Alfred Ganz wrote:
> 
> Peter,
> 
> Here are the transitions that I have tested with your latest changes
> (on the APC/Back-UPS ES 650):
> 1) OL ==> OB DISCHRG followed by OB DISCHRG ==> OL (no CHRG inbetween)
> 2) OL CHRG ==> OL
> 3) OL CHRG ==> OL CHRG LB (by manipulating battery.charge.low)
> 4) OL CHRG LB ==> OL CHRG (i.e. transition from below)
> 5) OB DISCHRG ==> FSD OB DISCHRG LB followed by proper shutdown
> In other words, as far as I can see everything works as expected.
> Also, "load.off" indeed shuts the load on my APC/Back-UPS ES 650 
> instantaneously (not that I intended to test that!).

Excellent! Thanks for the testing. -- Peter