[Nut-upsuser] UPS not Shutting Down
chribonn at duck.com
chribonn at duck.com
Sun Jun 2 12:52:58 BST 2024
My bad. I'll check it out.
On Sun, 2 Jun 2024 at 08:14, Roger Price <
roger_at_rogerprice.org_chribonn at duck.com> wrote:
> On Sat, 1 Jun 2024, Alan via Nut-upsuser wrote:
>
> > root at proxmox-01:~# cat nano /etc/nut/ups.conf
>
> If you send us hundreds of lines of comments it makes your post difficult
> to
> understand. Could you trim out the comments with for example
>
> cat /etc/nut/ups.conf | grep -v "#"
>
> which would show us the following, which is what we need to see.
>
> > maxretry = 3
> >
> > offdelay = 120
> > ondelay = 240
> >
> > [pve1]
> > driver = "usbhid-ups"
> > port = "auto"
> > vendorid = "06DA"
> > productid = "FFFF"
> > desc = "Phoenixtec Power Co., Ltd Innova Unity"
> > serial = "CPANM2436540037"
> > override.battery.charge.low = 70
> > override.battery.runtime.low = 2500
> > # wait 5 minutes for ups to power off
> > override.ups.delay.shutdown = 300
>
> I don't see the line
>
> lowbatt = 70
>
> which you need to make a permanent change to the value. If you use the
> "override", the driver will restore the default. See chapter 2.7 in
> https://rogerprice.org/NUT/ConfigExamples.A5.pdf
>
> Try re-running your test with lowbatt = 70 .
> Roger_______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>