Thanks for the tip, Jim. I just figured out what is going on. The
system is now working. ==> This one is on me. <==
The root cause was the specification of the bus number in the ups.conf
file. Here is what it looks like now:
============
[cyberpower]
driver = "usbhid-ups"
port = "auto"
vendorid = "0764"
productid = "0501"
product = "UPS CP1000AVRLCD"
vendor = "CPS"
# bus = "006"
================
It had been running with the bus= line uncommented. I don't remember
why that was needed, but sometime in the dark past I added it.
Commenting it out and restarting both nut-server and nut-monitor brought
everything to life.
Charles' reply below had the seed of the answer when he mentioned how
the UPS will appear in the /dev/ directory. I had been looking at every
other file except ups.conf and so the bus number was not top of mind.
The documentation linked by Jim says that the DEBUG_MIN setting is
supported in all of the .conf files. I changed it in upsd.conf, then
went looking in other files. That is when I noticed the bus number in
ups.conf. A very big DOH slap was promptly administered!
I think the messages about permissions were the result of not having bus
number 6 at all. There was no /dev device to connect to and that was
interpreted as lack of permissions.
As for the messages about missing libusb ... I am still puzzled over
that. nut-scanner still complains about it. It is hard to argue with
success, though, so that question is now sort of moot. "upsc cyberpower"
returns valid information and nut-monitor is no longer attempting
restart once per minute.
Thanks everyone for the help.
===============
Bill Gee
On 11/10/24 11:45, Jim Klimov wrote:
> Can you try starting the driver with higher debug verbosity to see more
> details, e.g. add `debug_min = 6` to the `ups.conf` section, or stop the
> auto-starting driver attempts and run the driver program with CLI options?
>
> * https://github.com/networkupstools/nut/wiki/Changing-NUT-daemon-debug-
> verbosity <https://github.com/networkupstools/nut/wiki/Changing-NUT-
> daemon-debug-verbosity>
>
> With `upsdrvctl` driven attempts, you may also be in conflict with a
> generated `nut-driver at cyberpower.service` instance (although this is not
> the only problem, as the unit seems to fail starting for you too), more
> details about such units at:
>
> * https://github.com/networkupstools/nut/wiki/
> nut%E2%80%90driver%E2%80%90enumerator-(NDE) <https://github.com/
> networkupstools/nut/wiki/nut%E2%80%90driver%E2%80%90enumerator-(NDE)>
>
> Jim
>
>
> On Sun, Nov 10, 2024 at 4:47 PM Bill Gee <bgee at campercaver.net
> <mailto:bgee at campercaver.net>> wrote:
>
> I also am wondering if the message about libusb driver missing might be
> the real problem.
>
> Checking my system, I see this:
>
> ===================
> [root at mythtv dev]# ll /dev/bus/usb/001
> total 0
> crw-rw-r--+ 1 root root 189, 0 Nov 9 08:21 001
> crw-rw-r--+ 1 root root 189, 1 Nov 9 08:21 002
> crw-rw-r--+ 1 root root 189, 2 Nov 9 08:21 003
> crw-rw-r--+ 1 root dialout 189, 3 Nov 10 09:43 004
> ==================
>
> That looks to me like the udev rule worked.
>
> ===============
> Bill Gee
>
> On 11/10/24 08:38, Charles Lepple via Nut-upsuser wrote:
> > On Nov 9, 2024, at 8:09 PM, Tim Dawson <tadawson at tpcsvc.com
> <mailto:tadawson at tpcsvc.com>> wrote:
> >>
> >> Check /dev/hidraw6, as noted in your dmesg output (and any other
> *hid*
> >> devices under /dev). User nut has almost zero privs to devices
> unless
> >> a udev rule changes the perms on the dev for nut . . .
> >
> > I admit I am not fully tracking the latest NUT developments, but
> I don't
> > think the current drivers use /dev/hidraw*, especially when the
> drivers
> > mention libusb. (Once the libusb-based drivers start, they should
> detach
> > the kernel's HID drivers such that the corresponding /dev/hidraw*
> device
> > disappears.)
> >
> > You are correct that the udev rules need to change permissions on
> one of
> > the UPS /dev nodes, though.
> >
> > From Bill's lsusb output:
> >
> > [root at mythtv ups]# lsusb
> > ...
> > Bus 001 Device 004: ID 0764:0501 Cyber Power System, Inc. CP1500
> AVR UPS
> >
> > The libusb path for this UPS would typically be /dev/bus/usb/001/004
> >
> > --
> > Charles Lepple
> > clepple at gmail
> >
> >
> >> _______________________________________________
> >> Nut-upsuser mailing list
> >> Nut-upsuser at alioth-lists.debian.net <mailto:Nut-upsuser at alioth-
> lists.debian.net>
> >> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-
> upsuser <https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/
> nut-upsuser>
> >
> >
> > _______________________________________________
> > Nut-upsuser mailing list
> > Nut-upsuser at alioth-lists.debian.net <mailto:Nut-upsuser at alioth-
> lists.debian.net>
> > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-
> upsuser <https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/
> nut-upsuser>
>
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net <mailto:Nut-upsuser at alioth-
> lists.debian.net>
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
> <https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser>
>
More information about the Nut-upsuser