
> Matus UHLAR - fantomas, uhlar at fantomas.sk ; http://www.fantomas.sk/
> Warning: I wish NOT to receive e-mail advertising to this address.
> Varovanie: na tuto adresu chcem NEDOSTAVAT akukolvek reklamnu postu.
> Micro$oft random number generator: 0, 0, 0, 4.33e+67, 0, 0, 0...
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
More information about the Nut-upsuser
mailing list