[Nut-upsdev] Driver for Cyberpower PR2200

Russ Romano russ at cb-1.com
Sat Apr 28 03:31:18 UTC 2007


> What we need you to do, is play around with the settings a 
> little, while recording what is sent to the UPS. Change a 
> value, wait a couple of seconds and go to the next one for 
> that parameter. Start with the default value and sequentially 
> move through the list twice. The latter is important, since 
> we also want to know how to go back to the default value once 
> that has changed.
> 
> From the list you sent earlier, I estimate that you will be 
> able to set the following values in the UPS (the others 
> appear to be done by the software on the host):
> 
> buzzer : [on],off
> cold start : on,[off]
> high input voltage : [138],139,140,141,142,143,144,145,146,147
> low input voltage : 88,89,90,91,92,93,94,95,96,[97]
> battery critical capacity : [25],30,35,40,45,50,55,60
> battery mode output voltage configuration : 110,[120],130
> 
> Make a separate sheet for each of the commands, so that we 
> don't mix them up.
> 

As requested, the spreadsheet has been updated with new sheets for each
of the above parameters.

http://www.lvahs.com/pr2200.xls

Thanks!
-Russ