[Nut-upsuser] Examples of PDU integration?
Greg Troxel
gdt at lexort.com
Mon Aug 17 17:31:59 BST 2026
"Kevin P. Fleming via Nut-upsuser" <nut-upsuser at alioth-lists.debian.net>
writes:
> On Mon, Aug 17, 2026, at 11:24, Greg Troxel via Nut-upsuser wrote:
>> How do you get those machines to come back on when power is on and say
>> stable for an hour?
>
> The PDUs have the ability to delay power-on of individual ports, so
> the ones that need to come up 'after the core' are delayed by 10-15
> minutes. The PDUs don't know about power stability though, only
> availability, but they don't receive power until the UPS thinks the
> power is stable enough (and there's a decent amount of battery
> charge).
Sorry, I meant that differently:
If you aren't using an ePDU, and you just "shutdown -p" the host, and
say that power comes back before the UPS runs out (because, on
important-loads-only, it lasted long enough), how does the host that
shutdown restart? In this case, an ePDU with commanded power off and
power on would solve the problem.
More information about the Nut-upsuser
mailing list