[Nut-upsdev] [Nut-upsuser] Powerware 9155 with SNMP card
Bernd Markgraf
Bernd.Markgraf at med.ovgu.de
Fri Aug 10 12:28:50 UTC 2007
Hi again,
further on with my investigations snmpwalk came handy (should have
thought of that earlier!)
[snip]
mib-2.33.1.3.2.0 = INTEGER: 3 // should be my number input phases
mib-2.33.1.3.3.1.2.1 = INTEGER: 500 //input freq 1 10ths of Hz
mib-2.33.1.3.3.1.2.2 = INTEGER: 500 //input freq 2
mib-2.33.1.3.3.1.2.3 = INTEGER: 500 //input freq 3
mib-2.33.1.3.3.1.3.1 = INTEGER: 234 //input volt 1
mib-2.33.1.3.3.1.3.2 = INTEGER: 234 //input volt 2
mib-2.33.1.3.3.1.3.3 = INTEGER: 235 //input volt 3
mib-2.33.1.3.3.1.4.1 = INTEGER: 20 //input amps 1
mib-2.33.1.3.3.1.4.2 = INTEGER: 20 //input amps 2
mib-2.33.1.3.3.1.4.3 = INTEGER: 20 //input amps 3
mib-2.33.1.4.1.0 = INTEGER: 3 //power status OL
mib-2.33.1.4.2.0 = INTEGER: 500 //output freq in 0.1Hz
mib-2.33.1.4.3.0 = INTEGER: 1 //number output phases
mib-2.33.1.4.4.1.1.1 = INTEGER: 1
mib-2.33.1.4.4.1.2.1 = INTEGER: 229 //output voltage
mib-2.33.1.4.4.1.3.1 = INTEGER: 70 //output amps
mib-2.33.1.4.4.1.4.1 = INTEGER: 1413 //output watts
mib-2.33.1.4.4.1.5.1 = INTEGER: 13 //output load %
[snip]
This leads me to a few conclusions regarding pwmib.h
{ "output.voltage", 0, 1.0, PW_OID_OUT_VOLTAGE ".0", "",
SU_OUTPUT_1, NULL },
{ "output.current", 0, 0.1, PW_OID_OUT_CURRENT ".0", "",
SU_OUTPUT_1, NULL },
{ "output.realpower", 0, 0.1, PW_OID_OUT_POWER ".1", "",
SU_OUTPUT_1, NULL },
should rather be
{ "output.voltage", 0, 1.0, PW_OID_OUT_VOLTAGE ".1", "",
SU_OUTPUT_1, NULL },
{ "output.current", 0, 1.0, PW_OID_OUT_CURRENT ".1", "",
SU_OUTPUT_1, NULL },
{ "output.realpower", 0, 1.0, PW_OID_OUT_POWER ".1", "",
SU_OUTPUT_1, NULL },
to report a load of 1413W instead of 143.1 and to report a current of 7A
instead of 0.7A (Though the MIB says currents are reported in Amps I
don't think I'm running 70A on the output ;-)) My question about whether
one should append .0 or .1 for the OIDs of a single output also answer
itself now.
while looking further i guess the same is true for
{ "input.current", 0, 0.1, PW_OID_IN_CURRENT ".0", "",
SU_INPUT_1, NULL },
and all other appearances of realpower. Though I don't know if this is
also valid for other UPS models. Maybe Niels' work can enlighten things
here?
Bernd
More information about the Nut-upsdev
mailing list