[Nut-upsuser] Bluetti as a UPS?
Bill Gee
bgee at campercaver.net
Tue Sep 8 15:55:54 BST 2026
I don't have a way to do a controlled discharge at 25 amps. The best I
can do on my test jig is about 6 amps. This is mainly due to a limit on
the relay contacts which have a max rating of 10 amps DC.
When I bought the current batteries back in February, I ran them through
my test jig using a 4 ohm load resistor and 11.0 volt cutoff. With that
they ran for a bit over 9 hours and delivered around 31 amp-hours. I
figured with a rating of 35ah that they were at least in the ball park.
Those ratings are not an exact science ...
How do I change the shutdown to trigger at 22volts? That has to be a
NUT setting. The display on the UPS says it has 15 minutes of runtime.
A query from NUT shows variable runtime numbers in the range of about
950 to 1100 seconds. Here is a partial dump from NUT:
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.date: 2001/09/25
battery.mfr.date: 2026/02/13
battery.runtime: 1107
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 26.9
battery.voltage.nominal: 24.0
ups.beeper.status: disabled
ups.delay.shutdown: 20
ups.firmware: 865.L5 .D
ups.firmware.aux: L5
ups.load: 37
ups.mfr: American Power Conversion
ups.mfr.date: 2015/06/18
ups.model: Back-UPS RS 1500G
ups.productid: 0002
ups.realpower.nominal: 865
ups.serial: 3B1525X12484
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d
Even if I can figure out a way to get these batteries to really run, the
runtime will still only be in the range of 45 minutes. An
improvement, but nothing like what a 2kwh power bank might offer. My
calculation shows that two 35ah 12 volt lead-acid batteries will store
around 400 watt-hours of energy, and might deliver only a bit more than
half of that.
Your point about BlueTooth Disease is well taken! I agree completely.
I have an Android tablet but not a smartphone, so running that app might
not work for me anyway. Another person commented that his EcoFlow works
with recent versions of usbhid.
==========
Bill Gee
On 9/8/26 8:13 AM, Greg Troxel wrote:
> Bill Gee <bgee at campercaver.net> writes:
>
>> I have been getting very frustrated by the short runtime of my main
>> UPS. It is an APC BR1500G. I have a pair of 35ah batteries on it,
>> but even so it runs for only 10 minutes. The batteries are good
>> (independent testing) and the load is only 350 watts. I think the UPS
>> runtime calibration just does not work.
>
> Did the testing do a controlled discharge at 25A and measure the
> capacity to 10.5V?
>
> Change your shutdown to trigger at 22V, instead of remaining lifetime.
> I suggest logging battery voltage and claimed remaining runtime, and
> doing a test with a simulated failure, graphing that, and posting it for
> comment.
>
>> Recently I noticed that some models of Bluetti power bank, such as
>> AC200L and Fridge, have a "UPS" feature. They boast of switching time
>> under 10ms in event of a power failure on the AC mains. The energy
>> capacity is around 2kwh which should run my load for three to four
>> hours. Expansion batteries can be added. And the price is not much
>> different from a brand new 1500 VA traditional UPS.
>
> That's interesting. The first thing I checked was the battery
> technology. Units like this used to have Lithium ion and that would
> seem dangerous. This says it is LiFePO4. It claims listing to UL2743.
>
>> Has anyone used one of these as a computer UPS?
>
> not me :-)
>
>> Is there a way to have NUT monitor it?
>
> It looks like bluetooth/app, the modern disease. I would suggest
> contacting bluetti, exlaining NUT, and asking for protocol details.
> I suspect if you asked a lot the manufacturers of UL listed LiFePO4
> power banks, one of them might end up being reasonable.
More information about the Nut-upsuser