<div style="line-height:1.7;color:#000000;font-size:14px;font-family:arial">Hi, Charles!<br><br><pre>>
>> However, it seemed that the APC UPS is not recognized by usbhid-ups as long as the Cyper-power UPS is also plugged to the same system. Is that behavior correct?
>
>usbhid-ups will try to connect to the first PDC HID UPS that it finds, but if the CyberPower UPS prevents either UPS from being recognized, then no, that's not expected.<br><br>Situation 1:<br>Step 1: APC UPS plugged<br>Step 2: Cyber-power UPS pluged<br>Step 3: upsdrvctl start, Cyper-power UPS recognized<br><br>Situation2:<br>Step 1: APC UPS plugged<br>Step 2: upsdrvctl start, APC UPS recognized<br>Step 3: upsdrvctl stop<br>Step 4: Cyber-power UPS pluged<br>Step 5: upsdrvctl start, Cyper-power UPS recognized<br></pre><br>Situation3:<br>
Step 1: Cyber-power UPS plugged<br>
Step 2: upsdrvctl start, Cyber-power UPS recognized<br>
Step 3: upsdrvctl stop<br>
Step 4: APC UPS pluged<br>Step 5: upsdrvctl start, Cyper-power UPS recognized<br><br>I check /proc/bus/usb/device, the cyper-ups is always ahead of the UPS one if thay are all plugged. <br>
<br>
That comes another question: If two UPS device with different driver
plugged, and the two drivers are both configured, are they both
recognized?<pre><br> >
>You can used the vendorid or productid parameters (see 'man usbhid-ups' or docs/man/usbhid-ups.txt) to point usbhid-ups to one or the other.
>
I have only read of information of upsd pointed from User Manual. I will read and learn more about that.
>
<br>--<br>Andrew Chang<br>2012-03-11