[Nut-upsuser] Cyber Power System CP1500 AVR UPS: changing battery.charge.low value
    chribonn at duck.com 
    chribonn at duck.com
       
    Sat Mar  9 21:39:34 GMT 2024
    
    
  
Hi Charles,
The posting at
https://github.com/networkupstools/nut/issues/432#issuecomment-405371395
references ups.delay.start and suggests setting it to -1.
upsrw -l pve1 at localhost listed this as modifiable but any attempt at
modifying the value failed.  I used the *override.ups.delay.start = -1* in
nut.conf and this is now being reported.
Two observations are that once a variable setting is overridden, *upsrw -w*
will not show these values.  Is it by design?
Below is the output from *upsc *for the Cyber Power System CP1500 AVR
Init SSL without certificate database
battery.charge: 100
battery.charge.low: 70
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 6000
battery.runtime.low: 900
battery.type: PbAcid
battery.voltage: 26.0
battery.voltage.nominal: 24
device.mfr: CPS
device.model: Value2200E
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0501
driver.parameter.synchronous: auto
driver.parameter.vendorid: 0764
driver.version: 2.8.0
driver.version.data: CyberPower HID 0.6
driver.version.internal: 0.47
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.transfer.high: 0
input.transfer.low: 0
input.voltage: 241.0
input.voltage.nominal: 230
output.voltage: 243.0
ups.beeper.status: disabled
ups.delay.shutdown: 300
*ups.delay.start: -1*
ups.load: 0
ups.mfr: CPS
ups.model: Value2200E
ups.productid: 0501
ups.realpower.nominal: 1320
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764
Regards,
Alan
On Fri, 8 Mar 2024 at 15:02, Charles Lepple via Nut-upsuser <
nut-upsuser_at_alioth-lists.debian.net_chribonn at duck.com> wrote:
> On Mar 8, 2024, at 7:07 AM, Roger Price <roger at rogerprice.org> wrote:
> >
> > Perhaps setting lowbatt = 50 in ups.conf would help.
>
> Roger, good point.
>
> That option is missing in the usbhid-ups man page, so I logged an issue to
> remind us to fix that: https://github.com/networkupstools/nut/issues/2356
>
> Since I am used to fighting the Cyber Power Systems shutdown timers, I
> automatically assumed it was a similar issue where the UPS accepts the
> value then ignores it.
>
> Alan, your shutdown timers might need to be multiples of 60 seconds (I see
> 20 and 30 for ups.delay.shutdown and ups.delay.start, respectively), and
> that might not even be enough. Discussion:
> https://github.com/networkupstools/nut/issues/432#issuecomment-405371395
> and https://github.com/networkupstools/nut/issues/625
>
> --
> Charles Lepple
> clepple at gmail
>
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20240309/23b5fcbe/attachment.htm>
    
    
More information about the Nut-upsuser
mailing list