[Nut-upsdev] Tripp-Lite OMNI650LCD

Mike Greaves mike.greaves at itlcircuits.com
Tue Sep 26 20:01:59 UTC 2006


On 15:22 2006-09-26 selinger at mathstat.dal.ca (Peter Selinger) wrote:
> You can run "upsmon -c fsd" to force a shutdown of your computer.
> (Assuming the driver, upsd, and upsmon are all configured, running,
> and monitoring the system correctly). This will only allow you to test
> whether the system shuts down correctly and the UPS shuts off at the
> correct moment. It will not reveal whether NUT would actually detect a
> low battery correctly.
>
> P.S. the "battery.voltage: 0.0" is a harmless bug that I have been
> planning to fix for a while. Upsmon actually only looks at ups.status,
> so this misreported value is purely cosmetic. -- Peter

Everything seems to work fine, thanks.

Mike

--
---------------------------------------------------------------
Mike Greaves
ITL Circuits
(905) 475-6658 ext. 119
---------------------------------------------------------------




More information about the Nut-upsdev mailing list