Fwd: [Nut-upsdev] Fun with TrippLite
    Brandon Siegel 
    bsiegel at fastmail.fm
       
    Mon May  8 22:43:24 UTC 2006
    
    
  
-----BEGIN PGP SIGNED MESSAGE-----
Hash: SHA1
Peter:
Note: I checked out and recompiled the latest SVN before proceeding with
anything else.
I've attached the log of "newhidups -u root -DD auto" to this message.
I'm still fighting with hotplug to get it to set the permissions. I'm
down to the point where I made a hotplug script that should echo
something to a text file whenever ANY usb hotplug event happens, and
still nothing shows up despite repeatedly restarting udev and hotplug.
I'm beginning to think that the only way to figure this out is to go
down to the machine I am working on and physically plug/unplug the USB
cord (which won't be too bad since I will be heading down there to test
the beeper and so on already).
Interestingly, a quick check of "upscmd -l" shows that some commands are
"unavailable". Not sure if that's intended or what.
test.battery.start.quick - Unavailable
test.battery.start.deep - Unavailable
test.battery.stop - Stop the battery test
load.off - Turn off the load immediately
shutdown.return - Turn off the load and return when power is back
shutdown.stop - Stop a shutdown in progress
beeper.on - Enable the UPS beeper
beeper.off - Disable the UPS beeper
Anyhow, my command-throwing exploits follow. Beware, there is a bunch of
log text pasted below, but I thought it better than to attach two
different log files to this message. Once I am actually on-site, I will
try the other noisier / more dangerous tests.
- --Brandon
- -----
This is the output when I have run upsc without issuing any commands yet.
- -----
root at blah:/usr/local/ups/bin# ./upsc omnivs at localhost
battery.charge: 100
battery.type: PbAc
battery.voltage.nominal: 12.0
driver.name: newhidups
driver.parameter.port: auto
driver.version: 2.1.0
driver.version.data: TrippLite HID 0.1 (experimental)
driver.version.internal: 0.28
input.voltage.nominal: 120
output.frequency.nominal: 60
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 1000
ups.serial: 692195 A
ups.status: OL CHRG
ups.test.result: Done and passed
- -----
Here I just ran a quick test. Notice it successfully completes both the
on-battery discharge and on-line charge tests
- -----
root at blah:/usr/local/ups/bin# ./upscmd -u admin omnivs at localhost
test.battery.start.quick
root at blah:/usr/local/ups/bin# ./upsc omnivs at localhost
battery.charge: 100
battery.type: PbAc
battery.voltage.nominal: 12.0
driver.name: newhidups
driver.parameter.port: auto
driver.version: 2.1.0
driver.version.data: TrippLite HID 0.1 (experimental)
driver.version.internal: 0.28
input.voltage.nominal: 120
output.frequency.nominal: 60
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 1000
ups.serial: 692195 A
ups.status: OB DISCHRG
ups.test.result: In progress
root at blah:/usr/local/ups/bin# ./upsc omnivs at localhost
battery.charge: 100
battery.type: PbAc
battery.voltage.nominal: 12.0
driver.name: newhidups
driver.parameter.port: auto
driver.version: 2.1.0
driver.version.data: TrippLite HID 0.1 (experimental)
driver.version.internal: 0.28
input.voltage.nominal: 120
output.frequency.nominal: 60
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 1000
ups.serial: 692195 A
ups.status: OL CHRG
ups.test.result: In progress
root at blah:/usr/local/ups/bin# ./upsc omnivs at localhost
battery.charge: 100
battery.type: PbAc
battery.voltage.nominal: 12.0
driver.name: newhidups
driver.parameter.port: auto
driver.version: 2.1.0
driver.version.data: TrippLite HID 0.1 (experimental)
driver.version.internal: 0.28
input.voltage.nominal: 120
output.frequency.nominal: 60
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 1000
ups.serial: 692195 A
ups.status: OL CHRG
ups.test.result: Done and passed
- -----
Here I try to start a deep test. No such luck.
- -----
root at blah:/usr/local/ups/bin# ./upscmd -u admin omnivs at localhost
test.battery.start.deep
root at blah:/usr/local/ups/bin# ./upsc omnivs at localhost
battery.charge: 100
battery.type: PbAc
battery.voltage.nominal: 12.0
driver.name: newhidups
driver.parameter.port: auto
driver.version: 2.1.0
driver.version.data: TrippLite HID 0.1 (experimental)
driver.version.internal: 0.28
input.voltage.nominal: 120
output.frequency.nominal: 60
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 1000
ups.serial: 692195 A
ups.status: OL CHRG
ups.test.result: Done and passed
- -----
Finally, I try another quick test (which I know works and takes some
seconds to complete). Then I try to stop the test. No luck with this
command either.
- -----
root at blah:/usr/local/ups/bin# ./upscmd -u admin omnivs at localhost
test.battery.start.quick
root at blah:/usr/local/ups/bin# ./upscmd -u admin omnivs at localhost
test.battery.stop
root at blah:/usr/local/ups/bin# ./upsc omnivs at localhost
battery.charge: 100
battery.type: PbAc
battery.voltage.nominal: 12.0
driver.name: newhidups
driver.parameter.port: auto
driver.version: 2.1.0
driver.version.data: TrippLite HID 0.1 (experimental)
driver.version.internal: 0.28
input.voltage.nominal: 120
output.frequency.nominal: 60
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 1000
ups.serial: 692195 A
ups.status: OB DISCHRG
ups.test.result: In progress
Peter Selinger wrote:
> Hi Brandon,
> 
> excellent, that's great progress. Based on your output, I have cleaned
> up the variable mappings a bit; support for this UPS should now almost
> be clean. The new version is in SVN.
> 
> There are a couple of issues remaining.
> 
> 1) the -u root flag: the driver normally drops root privileges; this
>   option prevents it from doing so. However, it should not be
>   necessary if your file permissions / hotplugging is set up
>   correctly. See scripts/hotplug or scripts/hotplug-ng.
> 
> 2) the device usage tree. I would still quite like to see the output
>   of "newhidups -u root -DD auto". Could you post this?
> 
> 3) instant commands. We currently have no information on which of them,
>   if any, work, and whether they work correctly. Could you try the
>   following instant commands (use upscmd to send commands to the UPS):
> 
>   test.battery.start.quick     // start quick battery test
>   test.battery.start.deep      // start deep battery test
>   test.battery.stop            // interrupt running test
> 
>   (check how this affects ups.test.result from upsc)
> 
>   beeper.on  // turn beeper on/off
>   beeper.off
> 
>   (the beeper commands may only work during "on battery" situation)
> 
>   load.off          // turn off load
>   shutdown.return   // turn load off and back on after delay
>   shutdown.stop     // cancel turning load off
> 
>   (make sure your computer does not get its power supply via the UPS
>   when experimenting with these). 
> 
> 4) double-check output from upsc
> 
> Could you report back on items 2-4) above? Thanks, -- Peter
> 
> 
> Brandon Siegel wrote:
> Ah, quite right. Things seem to work nicely (I can run newhidups,
> upsdrvctl, and upsd) as long as I include the "-u root" flag. It's
> strange because I have to do that even when I am running them from a
> root prompt. Anyhow, the output from upsc looks good - I've pasted it
> below in case you're interested. Again, thanks for getting this working!
> 
> battery.charge: 100
> battery.type: PbAc
> battery.voltage.nominal: 12.0
> driver.name: newhidups
> driver.parameter.port: auto
> driver.version: 2.1.0
> driver.version.data: TrippLite HID 0.1 (experimental)
> driver.version.internal: 0.28
> input.voltage.nominal: 120
> output.voltage.nominal: 120.0
> UPS.BatterySystem.Battery.PresentStatus.Charging: 1
> UPS.BatterySystem.Battery.PresentStatus.Discharging: 0
> UPS.BatterySystem.Battery.PresentStatus.NeedReplacement: 0
> ups.beeper.status: enabled
> ups.delay.shutdown: 65535
> UPS.ffff0010.00ff0001.ffff007d: 8197
> UPS.ffff0015.00ff0001.ffff00c0: 255
> UPS.ffff0015.00ff0001.ffff00c1: 255
> UPS.ffff0015.00ff0001.ffff00c2: 255
> UPS.ffff0015.00ff0001.ffff00c3: 255
> UPS.ffff0015.00ff0001.ffff00c4: 154
> UPS.ffff0015.00ff0001.ffff00c5: 3
> UPS.ffff0015.00ff0001.ffff00d2: 255
> UPS.Flow.ConfigFrequency: 60
> UPS.Flow.ConfigVoltage: 120
> ups.mfr: Tripp Lite
> ups.model: TRIPP LITE UPS
> UPS.OutletSystem.Outlet.DelayBeforeShutdown: 65535
> UPS.OutletSystem.Outlet.ffff0091: 0
> UPS.OutletSystem.Outlet.ffff0092: 0
> UPS.OutletSystem.Outlet.ffff00c7: 1
> ups.power.nominal: (null)
> UPS.PowerSummary.CapacityMode: 2
> UPS.PowerSummary.FullChargeCapacity: 100
> UPS.PowerSummary.iManufacturer: Tripp Lite
> UPS.PowerSummary.iProduct: TRIPP LITE UPS
> UPS.PowerSummary.iSerialNumber: 692195 A
> ups.serial: 692195 A
> ups.status: OL CHRG
> ups.test.result: Done and passed
> 
> 
> Peter Selinger wrote:
>>>> I may be wrong, but it looks to me like what you sent is the output of
>>>> the "tripplite_usb" driver, not the "newhidups" driver. Also, the fact
>>>> that you had to override the productid suggests the same thing.
>>>>
>>>> Note that "tripplite_usb" is not the correct driver for this device.
>>>> It is a serial-over-usb driver, and only works for the Tripp Lite
>>>> 09AE/0001 devices.
>>>>
>>>> -- Peter
>>>>
>>>> Brandon Siegel wrote:
>>>> Peter:
>>>>
>>>> Thanks for taking a look at this! I gave it a go just now. Without -x
>>>> productid=2005, it still does not match:
>>>>
>>>> Checking device (09AE/2005) (001/003)
>>>> - VendorID: 09ae
>>>> - ProductID: 2005
>>>> - Manufacturer: Tripp Lite
>>>> - Product: TRIPP LITE UPS
>>>> - Serial Number: 692195 A
>>>> - Bus: 001
>>>> Trying to match device
>>>> Device does not match - skipping
>>>>
>>>> With the productid specified, however, this is the output:
>>>>
>>>> Checking device (09AE/2005) (001/003)
>>>> - VendorID: 09ae
>>>> - ProductID: 2005
>>>> - Manufacturer: Tripp Lite
>>>> - Product: TRIPP LITE UPS
>>>> - Serial Number: 692195 A
>>>> - Bus: 001
>>>> Trying to match device
>>>> Device matches
>>>> HID descriptor retrieved (Reportlen = 459)
>>>> Report descriptor retrieved (Reportlen = 459)
>>>> Found HID device
>>>> Report Descriptor size = 459
>>>> Detected a UPS: Tripp Lite /TRIPP LITE UPS
>>>> libusb_set_report() returned -32 instead of 8
>>>> Could not reset watchdog. Please send model information to nut-upsdev
>>>> mailing list
>>>> libusb_set_report() returned -32 instead of 8
>>>> Error reading protocol
>>>>
>>>> Not exactly what we were looking for, I suspect. But I hope that helps!
>>>>
>>>> --Brandon
>>>>
>>>> Peter Selinger wrote:
>>>>>>> Hi Brandon,
>>>>>>>
>>>>>>> thanks for this piece of detective work. So yes, I think I can confirm
>>>>>>> that the 09AE/2005 is indeed a HID device, and it should now be
>>>>>>> recognized by newhidups (although the support for it is still a bit
>>>>>>> rudimentary). I just committed a few changes as suggested by you and
>>>>>>> Charles. It would be great if you could get the newest development
>>>>>>> sources from SVN and try to run newhidups on this device. It might be
>>>>>>> useful to see the output of "newhidups -u root -DD auto" (not -DDDDD,
>>>>>>> please!).
>>>>>>>
>>>>>>> More importantly, if the driver is running, I would like to see the
>>>>>>> output of "upsc ups at localhost". This will be crucial to confirm that
>>>>>>> the variables have been mapped correctly, and to figure out the
>>>>>>> meanings of some of the unmapped variables are. It would also be good
>>>>>>> to observe how the output of "upsc ups at localhost" changes through
>>>>>>> various state changes (on battery, low battery, charging, discharging,
>>>>>>> self-test, etc). Of course, the ups.status variable is especially
>>>>>>> important here. 
>>>>>>>
>>>>>>> Could you try this and report back? Thanks, -- Peter
>>>>>>>
>>>>>>> Brandon Siegel wrote:
>>>>>>>> Peter:
>>>>>>>>
>>>>>>>> I posted on this list in March trying to get the Tripplite Omni1000 I
>>>>>>>> have working with NUT. I posted a bunch of debug output for the
>>>>>>>> developers, which I'll paste below, in case it's of use to you. If there
>>>>>>>> is any other output you need, please don't hesitate to ask :)
>>>>>>>>
>>>>>>>> - --Brandon Siegel
>>>>>>>>
>>>>>>>> The device IDs are:
>>>>>>>>
>>>>>>>> Checking device (09AE/2005) (001/002)
>>>>>>>> - - VendorID: 09ae
>>>>>>>> - - ProductID: 2005
>>>>>>>> - - Manufacturer: unknown
>>>>>>>> - - Product: unknown
>>>>>>>> - - Serial Number: unknown
>>>>>>>> - - Bus: 001
>>>>>>>>
>>>>>>>> When I manually listened for events, these are what I saw when I
>>>>>>>> plugged/unplugged the power. The comments below each one are Charles'
>>>>>>>> interpretation (seems Tripplite messed up the usage page for this model).
>>>>>>>>
>>>>>>>>> 8400d0: 0 when on battery, 1 when on wall power
>>>>>>>> potentially 0x8500d0 instead (battery page, ACPresent)
>>>>>>>>
>>>>>>>>> 84004b: 0 when on wall power and battery (sorry, not much help on
>>>>>>>>> this one)
>>>>>>>> could be 0x85004b (battery page, NeedReplacement)
>>>>>>>>
>>>>>>>>> 840045: 1 when on battery and also 1 immediately after wall power is 
>>>>>>>>> restored, but changes to 0 after about 5-10 seconds
>>>>>>>> looks like 0x850045 (battery page, Discharging)
>>>>>>>>
>>>>>>>>> 840044: 0 when on battery and also 0 immediately after wall power is 
>>>>>>>>> restored, but changes to 1 after about 5-10 seconds
>>>>>>>> looks like 0x850044 (battery page, Charging)
>>>>>>>>
>>>>>>>> So it looks like someone confused pages 0x84 and 0x85.
>>>>>>>>
>>>>>>>> Where are these events coming from, by the way? Did you test with hidups?
>>>>>>>>
>>>>>>>>> I noticed that immediately after wall power was restored, the LCD 
>>>>>>>>> displayed voltage level of 122 volts. I suspect it is possible that
>>>>>>>>> the changing of those last two after a few seconds may involve
>>>>>>>>> automatic voltage regulation, or perhaps when the battery is
>>>>>>>>> charging.
>>>>>>>> Sounds like the latter.
>>>>>>>>
>>>>>>>>
>>>>>>>> Peter Selinger wrote:
>>>>>>>>> Hi Charles and Jonathan,
>>>>>>>>>
>>>>>>>>> I am going through my over 300 unread NUT messages, and I just 
>>>>>>>>> discovered this one from mid-December. At the time, I was trying to 
>>>>>>>>> clean up the tripplite subdriver of newhidups, but never got the 
>>>>>>>>> information I needed. I have enabled this driver now, but it is
>>>>>>>>> marked "experimental". The driver is still incomplete, in the sense
>>>>>>>>> that there are many unmapped device variables. "upsc" should show
>>>>>>>>> variables such as these:
>>>>>>>>>
>>>>>>>>> UPS.ffff0010.00ff0001.ffff007d 
>>>>>>>>> UPS.PowerSummary.PresentStatus.0084004b UPS.Flow.ConfigVoltage
>>>>>>>>>
>>>>>>>>> Cleaning this up requires the help of someone who actually has such a
>>>>>>>>>  device.
>>>>>>>>>
>>>>>>>>> Jonathan, if you run this driver, could you use "upsc" to print out 
>>>>>>>>> the states of the various variables? Also observe how they change
>>>>>>>>> over time as you plug/unplug the power, initiate battery tests, etc. 
>>>>>>>>> Perhaps you can figure out the meaning of some of the variables 
>>>>>>>>> starting with "UPS.*", which are the ones I haven't yet mapped. For 
>>>>>>>>> example, one of them might be the system load that you were looking 
>>>>>>>>> for.
>>>>>>>>>
>>>>>>>>> Some of the instant commands have been implemented, and may/may not
>>>>>>>>> be working. You could test the behavior of
>>>>>>>>>
>>>>>>>>> test.battery.start.quick test.battery.start.deep test.battery.stop 
>>>>>>>>> load.off shutdown.return shutdown.stop beeper.on beeper.off
>>>>>>>>>
>>>>>>>>> and let me know if they do anything sensible. Note: only run these 
>>>>>>>>> tests if nothing important is plugged into the UPS, as it might cut 
>>>>>>>>> power. Also, beeper.on and beeper.off might not do anything unless 
>>>>>>>>> there is an "alarm condition" (such as low battery).
>>>>>>>>>
>>>>>>>>> The most important variable to look out for is ups.status, as this is
>>>>>>>>>  what upsmon uses to figure out if/when to shutdown the system. You
>>>>>>>>> may test that it shows OL (which the UPS is on line), OB (when it is
>>>>>>>>> on battery), or LB (when the battery is low).
>>>>>>>>>
>>>>>>>>> Also, Jonathan, the segmentation fault bug that you encountered in 
>>>>>>>>> December should hopefully have been fixed by now. So you might want
>>>>>>>>> to give this another try if you have not been using it the last few 
>>>>>>>>> months.
>>>>>>>>>
>>>>>>>>> Your help will be appreciated in rounding off this driver to a 
>>>>>>>>> distributable state! Thanks, -- Peter
>>>>>>>>>
>>>>>>>>>
>>>>>>>>> Charles Lepple wrote:
>>>>>>>>>> Peter,
>>>>>>>>>>
>>>>>>>>>> any objections to enabling the Tripp-Lite HID subdriver?
>>>>>>>>>>
>>>>>>>>>> ---------- Forwarded message ---------- From: Jonathan Freedman
>>>>>>>>>> <jef at pleiades.ca> Date: Dec 15, 2005 1:20 AM Subject: Re:
>>>>>>>>>> [Nut-upsdev] Fun with TrippLite To: Charles Lepple
>>>>>>>>>> <clepple at gmail.com>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> Hey
>>>>>>>>>>
>>>>>>>>>> So yeah. Instead of sleeping I decided to get this working. As you 
>>>>>>>>>> mentioned, there appears to be a subdriver for the tripplite in
>>>>>>>>>> existence. However it was not enabled. That part was easy... I
>>>>>>>>>> simply added a " &tripplite_subdriver" on line 42 and a "#include
>>>>>>>>>> "tripplite-hid.h" on line 34 with the rest of the includes.
>>>>>>>>>>
>>>>>>>>>> It works; and the nagios plugin works; and I am happy. The only
>>>>>>>>>> catch is it doesn't seem to give the current load; but it didn't do
>>>>>>>>>> that under windows either so I can live with it.
>>>>>>>>>>
>>>>>>>>>> Cheers
>>>>>>>>>>
>>>>>>>>>> Jonathan Freedman Vice President Pleiades Consulting (902) 444-4335
>>>>>>>>>> x400
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> -- - Charles Lepple
> _______________________________________________
> Nut-upsdev mailing list
> Nut-upsdev at lists.alioth.debian.org
> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
>>
_______________________________________________
Nut-upsdev mailing list
Nut-upsdev at lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
>>
-----BEGIN PGP SIGNATURE-----
Version: GnuPG v1.2.5 (MingW32)
Comment: Using GnuPG with Mozilla - http://enigmail.mozdev.org
iD8DBQFEX8mKVtFSfAZ1XPERAlBcAJ0Sg+QQPiSe4FnVAWUV069u3m+HPACgomEO
kMTwe9N/xiA1QQFck5TyBRA=
=x1oG
-----END PGP SIGNATURE-----
-------------- next part --------------
debug level is '2'
Checking device (0000/0000) (002/001)
- VendorID: 0000
- ProductID: 0000
- Manufacturer: Linux 2.6.12-10-amd64-k8-smp ehci_hcd
- Product: nVidia Corporation CK804 USB Controller
- Serial Number: 0000:00:02.1
- Bus: 002
Trying to match device
Device does not match - skipping
Checking device (09AE/2005) (001/003)
- VendorID: 09ae
- ProductID: 2005
- Manufacturer: Tripp Lite 
- Product: TRIPP LITE UPS 
- Serial Number: 692195 A 
- Bus: 001
Trying to match device
Device matches
HID descriptor retrieved (Reportlen = 459)
Report descriptor retrieved (Reportlen = 459)
Found HID device
Report Descriptor size = 459
Detected a UPS: Tripp Lite /TRIPP LITE UPS 
Using subdriver: TrippLite HID 0.1 (experimental)
Path: UPS.PowerSummary.iProduct, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.iSerialNumber, Type: Feature, Value: 2.000000
Path: UPS.PowerSummary.iManufacturer, Type: Feature, Value: 3.000000
Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, Value: 120.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, Value: 2.000000
Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, Value: 24.000000
Path: UPS.PowerSummary.CapacityMode, Type: Feature, Value: 2.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Input, Value: 100.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, Value: 100.000000
Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, Value: 100.000000
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, Value: 0.000000
Can't find object UPS.PowerSummary.PresentStatus.TLACPresent
Path: UPS.PowerSummary.PresentStatus.TLACPresent, Type: Input
Can't find object UPS.PowerSummary.PresentStatus.TLCharging
Path: UPS.PowerSummary.PresentStatus.TLCharging, Type: Input
Can't find object UPS.PowerSummary.PresentStatus.TLDischarging
Path: UPS.PowerSummary.PresentStatus.TLDischarging, Type: Input
Can't find object UPS.PowerSummary.PresentStatus.TLNeedReplacement
Path: UPS.PowerSummary.PresentStatus.TLNeedReplacement, Type: Input
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, Value: 0.000000
Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, Value: 12.000000
Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, Value: 1.000000
Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, Value: 0.000000
Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature, Value: 0.000000
Path: UPS.BatterySystem.Test, Type: Feature, Value: 1.000000
Path: UPS.Flow.ConfigVoltage, Type: Feature, Value: 120.000000
Path: UPS.Flow.ConfigFrequency, Type: Feature, Value: 60.000000
Path: UPS.Flow.ConfigApparentPower, Type: Feature, Value: 1000.000000
Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, Value: 65535.000000
Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature, Value: 0.000000
Path: UPS.OutletSystem.Outlet.ffff0092, Type: Feature, Value: 0.000000
Path: UPS.OutletSystem.Outlet.ffff00c7, Type: Feature, Value: 1.000000
Path: UPS.ffff0010.00ff0001.ffff007d, Type: Feature, Value: 8197.000000
Path: UPS.ffff0015.00ff0001.ffff00c0, Type: Feature, Value: 255.000000
Path: UPS.ffff0015.00ff0001.ffff00d2, Type: Feature, Value: 255.000000
Path: UPS.ffff0015.00ff0001.ffff00c1, Type: Feature, Value: 255.000000
Path: UPS.ffff0015.00ff0001.ffff00c2, Type: Feature, Value: 255.000000
Path: UPS.ffff0015.00ff0001.ffff00c3, Type: Feature, Value: 255.000000
Path: UPS.ffff0015.00ff0001.ffff00c5, Type: Feature, Value: 3.000000
Can't retrieve Report 154 (-32/32): Broken pipe
Path: UPS.ffff0015.00ff0001.ffff00c4, Type: Feature
entering identify_ups(0x09ae, 0x2005)
Can't find object UPS.PowerSummary.RemainingCapacityLimit
Can't find object UPS.BatterySystem.Battery.Voltage
-> String: PbAc (len = 4/8)
Can't find object UPS.OutletSystem.Outlet.DelayBeforeReboot
process_status_info: online
process_status_info: !dischrg
process_status_info: chrg
process_status_info: !shutdownimm
Can't find object UPS.PowerConverter.PresentStatus.Overload
process_status_info: !replacebatt
Can't find object UPS.PowerConverter.PresentStatus.Boost
Can't find object UPS.PowerConverter.PresentStatus.Buck
Can't find object UPS.PowerSummary.PresentStatus.TLACPresent
Can't find object UPS.PowerSummary.PresentStatus.TLDischarging
Can't find object UPS.PowerSummary.PresentStatus.TLCharging
Can't find object UPS.PowerSummary.PresentStatus.TLNeedReplacement
Can't find object UPS.PowerConverter.PresentStatus.OverTemperature
Can't find object UPS.PowerConverter.PresentStatus.AwaitingPower
Can't find object UPS.PowerConverter.PresentStatus.InternalFailure
Can't find object UPS.PowerConverter.PresentStatus.VoltageOutOfRange
Can't find object UPS.PowerConverter.Input.Voltage
Can't find object UPS.PowerConverter.Input.Frequency
Can't find object UPS.PowerSummary.Voltage
upsdrv_updateinfo...
-> String: PbAc (len = 4/8)
process_status_info: online
process_status_info: !dischrg
process_status_info: chrg
process_status_info: !shutdownimm
process_status_info: !replacebatt
dstate_init: sock /var/state/ups/newhidups-auto open on fd 5
upsdrv_updateinfo...
Waiting for notifications...
=>Got 5 HID Objects...
ups.status = !replacebatt
process_status_info: !replacebatt
ups.status = !dischrg
process_status_info: !dischrg
ups.status = chrg
process_status_info: chrg
ups.status = online
process_status_info: online
ups.status = !shutdownimm
process_status_info: !shutdownimm
upsdrv_updateinfo...
Waiting for notifications...
=>Got 1 HID Objects...
battery.charge = 100
upsdrv_updateinfo...
Waiting for notifications...
=>Got 5 HID Objects...
ups.status = !replacebatt
process_status_info: !replacebatt
ups.status = !dischrg
process_status_info: !dischrg
ups.status = chrg
process_status_info: chrg
ups.status = online
process_status_info: online
ups.status = !shutdownimm
process_status_info: !shutdownimm
upsdrv_updateinfo...
Waiting for notifications...
=>Got 1 HID Objects...
battery.charge = 100
upsdrv_updateinfo...
Waiting for notifications...
=>Got 5 HID Objects...
ups.status = !replacebatt
process_status_info: !replacebatt
ups.status = !dischrg
process_status_info: !dischrg
ups.status = chrg
process_status_info: chrg
ups.status = online
process_status_info: online
ups.status = !shutdownimm
process_status_info: !shutdownimm
upsdrv_updateinfo...
Waiting for notifications...
=>Got 1 HID Objects...
battery.charge = 100
upsdrv_updateinfo...
Waiting for notifications...
    
    
More information about the Nut-upsdev
mailing list