[Nut-upsuser] POWERCOM UPS USB : UPS Shutdown
    Alexey Korobeinikov 
    alexey at fseafood.com
       
    Thu May 15 12:04:19 BST 2025
    
    
  
After reseting usb (usbreset 0d9f:0004), I can connect to UPS. But still 
have problem to shuting down the UPS:
/usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k
Network UPS Tools 2.8.3.1 (development iteration after 2.8.3) - Generic 
HID driver 0.63
USB communication driver (libusb 1.0) 0.50
   0.000000     [D1] upsdrv_makevartable...
   0.000078     [D1] Using USB implementation: libusb-1.0.26 (API: 
0x01000109)
   0.000238     [D3] main_arg: var='driver' val='usbhid-ups'
   0.000253     [D3] main_arg: var='vendorid' val='0d9f'
   0.000272     [D3] main_arg: var='productid' val='0004'
   0.000289     [D3] main_arg: var='port' val='auto'
   0.000310     [D3] main_arg: var='pollinterval' val='2'
...
   0.004914     [D2] Checking device 4 of 10 (0D9F/0004)
   0.019235     [D2] - VendorID: 0d9f
   0.019276     [D2] - ProductID: 0004
   0.019282     [D2] - Manufacturer: POWERCOM Co.,LTD
   0.019288     [D2] - Product: HID UPS Battery
   0.019293     [D2] - Serial Number: 004-0D9F-000
   0.019298     [D2] - Bus: 006
   0.019303     [D2] - Bus Port: 002
   0.019308     [D2] - Device: 003
   0.019313     [D2] - Device release number: 0002
   0.019318     [D2] Trying to match device
   0.019327     [D2] match_function_subdriver (non-SHUT mode): matching 
a device...
   0.019347     [D3] match_function_regex: matching a device...
   0.019420     [D2] Device matches
   0.019438     [D2] Reading configuration descriptor 1 of 1
   0.019479     [D3] libusb_kernel_driver_active() returned 0: Success
   0.019516     [D2] Claimed interface 0 successfully
   0.019533     [D3] nut_libusb_set_altinterface: skipped 
libusb_set_interface_alt_setting(udev, 0, 0)
   0.021265     [D2] Retrieved HID descriptor (expected 9, got 9)
   0.021306     [D3] HID descriptor, method 1: (9 bytes) => 09 21 00 01 
00 01 22 e4 03
   0.021314     [D3] HID descriptor length (method 1) 996
   0.021330     [D4] i=0, extra[i]=09, extra[i+1]=21
   0.021344     [D3] HID descriptor, method 2: (9 bytes) => 09 21 00 01 
00 01 22 e4 03
   0.021369     [D3] HID descriptor length (method 2) 996
   0.021381     [D2] HID descriptor length 996
   0.062245     [D2] Report Descriptor size = 996
   0.062294     [D3] Report Descriptor: (996 bytes) => 05 84 09 04 a1 01 
09 24 a1 02 85 01 09 fe
   0.062308     [D3]  79 01 75 08 95 01 15 00 26 ff 00 b1 22 85 02 09 ff 
79 02 b1 22 05 85 85 05
   0.062322     [D3]  09 89 79 04 b1 22 85 07 09 8b b1 22 85 08 09 2c 25 
03 b1 22 85 09 09 83 25
   0.062335     [D3]  64 b1 22 09 67 b1 22 85 0e 09 66 81 22 09 66 b1 a2 
85 0b 09 8c b1 22 85 0c
   0.062347     [D3]  09 29 b1 a2 85 0d 09 85 75 10 27 ff ff 00 00 b1 a2 
85 37 09 68 81 22 09 68
   0.062363     [D3]  b1 a2 05 84 85 0f 09 57 75 10 16 00 00 27 ff ff 00 
00 b1 a2 85 10 09 56 75
   0.062380     [D3]  20 16 00 00 27 9f 86 01 00 b1 a2 85 11 09 40 75 10 
16 64 00 26 f0 00 b1 22
   0.062395     [D3]  85 12 09 30 75 10 16 00 00 26 40 01 b1 a2 85 2c 09 
36 75 08 25 5a b1 a2 85
   0.062410     [D3]  13 09 5a 75 08 15 00 25 03 b1 a2 09 02 a1 02 05 85 
85 0a 09 44 75 01 15 00
   0.062437     [D3]  25 01 81 a2 09 44 b1 a2 09 45 81 a2 09 45 b1 a2 09 
d0 81 a2 09 d0 b1 a2 09
   0.062455     [D3]  d1 81 a2 09 d1 b1 a2 09 42 81 a2 09 42 b1 a2 09 43 
81 a2 09 43 b1 a2 09 4b
   0.062474     [D3]  81 a2 09 4b b1 a2 09 db 81 a2 09 db b1 a2 05 84 09 
68 81 a2 09 68 b1 a2 09
   0.062491     [D3]  69 81 a2 09 69 b1 a2 09 73 81 a2 09 73 b1 a2 09 65 
81 a2 09 65 b1 a2 95 03
   0.062510     [D3]  81 01 b1 01 95 01 06 86 ff 09 80 81 a2 09 80 b1 a2 
c0 c0 05 84 09 12 a1 00
   0.062526     [D3]  85 15 09 58 75 08 25 66 b1 a2 85 16 09 70 75 08 25 
03 b1 a2 05 85 85 17 09
   0.062544     [D3]  85 75 10 27 ff ff 00 00 b1 a2 85 18 09 66 75 08 15 
00 25 64 b1 a2 05 84 85
   0.062559     [D3]  19 09 40 75 10 16 00 0c 26 00 30 b1 22 85 1a 09 30 
75 10 16 00 09 26 00 24
   0.062577     [D3]  b1 a2 85 1b 09 56 75 20 16 00 00 27 9f 86 01 00 b1 
a2 85 2d 09 36 75 08 25
   0.062594     [D3]  5a b1 a2 c0 05 84 09 1a a1 00 85 1c 09 40 75 10 16 
64 00 26 f0 00 b1 22 85
   0.062612     [D3]  1d 09 30 75 10 16 00 00 26 40 01 b1 a2 85 2e 09 30 
75 10 16 00 00 26 40 01
   0.062627     [D3]  b1 a2 85 1e 09 32 75 08 15 00 25 46 b1 a2 c0 05 84 
09 1c a1 00 85 2f 09 41
   0.062645     [D3]  75 08 15 01 25 0c b1 22 85 1f 09 35 75 08 15 00 25 
64 b1 a2 85 20 09 40 75
   0.062664     [D3]  10 16 64 00 26 f0 00 b1 22 85 21 09 30 75 10 16 00 
00 26 40 01 b1 a2 85 30
   0.062681     [D3]  09 42 75 08 15 32 25 3c b1 22 85 22 09 32 75 08 15 
00 25 46 b1 a2 85 23 09
   0.062699     [D3]  57 75 08 15 00 25 12 b1 a2 85 24 09 56 75 20 16 00 
00 27 9f 86 01 00 b1 a2
   0.062716     [D3]  c0 05 84 85 06 09 01 79 05 b1 a2 85 25 09 5a 75 08 
15 00 25 03 b1 a2 09 02
   0.062736     [D3]  a1 02 05 85 85 26 09 44 75 01 15 00 25 01 b1 a2 09 
45 b1 a2 09 d0 b1 a2 09
   0.062752     [D3]  d1 b1 a2 09 42 b1 a2 09 43 b1 a2 09 4b b1 a2 09 db 
b1 a2 05 84 09 68 b1 a2
   0.062768     [D3]  09 69 b1 a2 09 73 b1 a2 09 65 b1 a2 09 6e b1 a2 09 
6f b1 a2 09 71 b1 a2 06
   0.062791     [D3]  86 ff 09 80 b1 a2 c0 85 27 05 84 09 69 75 08 15 00 
25 01 b1 a2 09 1e a1 00
   0.062807     [D3]  85 a0 09 01 75 08 95 07 15 00 26 ff 00 b1 03 85 a1 
09 01 75 08 95 07 15 00
   0.062835     [D3]  26 ff 00 b1 03 85 a2 09 01 75 08 95 07 15 00 26 ff 
00 b1 03 85 a3 09 01 75
   0.062853     [D3]  08 95 07 15 00 26 ff 00 b1 03 85 a4 09 01 75 08 95 
07 15 00 26 ff 00 b1 03
   0.062871     [D3]  85 a5 09 01 75 08 95 07 15 00 26 ff 00 b1 03 85 a6 
09 01 75 08 95 07 15 00
   0.062889     [D3]  26 ff 00 b1 03 85 a7 09 01 75 08 95 07 15 00 26 ff 
00 b1 03 85 a8 09 01 75
   0.062905     [D3]  08 95 07 15 00 26 ff 00 b1 03 85 a9 09 01 75 08 95 
07 15 00 26 ff 00 b1 03
   0.062923     [D3]  85 aa 09 01 75 08 95 07 15 00 26 ff 00 b1 03 85 ab 
09 01 75 08 95 07 15 00
   0.062940     [D3]  26 ff 00 b1 03 85 ac 09 01 75 08 95 07 15 00 26 ff 
00 b1 03 85 ad 09 01 75
   0.062960     [D3]  08 95 07 15 00 26 ff 00 b1 03 85 ae 09 01 75 08 95 
07 15 00 26 ff 00 b1 03
   0.062977     [D3]  85 31 09 01 75 08 95 01 15 00 26 ff 00 b1 03 85 32 
09 01 75 08 95 01 15 00
   0.062990     [D3]  26 ff 00 b1 03 c0 c0
   0.063197     Using subdriver: PowerCOM HID 0.71
   0.063214     [D1] 102 HID objects found
   0.063229     [D4] Entering libusb_get_report
   0.064157     [D3] Report[get]: (2 bytes) => 01 01
   0.064197     [D1] Path: UPS.PowerSummary.iProduct, Type: Feature, 
ReportID: 0x01, Offset: 0, Size: 8, Value: 1
   0.064209     [D4] Entering libusb_get_report
   0.066271     [D3] Report[get]: (2 bytes) => 02 02
   0.066311     [D1] Path: UPS.PowerSummary.iSerialNumber, Type: 
Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 2
   0.066320     [D4] Entering libusb_get_report
...
   0.186774     [D4] Entering libusb_get_report
   0.188120     nut_libusb_get_report: Success
   0.188164     [D1] Can't retrieve Report 2d: Success
   0.188182     [D4] string_to_path: depth = 3
   0.188197     [D4] HIDGetItemData: FindObject_with_Path() failed to 
locate 'PowercomUPS.PowercomBatterySystem.PowercomVoltage'
   0.188210     [D4] string_to_path: depth = 4
...
   0.188755     Initiating UPS [UPS] shutdown
   0.188770     [D1] loop_shutdown_commands: call 
do_loop_shutdown_commands() with driver-default sdcommands
   0.188780     [D1] Starting 
do_loop_shutdown_commands(shutdown.default), call depth 1...
   0.188791     [D1] upsdrv_shutdown...
   0.188802     [D1] Starting 
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff), 
call depth 2...
   0.188813     [D1] instcmd(shutdown.return, [NULL])
   0.188822     [D3] instcmd: using Path 
'UPS.PowerSummary.DelayBeforeShutdown'
   0.188833     [D2] instcmd: shutdown.return requires an explicit 
parameter
   0.188842     [D1] instcmd(shutdown.reboot, [NULL])
   0.188856     [D2] find_nut_info: unknown info type: shutdown.reboot
   0.188866     [D3] instcmd: cmdname 'shutdown.reboot' not found; 
checking for alternatives
   0.188879     [D2] instcmd: info element unavailable shutdown.reboot
   0.188890     [D1] instcmd(load.off.delay, [NULL])
   0.188902     [D2] find_nut_info: unknown info type: load.off.delay
   0.188911     [D3] instcmd: cmdname 'load.off.delay' not found; 
checking for alternatives
   0.188921     [D2] instcmd: info element unavailable load.off.delay
   0.188935     [D1] instcmd(shutdown.stayoff, [NULL])
   0.188945     [D3] instcmd: using Path 
'UPS.PowerSummary.DelayBeforeShutdown'
   0.188956     [D2] instcmd: shutdown.stayoff requires an explicit 
parameter
   0.188966     [D1] Ending 
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff), 
call depth 2: return-code 2
   0.188974     Shutdown failed!
   0.188986     [D1] set_exit_flag: raising exit flag due to signal -1
   0.188996     [D1] do_loop_shutdown_commands(): command 
'shutdown.default' was handled successfully
   0.189005     [D1] Ending do_loop_shutdown_commands(shutdown.default), 
call depth 1: return-code 0
   0.189014     UPS [UPS]: shutdown request was successful with 
'shutdown.default'
   0.189022     [D1] set_exit_flag: raising exit flag due to 
programmatic abort: EXIT_FAILURE
   0.189040     [D1] upsdrv_cleanup...
   0.189311     [D1] upsnotify: failed to notify about state 
NOTIFY_STATE_STOPPING: no notification tech defined, will not spam more 
about it
   0.189331     [D1] On systems without service units, consider `export 
NUT_QUIET_INIT_UPSNOTIFY=true`
The UPS didn't  shut down, just still BEEP because on battery ( >3 min 
wait )...
13.05.2025 18:31, Jim Klimov:
> Check https://github.com/networkupstools/nut/pull/2955 please.
>
> Jim
>
> On Mon, May 12, 2025 at 12:04 PM Jim Klimov <jimklimov+nut at gmail.com 
> <mailto:jimklimov%2Bnut at gmail.com>> wrote:
>
>     Hoped to look into this just today, if nobody beat me to it yet.
>
>     Jim
>
>     On Mon, May 12, 2025 at 11:54 AM Alexey Korobeinikov
>     <alexey at fseafood.com> wrote:
>
>         Are there any chances that this error can be fixed?
>
>         06.05.2025 18:19, Alexey Korobeinikov:
>>         Hi! Thank You!
>>
>>         The UPS behavior are chages with NUT v.2.8.2 but more strange
>>
>>         After this command (if power cord unpluged)
>>         /usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k
>>
>>         ....
>>         0.188173     [D4] string_to_path: depth = 3
>>            0.188187     [D4] string_to_path: depth = 3
>>            0.188199     [D4] string_to_path: depth = 3
>>            0.188211     [D4] string_to_path: depth = 3
>>            0.188246     [D2] find_nut_info: unknown info type:
>>         load.off.delay
>>            0.188267     [D2] find_nut_info: unknown info type:
>>         load.off.delay
>>            0.188280     Initiating UPS shutdown
>>            0.188290     [D1] upsdrv_shutdown...
>>            0.188298     [D1] instcmd(shutdown.return, [NULL])
>>            0.188316     [D3] instcmd: using Path
>>         'UPS.PowerSummary.DelayBeforeShutdown'
>>            0.188332     [D3] powercom_shutdown_nuf: value = (null),
>>         command = 5E00
>>            0.224970     [D3] Report[set]: (3 bytes) => 0f 00 5e
>>            0.225003     [D4] Set report succeeded
>>            0.225012     [D3] instcmd: SUCCEED
>>
>>         The UPS are start double beeping every 2 seconds, but didn't
>>         turn off himself ( 2 minutes wait )
>>         UPS are still beeping if power are restored
>>
>>         Status are:
>>         # upsc ups at localhost
>>         battery.charge: 100
>>         battery.charge.low: 70
>>         battery.charge.warning: 30
>>         battery.mfr.date: 2014/01/15
>>         battery.runtime: 800
>>         battery.type: PbAc
>>         device.mfr: POWERCOM Co.,LTD
>>         device.model: HID UPS Battery
>>         device.serial: 004-0D9F-000
>>         device.type: ups
>>         driver.debug: 0
>>         driver.flag.allow_killpower: 0
>>         driver.flag.ignorelb: enabled
>>         driver.name <http://driver.name>: usbhid-ups
>>         driver.parameter.offdelay: 30
>>         driver.parameter.ondelay: 60
>>         driver.parameter.override.battery.charge.low: 70
>>         driver.parameter.pollfreq: 30
>>         driver.parameter.pollinterval: 2
>>         driver.parameter.port: auto
>>         driver.parameter.productid: 0004
>>         driver.parameter.synchronous: auto
>>         driver.parameter.vendorid: 0d9f
>>         driver.state: quiet
>>         driver.version: 2.8.2
>>         driver.version.data: PowerCOM HID 0.7
>>         driver.version.internal: 0.53
>>         driver.version.usb: libusb-1.0.26 (API: 0x1000109)
>>         input.frequency: 50.0
>>         input.voltage: 224.0
>>         input.voltage.nominal: 220
>>         output.frequency: 50.0
>>         output.voltage: 224.0
>>         output.voltage.nominal: 220
>>         ups.beeper.status: enabled
>>         ups.date: 2014/01/15
>>         ups.delay.shutdown: 30
>>         ups.delay.start: 60
>>         ups.load: 1
>>         ups.mfr: POWERCOM Co.,LTD
>>         ups.model: HID UPS Battery
>>         ups.productid: 0004
>>         ups.serial: 004-0D9F-000
>>         ups.status: OL
>>         ups.test.result: Done and passed
>>         ups.timer.shutdown: 269
>>         ups.timer.start: 0
>>         ups.vendorid: 0d9f
>>         root at vTEMPLATE8:/var/log# upsc ups at localhost
>>         battery.charge: 100
>>         battery.charge.low: 70
>>         battery.charge.warning: 30
>>         battery.mfr.date: 2014/01/15
>>         battery.runtime: 800
>>         battery.type: PbAc
>>         device.mfr: POWERCOM Co.,LTD
>>         device.model: HID UPS Battery
>>         device.serial: 004-0D9F-000
>>         device.type: ups
>>         driver.debug: 0
>>         driver.flag.allow_killpower: 0
>>         driver.flag.ignorelb: enabled
>>         driver.name <http://driver.name>: usbhid-ups
>>         driver.parameter.offdelay: 30
>>         driver.parameter.ondelay: 60
>>         driver.parameter.override.battery.charge.low: 70
>>         driver.parameter.pollfreq: 30
>>         driver.parameter.pollinterval: 2
>>         driver.parameter.port: auto
>>         driver.parameter.productid: 0004
>>         driver.parameter.synchronous: auto
>>         driver.parameter.vendorid: 0d9f
>>         driver.state: quiet
>>         driver.version: 2.8.2
>>         driver.version.data: PowerCOM HID 0.7
>>         driver.version.internal: 0.53
>>         driver.version.usb: libusb-1.0.26 (API: 0x1000109)
>>         input.frequency: 50.0
>>         input.voltage: 224.0
>>         input.voltage.nominal: 220
>>         output.frequency: 50.0
>>         output.voltage: 224.0
>>         output.voltage.nominal: 220
>>         ups.beeper.status: enabled
>>         ups.date: 2014/01/15
>>         ups.delay.shutdown: 30
>>         ups.delay.start: 60
>>         ups.load: 1
>>         ups.mfr: POWERCOM Co.,LTD
>>         ups.model: HID UPS Battery
>>         ups.productid: 0004
>>         ups.serial: 004-0D9F-000
>>         ups.status: OL
>>         ups.test.result: Done and passed
>>         ups.timer.shutdown: 89
>>         ups.timer.start: 0
>>         ups.vendorid: 0d9f
>>         root at vTEMPLATE8:/var/log# upsc ups at localhost
>>         battery.charge: 100
>>         battery.charge.low: 70
>>         battery.charge.warning: 30
>>         battery.mfr.date: 2014/01/15
>>         battery.runtime: 800
>>         battery.type: PbAc
>>         device.mfr: POWERCOM Co.,LTD
>>         device.model: HID UPS Battery
>>         device.serial: 004-0D9F-000
>>         device.type: ups
>>         driver.debug: 0
>>         driver.flag.allow_killpower: 0
>>         driver.flag.ignorelb: enabled
>>         driver.name <http://driver.name>: usbhid-ups
>>         driver.parameter.offdelay: 30
>>         driver.parameter.ondelay: 60
>>         driver.parameter.override.battery.charge.low: 70
>>         driver.parameter.pollfreq: 30
>>         driver.parameter.pollinterval: 2
>>         driver.parameter.port: auto
>>         driver.parameter.productid: 0004
>>         driver.parameter.synchronous: auto
>>         driver.parameter.vendorid: 0d9f
>>         driver.state: quiet
>>         driver.version: 2.8.2
>>         driver.version.data: PowerCOM HID 0.7
>>         driver.version.internal: 0.53
>>         driver.version.usb: libusb-1.0.26 (API: 0x1000109)
>>         input.frequency: 50.0
>>         input.voltage: 226.0
>>         input.voltage.nominal: 220
>>         output.frequency: 50.0
>>         output.voltage: 226.0
>>         output.voltage.nominal: 220
>>         ups.beeper.status: enabled
>>         ups.date: 2014/01/15
>>         ups.delay.shutdown: 30
>>         ups.delay.start: 60
>>         ups.load: 1
>>         ups.mfr: POWERCOM Co.,LTD
>>         ups.model: HID UPS Battery
>>         ups.productid: 0004
>>         ups.serial: 004-0D9F-000
>>         ups.status: OL
>>         ups.test.result: Done and passed
>>         ups.timer.shutdown: 3148
>>         ups.timer.start: 0
>>         ups.vendorid: 0d9f
>>
>>         And strange with timer parametr that are changes cycling:
>>         ups.timer.shutdown: 3570
>>         ups.timer.shutdown: 2430
>>         ups.timer.shutdown: 1710
>>         ...
>>         ups.timer.shutdown: 870
>>         ups.timer.shutdown: 3629
>>         ups.timer.shutdown: 2729
>>         ups.timer.shutdown: 1829
>>         ...
>>         ups.timer.shutdown: 89
>>         ups.timer.shutdown: 3148
>>         ...
>>
>>         the ups.conf are:
>>         [UPS]
>>             driver = usbhid-ups
>>             vendorid = 0d9f
>>             productid = 0004
>>         #    powercom_sdcmd_byte_order_fallback
>>             port = auto
>>         #    pollonly = enabled
>>             pollinterval = 2
>>             pollfreq = 30
>>             offdelay = 30
>>             ondelay = 60
>>             allow_killpower
>>             ignorelb
>>             override.battery.charge.low = 70
>>         #    override.battery.runtime.low = 600
>>
>>         06.05.2025 01:49, Jim Klimov:
>>>         At least the "shutdown.return requires a parameter" part
>>>         *may* be a regression of the new "sdcommands" change in
>>>         v2.8.3,though I don't think older code passed any. Maybe
>>>         something got lost in mass-edit changes though.
>>>
>>>         Can you please double-check with 2.8.2 if its older approach
>>>         to UPS shutdown behaved better?
>>>
>>>         Jim Klimov
>>>
>>>         On Tue, May 6, 2025, 00:41 Alexey Korobeinikov
>>>         <alexey at fseafood.com> wrote:
>>>
>>>             Hi, my UPS Model Powercom BNT400AP ( made 2017.12 ) on
>>>             Linux Devuan
>>>             Daedalus and NUT v2.8.3 (install from source tarball
>>>             with "configure
>>>             --with-usb --with-user=nut --with-group=nut
>>>             --with-libusb=1.0
>>>             --with-statepath=/run/nut --with-pidpath=/run/nut"
>>>             options) didn't
>>>             shutdown itself after OS is shuting down by signal of
>>>             UPS battary is low.
>>>
>>>             ...
>>>
>>>                0.184242     Initiating UPS [UPS] shutdown
>>>                0.184257     [D1] loop_shutdown_commands: call
>>>             do_loop_shutdown_commands() with driver-default sdcommands
>>>                0.184267     [D1] Starting
>>>             do_loop_shutdown_commands(shudown.default), call depth 1...
>>>                0.184280     [D1] upsdrv_shutdown...
>>>                0.184289     [D1] Starting
>>>             do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
>>>
>>>             call depth 2...
>>>                0.184299     [D1] instcmd(shutdown.return, [NULL])
>>>                0.184313     [D3] instcmd: using Path
>>>             'UPS.PowerSummary.DelayBeforehutdown'
>>>                0.184321     [D2] instcmd: shutdown.return requires
>>>             an explicit
>>>             parameter
>>>
>>>                0.184331     [D1] instcmd(shutdown.reboot, [NULL])
>>>                0.184348     [D2] find_nut_info: unknown info type:
>>>             shutdown.reboot
>>>                0.184358     [D3] instcmd: cmdname 'shutdown.reboot'
>>>             not found;
>>>             checking for alternatives
>>>                0.184371     [D2] instcmd: info element unavailable
>>>             shutdown.reboot
>>>
>>>                0.184387     [D1] instcmd(load.off.delay, [NULL])
>>>                0.184398     [D2] find_nut_info: unknown info type:
>>>             load.off.delay
>>>                0.184407     [D3] instcmd: cmdname 'load.off.delay'
>>>             not found;
>>>             checking for alternatives
>>>                0.184418     [D2] instcmd: info element unavailable
>>>             load.off.delay
>>>
>>>                0.184428     [D1] instcmd(shutdown.stayoff, [NULL])
>>>                0.184438     [D3] instcmd: using Path
>>>             'UPS.PowerSummary.DelayBeforehutdown'
>>>                0.184449     [D2] instcmd: shutdown.stayoff requires
>>>             an explicit
>>>             parameter
>>>
>>>                0.184462     [D1] Ending
>>>             do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
>>>
>>>             call
>>>             depth 2: return-code 2
>>>                0.184471     Shutdown failed!
>>>                0.184483     [D1] set_exit_flag: raising exit flag
>>>             due to signal -1
>>>                0.184493     [D1] do_loop_shutdown_commands(): command
>>>             'shutdown.default' was handled successfully
>>>                0.184502     [D1] Ending
>>>             do_loop_shutdown_commands(shutdown.default),
>>>             call depth 1: return-code 0
>>>                0.184512     UPS [UPS]: shutdown request was
>>>             successful with
>>>             'shutdown.default'
>>>                0.184523     [D1] set_exit_flag: raising exit flag
>>>             due to
>>>             programmatic abort: EXIT_FAILURE
>>>                0.184540     [D1] upsdrv_cleanup...
>>>                0.184899     [D1] upsnotify: failed to notify about
>>>             state
>>>             NOTIFY_STATE_STOPPING: no notification tech defined,
>>>             will not spam more about it
>>>                0.184936     [D1] On systems without service units,
>>>             consider `export
>>>             NUT_QUIET_INIT_UPSNOTIFY=true`
>>>
>>>             I try to use "powercom_sdcmd_byte_order_fallback"
>>>             option, with same effect.
>>>
>>>             Wat's wrong with my UPS/NUT ?
>>>             Thank You!
>>>
>>>             -- 
>>>             Oleksii Korobeinikov
>>>
>>>
>>>
>>>
>>>             _______________________________________________
>>>             Nut-upsuser mailing list
>>>             Nut-upsuser at alioth-lists.debian.net
>>>             https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>>
>>
>>         -- 
>>         З Повагою
>>         Коробейніков Олексій
>>         Системний адміністратор
>>
>>         ТОВ "Флагман Сіфуд"
>>         вул. Броварська 152, смт Велика Димерка
>>         Київська область, 07442
>>         р.+38 044 495-88-00
>>         вн.6101
>>         м.+38 067 994-40-48
>>
>>         _______________________________________________
>>         Nut-upsuser mailing list
>>         Nut-upsuser at alioth-lists.debian.net
>>         https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>
>         -- 
>         З Повагою
>         Коробейніков Олексій
>         Системний адміністратор
>
>         ТОВ "Флагман Сіфуд"
>         вул. Броварська 152, смт Велика Димерка
>         Київська область, 07442
>         р.+38 044 495-88-00
>         вн.6101
>         м.+38 067 994-40-48
>
-- 
З Повагою
Коробейніков Олексій
Системний адміністратор
ТОВ "Флагман Сіфуд"
вул. Броварська 152, смт Велика Димерка
Київська область, 07442
р.+38 044 495-88-00
вн.6101
м.+38 067 994-40-48
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20250515/215edbf8/attachment-0001.htm>
    
    
More information about the Nut-upsuser
mailing list