[Nut-upsuser] UPS not Shutting Down
    Roger Price 
    roger at rogerprice.org
       
    Sat Jun  1 16:44:18 BST 2024
    
    
  
On Sat, 1 Jun 2024, chribonn at duck.com wrote:
> Yes. I received both the email and the update from the console.  
> >From your email, I understand that the expected behaviour should have been that the os should have started the shutdown process.
NUT requires that 3 os services be running.  If you run the systemctl command 
and see something like:
   nut-driver.service     loaded    active   running   Network UPS Tools - power device driver controller
   nut-monitor.service    loaded    inactive dead      Network UPS Tools - power device monitor and shutdown controller
   nut-server.service     loaded    active   running   Network UPS Tools - power devices information server
then monitoring by upsmon of UPS battery levels has stopped, and there will be 
no NUT managed shutdown.
> Is there a log I could look at (Nut or Debian) to understand what is happening?
   journalctl -u nut-monitor
will tell you what is happening to the monitoring service.  You can also look at 
the nut-driver and nut-server services.
Roger
    
    
More information about the Nut-upsuser
mailing list