<HTML><BODY>Hello,<br><br>sorry for messing up the things. I mean many copies of the same text<br>in my previous message and mixing up the command names, it turned<br>out that I forgot the protocol details after so many years.<br><br>I found my records, connected a serial terminal to the UPS and found<br>that the device itself works as expected so my problem cannot be<br>explained with device incompatibility.<br><br>Below is excerpt from my session. After "//" characters go my comments,<br>these of course were not typed in.<br><br>Q1<br>(205.7 225.1 230.7 015 50.1 2.28 41.5 00000001<br>// 205.7 is the real mains voltage, this is the problem of mains not the device<br>F<br>#230.0 013 096.0 50.0<br>S10R0003<br>ACK<br>// UPS has shut down in 10 minues and restored power after 3 minutes,<br>// as expected<br>S03R0001<br>ACK<br>C<br>ACK<br>// Shutdown has been successfully cancelled<br>S03R0001<br>ACK<br>// UPS has shut down after 3 minutes and restored after 1 minute, as expected<br>S.7R0001<br>ACK<br>// UPS has shut down after 42 second and restored after 1 minute, as expected.<br><br>I see no problem with how the device communicates the Blazer/Megatec protocol.<br>I must have found a bug in the driver.<br><br>Regards,<br>Alexander.<br></BODY></HTML>