[Nut-upsdev] Newhidups gets unbound after a while
Peter Selinger
selinger at mathstat.dal.ca
Tue May 2 15:31:35 UTC 2006
Strange. So the device first identifies itself as:
Checking device (0463/FFFF) (001/002)
- VendorID: 0463
- ProductID: ffff
- Manufacturer: MGE UPS SYSTEMS
- Product: ELLIPSE
- Serial Number: 1HDF44001
- Bus: 001
But after disconnecting, it identifies itself as:
Checking device (0463/FFFF) (002/002)
- VendorID: 0463
- ProductID: ffff
- Manufacturer: unknown
- Product: unknown
- Serial Number: 1HDF44001
- Bus: 002
In particular, the Manufacturer and Product become "unknown". This is
the reason NUT does not reconnect to the device; it cannot determine
that it is indeed the same device. (Also, in the example above, the
bus changed from 001 to 002, but this is because you plugged the UPS
into a different USB port for the two experiments; it does not bother
NUT).
The question is: why is this happening? I have no idea what might
cause this. Did you try unplugging and replugging the UPS while it is
connected? Will NUT reconnect to it then? Also, did you try unplugging
and replugging the UPS *after* it has disconnected itself? Will NUT
reconnect to it then?
Unfortunately, I am not a USB expert, and these strange behaviors
mystify me.
@Arnaud, do you have any suggestions here?
-- Peter
Patrick Agrain wrote:
>
> At 16:45 02/05/2006, you wrote:
> >Yes, I'd also like to see the log of the initial connection, i.e., the
> >beginning of "newhidups -a ups_on_usb -DD". What is your device's
> >actual vendor/product ID? Is it 0463/FFFF? -- Peter
>
> Hi Peter,
> Thanks to have interest in this.
>
>
> >Vendor/product ID is indeed 0463/FFFF. This is the identification of all
> >available (here) UPS from MGE ( Ellipse, Ellipse ASR and Extreme C models ).
>
> Here are the logs when newhidups starts:
> [root at xa000000 root]# newhidups -a ups_on_usb -DD
> Network UPS Tools: New USB/HID UPS driver 0.28 (2.0.3)
>
> debug level is '2'
> Checking device (0000/0000) (001/001)
> - VendorID: 0000
> - ProductID: 0000
> - Manufacturer: unknown
> - Product: unknown
> - Serial Number: unknown
> - Bus: 001
> Trying to match device
> Device does not match - skipping
> Checking device (0463/FFFF) (001/002)
> - VendorID: 0463
> - ProductID: ffff
> - Manufacturer: MGE UPS SYSTEMS
> - Product: ELLIPSE
> - Serial Number: 1HDF44001
> - Bus: 001
> Trying to match device
> Device matches
> failed to claim USB device, trying 2 more time(s)...
> detaching kernel driver from USB device...
> trying again to claim USB device...
> HID descriptor retrieved (Reportlen = 769)
> Report descriptor retrieved (Reportlen = 769)
> Found HID device
> Report Descriptor size = 769
> Detected a UPS: MGE UPS SYSTEMS/ELLIPSE
> Using subdriver: MGE HID 0.8
> Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, Value: 1.000000
> Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, Value: 1.000000
> Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, Value:
> 0.000000
> Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
> Feature, Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.Good, Type: Feature, Value: 1.000000
> Path: UPS.PowerSummary.PresentStatus.Undefined, Type: Feature, Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, Value: 1.000000
> Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, Value: 1.000000
> Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
> Input, Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.Good, Type: Input, Value: 1.000000
> Path: UPS.PowerSummary.PresentStatus.Undefined, Type: Input, Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature,
> Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.OverLoad, Type: Feature, Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, Value:
> 0.000000
> Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, Value:
> 0.000000
> Path: UPS.PowerSummary.PresentStatus.Undefined, Type: Feature, Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, Value:
> 0.000000
> Path: UPS.PowerSummary.PresentStatus.OverLoad, Type: Input, Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, Value:
> 0.000000
> Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, Value:
> 0.000000
> Path: UPS.PowerSummary.PresentStatus.Undefined, Type: Input, Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature,
> Value: 0.000000
> Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, Value:
> 0.000000
> Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, Value: 100.000000
> Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, Value: 3406.000000
> Path: UPS.PowerSummary.RemainingCapacity, Type: Input, Value: 100.000000
> Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, Value: 3406.000000
> Path: UPS.PowerSummary.RemainingCapacityLimitSetting, Type: Feature, Value:
> 30.000000
> Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, Value: 3406.000000
> Path: UPS.PowerSummary.PercentLoad, Type: Feature, Value: 1.000000
> Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, Value: 30.000000
> Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, Value: -1.000000
> Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, Value: -10.000000
> Path: UPS.PowerSummary.CapacityMode, Type: Feature, Value: 2.000000
> Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, Value: 1.000000
> Path: UPS.PowerSummary.DesignCapacity, Type: Feature, Value: 100.000000
> Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, Value: 100.000000
> Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, Value: 5.000000
> Path: UPS.PowerSummary.iManufacturer, Type: Feature, Value: 1.000000
> Path: UPS.PowerSummary.iProduct, Type: Feature, Value: 2.000000
> Path: UPS.PowerSummary.iSerialNumber, Type: Feature, Value: 4.000000
> Path: UPS.PowerSummary.PowerSummaryID, Type: Feature, Value: 1.000000
> Path: UPS.PowerSummary.FlowID, Type: Feature, Value: 4.000000
> Path: UPS.PowerSummary.iModel, Type: Feature, Value: 3.000000
> Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, Value: 2.000000
> Path: UPS.PowerSummary.AudibleAlarmControl, Type: Input, Value: 2.000000
> Path: UPS.OutletSystem.OutletSystemID, Type: Feature, Value: 1.000000
> Path: UPS.OutletSystem.Outlet.00ff0001.OutletID, Type: Feature, Value: 1.000000
> Path: UPS.OutletSystem.Outlet.00ff0001.FlowID, Type: Feature, Value: 4.000000
> Path: UPS.OutletSystem.Outlet.00ff0001.PresentStatus.Switchable, Type:
> Feature, Value: 0.000000
> Path: UPS.OutletSystem.Outlet.00ff0002.OutletID, Type: Feature, Value: 2.000000
> Path: UPS.OutletSystem.Outlet.00ff0002.FlowID, Type: Feature, Value: 1.000000
> Path: UPS.OutletSystem.Outlet.00ff0002.PresentStatus.Switchable, Type:
> Feature, Value: 0.000000
> Path: UPS.Flow.00ff0004.FlowID, Type: Feature, Value: 4.000000
> Path: UPS.Flow.00ff0004.ConfigFrequency, Type: Feature, Value: 50.000000
> Path: UPS.Flow.00ff0004.ConfigApparentPower, Type: Feature, Value: 1500.000000
> Path: UPS.Flow.00ff0004.ConfigVoltage, Type: Feature, Value: 230.000000
> Path: UPS.PowerConverter.PowerConverterID, Type: Feature, Value: 0.000000
> Path: UPS.PowerConverter.Output.0084001d, Type: Feature, Value: 0.000000
> Path: UPS.PowerConverter.Output.Voltage, Type: Feature, Value: 230.000000
> Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, Value:
> 184.000000
> Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, Value:
> 264.000000
> Path: UPS.ffff0018.ffff0019, Type: Feature, Value: 1.000000
> Path: UPS.ffff0018.ffff001a.00ff0001.ffff0090, Type: Feature, Value: 0.000000
> Path: UPS.ffff0018.ffff001a.00ff0001.ffff001b, Type: Feature, Value: 1.000000
> Path: UPS.ffff0018.ffff001a.00ff0001.ffff0094, Type: Feature, Value: 0.000000
> Path: UPS.ffff0018.ffff001a.00ff0001.ffff0092, Type: Feature, Value: 0.000000
> Path: UPS.ffff0018.ffff001a.00ff0001.ffff0091, Type: Feature, Value:
> -12298864.000000
> Path: UPS.ffff0018.ffff001a.00ff0001.PresentStatus.ffff0093, Type: Feature,
> Value: 0.000000
> Path: UPS.ffff0018.ffff001a.00ff0001.PresentStatus.ffff0093, Type: Input,
> Value: 0.000000
> Path: UPS.ffff0018.ffff001a.00ff0002.ffff0090, Type: Feature, Value: 0.000000
> Path: UPS.ffff0018.ffff001a.00ff0002.ffff001b, Type: Feature, Value: 2.000000
> Path: UPS.ffff0018.ffff001a.00ff0002.ffff0094, Type: Feature, Value: 0.000000
> Path: UPS.ffff0018.ffff001a.00ff0002.ffff0092, Type: Feature, Value: 0.000000
> Path: UPS.ffff0018.ffff001a.00ff0002.ffff0091, Type: Feature, Value:
> -16347728.000000
> Path: UPS.ffff0018.ffff001a.00ff0002.PresentStatus.ffff0093, Type: Feature,
> Value: 0.000000
> Path: UPS.ffff0018.ffff001a.00ff0002.PresentStatus.ffff0093, Type: Input,
> Value: 0.000000
> Path: UPS.BatterySystem.Battery.AudibleAlarmControl, Type: Feature, Value:
> 1.000000
> entering identify_ups(0x0463, 0xffff)
>
> -> String: 1500 (len = 4/4)
> get_model_name(ELLIPSE, 1500)
>
> comparing with: ellipse 300
> comparing with: ellipse 500
> comparing with: ellipse 650
> comparing with: ellipse 800
> comparing with: ellipse 1200
> comparing with: ellipse premium 500
> comparing with: ellipse premium 650
> comparing with: ellipse premium 800
> comparing with: ellipse premium 1200
> comparing with: Ellipse 600
> comparing with: Ellipse 750
> comparing with: Ellipse 1000
> comparing with: Ellipse 1500
> Found Ellipse 1500
>
> Can't find object UPS.BatterySystem.Battery.Temperature
> Can't find object UPS.PowerSummary.Voltage
> Can't find object UPS.BatterySystem.ConfigVoltage
> Can't find object UPS.PowerSummary.DelayBeforeReboot
> Can't find object UPS.BatterySystem.Battery.Test
> Can't find object UPS.BatterySystem.Battery.TestPeriod
> Can't find object UPS.PowerSummary.Temperature
> process_status_info: online
> process_status_info: !dischrg
> process_status_info: chrg
> process_status_info: !shutdownimm
> process_status_info: !lowbatt
> process_status_info: !overload
> process_status_info: !replacebatt
> Can't find object UPS.PowerConverter.Input.[1].PresentStatus.Buck
> Can't find object UPS.PowerConverter.Input.[1].PresentStatus.Boost
> process_status_info: !off
> Can't find object UPS.PowerConverter.Input.[1].Voltage
> Can't find object UPS.PowerConverter.Input.[1].Frequency
> Can't find object UPS.PowerConverter.Output.LowVoltageBoostTransfer
> Can't find object UPS.PowerConverter.Output.HighVoltageBoostTransfer
> Can't find object UPS.PowerConverter.Output.LowVoltageBuckTransfer
> Can't find object UPS.PowerConverter.Output.HighVoltageBuckTransfer
> Can't find object UPS.PowerConverter.Output.Current
> Can't find object UPS.PowerConverter.Output.Frequency
> Can't find object UPS.PowerSummary.ConfigVoltage
> Can't find object UPS.PowerSummary.ConfigVoltage
> Can't find object UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off
> Can't find object UPS.OutletSystem.Outlet.[2].RemainingCapacityLimit
> Can't find object UPS.OutletSystem.Outlet.[2].DelayBeforeShutdown
> Can't find object UPS.OutletSystem.Outlet.[2].DelayBeforeStartup
> Can't find object UPS.OutletSystem.Outlet.[3].OutletID
> Can't find object UPS.OutletSystem.Outlet.[3].OutletID
> Can't find object UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable
> Can't find object UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off
> Can't find object UPS.OutletSystem.Outlet.[3].RemainingCapacityLimit
> Can't find object UPS.OutletSystem.Outlet.[3].DelayBeforeShutdown
> Can't find object UPS.OutletSystem.Outlet.[3].DelayBeforeStartup
> Can't find object UPS.BatterySystem.Battery.Test
> Can't find object UPS.BatterySystem.Battery.Test
> Can't find object UPS.BatterySystem.Battery.Test
> upsdrv_updateinfo...
> process_status_info: online
> process_status_info: !dischrg
> process_status_info: chrg
> process_status_info: !shutdownimm
> process_status_info: !lowbatt
> process_status_info: !overload
> process_status_info: !replacebatt
> process_status_info: !off
> dstate_init: sock /var/state/ups/newhidups-auto open on fd 5
> upsdrv_updateinfo...
> Waiting for notifications...
> process_status_info: online
> process_status_info: !dischrg
> process_status_info: chrg
> process_status_info: !shutdownimm
> process_status_info: !lowbatt
> upsdrv_updateinfo...
> Waiting for notifications...
> process_status_info: online
> process_status_info: !dischrg
> process_status_info: chrg
> process_status_info: !shutdownimm
> process_status_info: !lowbatt
>
> <...>
>
> Thank in advance for your help.
> Regards,
> Patrick Agrain
>
More information about the Nut-upsdev
mailing list