I've just commited something in the trunk.<br>It works for newhidups, but I've not tested it much yet...<br><br>For the recall, the need is to have a special powering order of the outlets at boot time.<br><br>Use case:<br>
- we have two outlets, identified in the nut tree as outlet.1 and outlet.2<br>- we want to power up outlet.1 10 sec. after the UPS has restarted its _output_, and outlet.2 20 sec. after the UPS has restarted its _output_<br>
<br clear="all">How to set this up (while waiting for docs/powersave.txt completion):<br>- configure the ups {on,off}delay<br>driver.parameter.offdelay: 90<br>driver.parameter.ondelay: 120<br>This means that, in the end of the shutdown process, we will send an order to poweroff the ups 90 sec later. 
<br>When the power will be restored, the ups will wait for 30 more seconds (120 - 90), and will then power up output.<br>- 10 seconds later, outlet.1 will be powered up<br>- 10 more seconds later, outlet.2 will be powered up
<br>
<br>enjoy, and remember that it's still to be completed.<br>Feedback welcome.<br><br>Arnaud<br>-- <br>Linux / Unix Expert - MGE UPS SYSTEMS - R&amp;D Dpt<br>Network UPS Tools (NUT) Project Leader - <a href="http://www.networkupstools.org/">