[Nut-upsuser] POWERCOM UPS USB : UPS Shutdown
    Jim Klimov 
    jimklimov+nut at gmail.com
       
    Mon May 12 11:04:51 BST 2025
    
    
  
Hoped to look into this just today, if nobody beat me to it yet.
Jim
On Mon, May 12, 2025 at 11:54 AM Alexey Korobeinikov <alexey at fseafood.com>
wrote:
> Are there any chances that this error can be fixed?
>
> 06.05.2025 18:19, Alexey Korobeinikov:
>
> Hi! Thank You!
>
> The UPS behavior are chages with NUT v.2.8.2 but more strange
>
> After this command (if power cord unpluged)
> /usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k
>
> ....
> 0.188173     [D4] string_to_path: depth = 3
>    0.188187     [D4] string_to_path: depth = 3
>    0.188199     [D4] string_to_path: depth = 3
>    0.188211     [D4] string_to_path: depth = 3
>    0.188246     [D2] find_nut_info: unknown info type: load.off.delay
>    0.188267     [D2] find_nut_info: unknown info type: load.off.delay
>    0.188280     Initiating UPS shutdown
>    0.188290     [D1] upsdrv_shutdown...
>    0.188298     [D1] instcmd(shutdown.return, [NULL])
>    0.188316     [D3] instcmd: using Path
> 'UPS.PowerSummary.DelayBeforeShutdown'
>    0.188332     [D3] powercom_shutdown_nuf: value = (null), command = 5E00
>    0.224970     [D3] Report[set]: (3 bytes) => 0f 00 5e
>    0.225003     [D4] Set report succeeded
>    0.225012     [D3] instcmd: SUCCEED
>
> The UPS are start double beeping every 2 seconds, but didn't turn off
> himself ( 2 minutes wait )
> UPS are still beeping if power are restored
>
> Status are:
> # upsc ups at localhost
> battery.charge: 100
> battery.charge.low: 70
> battery.charge.warning: 30
> battery.mfr.date: 2014/01/15
> battery.runtime: 800
> battery.type: PbAc
> device.mfr: POWERCOM Co.,LTD
> device.model: HID UPS Battery
> device.serial: 004-0D9F-000
> device.type: ups
> driver.debug: 0
> driver.flag.allow_killpower: 0
> driver.flag.ignorelb: enabled
> driver.name: usbhid-ups
> driver.parameter.offdelay: 30
> driver.parameter.ondelay: 60
> driver.parameter.override.battery.charge.low: 70
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 0004
> driver.parameter.synchronous: auto
> driver.parameter.vendorid: 0d9f
> driver.state: quiet
> driver.version: 2.8.2
> driver.version.data: PowerCOM HID 0.7
> driver.version.internal: 0.53
> driver.version.usb: libusb-1.0.26 (API: 0x1000109)
> input.frequency: 50.0
> input.voltage: 224.0
> input.voltage.nominal: 220
> output.frequency: 50.0
> output.voltage: 224.0
> output.voltage.nominal: 220
> ups.beeper.status: enabled
> ups.date: 2014/01/15
> ups.delay.shutdown: 30
> ups.delay.start: 60
> ups.load: 1
> ups.mfr: POWERCOM Co.,LTD
> ups.model: HID UPS Battery
> ups.productid: 0004
> ups.serial: 004-0D9F-000
> ups.status: OL
> ups.test.result: Done and passed
> ups.timer.shutdown: 269
> ups.timer.start: 0
> ups.vendorid: 0d9f
> root at vTEMPLATE8:/var/log# upsc ups at localhost
> battery.charge: 100
> battery.charge.low: 70
> battery.charge.warning: 30
> battery.mfr.date: 2014/01/15
> battery.runtime: 800
> battery.type: PbAc
> device.mfr: POWERCOM Co.,LTD
> device.model: HID UPS Battery
> device.serial: 004-0D9F-000
> device.type: ups
> driver.debug: 0
> driver.flag.allow_killpower: 0
> driver.flag.ignorelb: enabled
> driver.name: usbhid-ups
> driver.parameter.offdelay: 30
> driver.parameter.ondelay: 60
> driver.parameter.override.battery.charge.low: 70
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 0004
> driver.parameter.synchronous: auto
> driver.parameter.vendorid: 0d9f
> driver.state: quiet
> driver.version: 2.8.2
> driver.version.data: PowerCOM HID 0.7
> driver.version.internal: 0.53
> driver.version.usb: libusb-1.0.26 (API: 0x1000109)
> input.frequency: 50.0
> input.voltage: 224.0
> input.voltage.nominal: 220
> output.frequency: 50.0
> output.voltage: 224.0
> output.voltage.nominal: 220
> ups.beeper.status: enabled
> ups.date: 2014/01/15
> ups.delay.shutdown: 30
> ups.delay.start: 60
> ups.load: 1
> ups.mfr: POWERCOM Co.,LTD
> ups.model: HID UPS Battery
> ups.productid: 0004
> ups.serial: 004-0D9F-000
> ups.status: OL
> ups.test.result: Done and passed
> ups.timer.shutdown: 89
> ups.timer.start: 0
> ups.vendorid: 0d9f
> root at vTEMPLATE8:/var/log# upsc ups at localhost
> battery.charge: 100
> battery.charge.low: 70
> battery.charge.warning: 30
> battery.mfr.date: 2014/01/15
> battery.runtime: 800
> battery.type: PbAc
> device.mfr: POWERCOM Co.,LTD
> device.model: HID UPS Battery
> device.serial: 004-0D9F-000
> device.type: ups
> driver.debug: 0
> driver.flag.allow_killpower: 0
> driver.flag.ignorelb: enabled
> driver.name: usbhid-ups
> driver.parameter.offdelay: 30
> driver.parameter.ondelay: 60
> driver.parameter.override.battery.charge.low: 70
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 0004
> driver.parameter.synchronous: auto
> driver.parameter.vendorid: 0d9f
> driver.state: quiet
> driver.version: 2.8.2
> driver.version.data: PowerCOM HID 0.7
> driver.version.internal: 0.53
> driver.version.usb: libusb-1.0.26 (API: 0x1000109)
> input.frequency: 50.0
> input.voltage: 226.0
> input.voltage.nominal: 220
> output.frequency: 50.0
> output.voltage: 226.0
> output.voltage.nominal: 220
> ups.beeper.status: enabled
> ups.date: 2014/01/15
> ups.delay.shutdown: 30
> ups.delay.start: 60
> ups.load: 1
> ups.mfr: POWERCOM Co.,LTD
> ups.model: HID UPS Battery
> ups.productid: 0004
> ups.serial: 004-0D9F-000
> ups.status: OL
> ups.test.result: Done and passed
> ups.timer.shutdown: 3148
> ups.timer.start: 0
> ups.vendorid: 0d9f
>
> And strange with timer parametr that are changes cycling:
> ups.timer.shutdown: 3570
> ups.timer.shutdown: 2430
> ups.timer.shutdown: 1710
> ...
> ups.timer.shutdown: 870
> ups.timer.shutdown: 3629
> ups.timer.shutdown: 2729
> ups.timer.shutdown: 1829
> ...
> ups.timer.shutdown: 89
> ups.timer.shutdown: 3148
> ...
>
> the ups.conf are:
> [UPS]
>     driver = usbhid-ups
>     vendorid = 0d9f
>     productid = 0004
> #    powercom_sdcmd_byte_order_fallback
>     port = auto
> #    pollonly = enabled
>     pollinterval = 2
>     pollfreq = 30
>     offdelay = 30
>     ondelay = 60
>     allow_killpower
>     ignorelb
>     override.battery.charge.low = 70
> #    override.battery.runtime.low = 600
>
> 06.05.2025 01:49, Jim Klimov:
>
> At least the "shutdown.return requires a parameter" part *may* be a
> regression of the new "sdcommands" change in v2.8.3,though I don't think
> older code passed any. Maybe something got lost in mass-edit changes
> though.
>
> Can you please double-check with 2.8.2 if its older approach to UPS
> shutdown behaved better?
>
> Jim Klimov
>
> On Tue, May 6, 2025, 00:41 Alexey Korobeinikov <alexey at fseafood.com>
> wrote:
>
>> Hi, my UPS Model Powercom BNT400AP ( made 2017.12 ) on Linux Devuan
>> Daedalus and NUT v2.8.3 (install from source tarball with "configure
>> --with-usb --with-user=nut --with-group=nut --with-libusb=1.0
>> --with-statepath=/run/nut --with-pidpath=/run/nut" options) didn't
>> shutdown itself after OS is shuting down by signal of UPS battary is low.
>>
>> ...
>
>    0.184242     Initiating UPS [UPS] shutdown
>>    0.184257     [D1] loop_shutdown_commands: call
>> do_loop_shutdown_commands() with driver-default sdcommands
>>    0.184267     [D1] Starting
>> do_loop_shutdown_commands(shudown.default), call depth 1...
>>    0.184280     [D1] upsdrv_shutdown...
>>    0.184289     [D1] Starting
>> do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
>>
>> call depth 2...
>>    0.184299     [D1] instcmd(shutdown.return, [NULL])
>>    0.184313     [D3] instcmd: using Path
>> 'UPS.PowerSummary.DelayBeforehutdown'
>>    0.184321     [D2] instcmd: shutdown.return requires an explicit
>> parameter
>>
>>    0.184331     [D1] instcmd(shutdown.reboot, [NULL])
>>    0.184348     [D2] find_nut_info: unknown info type: shutdown.reboot
>>    0.184358     [D3] instcmd: cmdname 'shutdown.reboot' not found;
>> checking for alternatives
>>    0.184371     [D2] instcmd: info element unavailable shutdown.reboot
>>
>>    0.184387     [D1] instcmd(load.off.delay, [NULL])
>>    0.184398     [D2] find_nut_info: unknown info type: load.off.delay
>>    0.184407     [D3] instcmd: cmdname 'load.off.delay' not found;
>> checking for alternatives
>>    0.184418     [D2] instcmd: info element unavailable load.off.delay
>>
>>    0.184428     [D1] instcmd(shutdown.stayoff, [NULL])
>>    0.184438     [D3] instcmd: using Path
>> 'UPS.PowerSummary.DelayBeforehutdown'
>>    0.184449     [D2] instcmd: shutdown.stayoff requires an explicit
>> parameter
>>
>>    0.184462     [D1] Ending
>> do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
>>
>> call
>> depth 2: return-code 2
>>    0.184471     Shutdown failed!
>>    0.184483     [D1] set_exit_flag: raising exit flag due to signal -1
>>    0.184493     [D1] do_loop_shutdown_commands(): command
>> 'shutdown.default' was handled successfully
>>    0.184502     [D1] Ending do_loop_shutdown_commands(shutdown.default),
>> call depth 1: return-code 0
>>    0.184512     UPS [UPS]: shutdown request was successful with
>> 'shutdown.default'
>>    0.184523     [D1] set_exit_flag: raising exit flag due to
>> programmatic abort: EXIT_FAILURE
>>    0.184540     [D1] upsdrv_cleanup...
>>    0.184899     [D1] upsnotify: failed to notify about state
>> NOTIFY_STATE_STOPPING: no notification tech defined, will not spam more
>> about it
>>    0.184936     [D1] On systems without service units, consider `export
>> NUT_QUIET_INIT_UPSNOTIFY=true`
>>
>> I try to use "powercom_sdcmd_byte_order_fallback" option, with same
>> effect.
>>
>> Wat's wrong with my UPS/NUT ?
>> Thank You!
>>
>> --
>> Oleksii Korobeinikov
>>
>>
>>
>>
>> _______________________________________________
>> Nut-upsuser mailing list
>> Nut-upsuser at alioth-lists.debian.net
>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>
>
> --
> З Повагою
> Коробейніков Олексій
> Системний адміністратор
>
> ТОВ "Флагман Сіфуд"
> вул. Броварська 152, смт Велика Димерка
> Київська область, 07442
> р.+38 044 495-88-00
> вн.6101
> м.+38 067 994-40-48
>
>
> _______________________________________________
> Nut-upsuser mailing listNut-upsuser at alioth-lists.debian.nethttps://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>
>
> --
> З Повагою
> Коробейніков Олексій
> Системний адміністратор
>
> ТОВ "Флагман Сіфуд"
> вул. Броварська 152, смт Велика Димерка
> Київська область, 07442
> р.+38 044 495-88-00
> вн.6101