[Nut-upsuser] UPS not shutting down, no syslogs; no wall messages plus other problems

M Man mman22 at hotmail.com
Mon Aug 10 11:57:45 BST 2026


Thanks for your replies 

Tried putting killpower file (with upsmon-shutdown-file string) in /run/nut/killpower since
upsmon.conf has :-
POWERDOWNFLAG "/run/nut/killpower"

and nothing happens - even tried in /etc/killpower and adjusted POWERDOWNFLAG

Its as though only a part of the nut "system"  is working, especially on the primary
(no syslogs, no walls, no calling of the upssched-cmd script (no logs))

I'm sure some of the errors shown in the /var/log/messages are possible problems ?

Aug 10 12:46:29 ipfire usbhid-ups[2155]: Listening on socket /var/state/ups/usbhid-ups-apc
Aug 10 12:46:29 ipfire usbhid-ups[2159]: Startup successful
Aug 10 12:46:29 ipfire usbhid-ups[2159]: upsnotify: notify about state NOTIFY_STATE_READY_WITH_PID with libsystemd: was requested, but not running as a service unit now, will not spam more about it
Aug 10 12:46:29 ipfire usbhid-ups[2159]: upsnotify: failed to notify about state NOTIFY_STATE_READY_WITH_PID: no notification tech defined, will not spam more about it
Aug 10 12:46:29 ipfire usbhid-ups[2159]: upsnotify: logged the systemd watchdog situation once, will not spam more about it
Aug 10 12:46:29 ipfire upsd[2160]: listening on 0.0.0.0 port 3493
Aug 10 12:46:29 ipfire upsd[2160]: Connected to UPS [apc]: usbhid-ups-apc
Aug 10 12:46:29 ipfire upsd[2160]: Found 1 UPS defined in ups.conf
Aug 10 12:46:29 ipfire usbhid-ups[2159]: sock_connect: enabling asynchronous mode (auto)
Aug 10 12:46:29 ipfire upsd[2161]: Startup successful
Aug 10 12:46:29 ipfire upsd[2161]: upsnotify: notify about state NOTIFY_STATE_READY_WITH_PID with libsystemd: was requested, but not running as a service unit now, will not spam more about it
Aug 10 12:46:29 ipfire upsd[2161]: upsnotify: failed to notify about state NOTIFY_STATE_READY_WITH_PID: no notification tech defined, will not spam more about it
Aug 10 12:46:29 ipfire upsd[2161]: upsnotify: logged the systemd watchdog situation once, will not spam more about it
Aug 10 12:46:29 ipfire upsmon[2163]: Startup successful
Aug 10 12:46:29 ipfire upsmon[2163]: OS user = not found




________________________________________
From: Nut-upsuser <nut-upsuser-bounces+mman22=hotmail.com at alioth-lists.debian.net> on behalf of Robert Nichols via Nut-upsuser <nut-upsuser at alioth-lists.debian.net>
Sent: Monday, August 10, 2026 02:52
To: nut-upsuser at alioth-lists.debian.net <nut-upsuser at alioth-lists.debian.net>
Subject: Re: [Nut-upsuser] UPS not shutting down, no syslogs; no wall messages plus other problems


On 8/9/26 09:24, Greg Troxel via Nut-upsuser wrote:
> The secondary shut down due to lack of comms from primary.
>
> The primary appears to have noticed it should shutdown but something is
> not right.
>
> Generally the system up/down scripts need to notice that the killpower
> flag file has been set.  That requires a lot of things, including that
> the filesystem it is written to have the right permissions and that it
> still be mounted.
>
> You should be able to test by first getting a shell as user nut, and
> then "touch /var/run/nut/killpower".  If that doesn't work, figure out
> why and fix that before continuing.  Then run the shutdown command
> manually.

According to some hard-to-find docs, that file will be ignored unless it
contains the magic string "upsmon-shutdown-file" (without the quotes, of
course). That string is found in the file /usr/sbin/upsmon.

-- 
Bob Nichols     "NOSPAM" is really part of my email address.
                 Do NOT delete it.


_______________________________________________
Nut-upsuser mailing list
Nut-upsuser at alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser