[Nut-upsdev] Re: [PATCH] upsstatus += HB, TEST
Peter Selinger
selinger at mathstat.dal.ca
Wed Jan 17 02:02:27 CET 2007
Arjen de Korte wrote:
>
> Kirill Smelkov wrote:
>
> > Here I propose 2 new status flags for inclusion into NUT:
> >
> > HB - HighBattery
>
> What is this? Is this a notification that the battery is full, or that
> the battery voltage is too high? At the very least, this should be a
> little more descriptive. Yet I'm not quite sure if this is not similar
> to RB (Replace Battery).
Perhaps this is just the negation of LB - Low Battery? In this case it
is not needed as a separate flag.
> > TEST - Battery test is running
>
> We already have CAL, which is essentially the same thing. Unless this is
> totally different, I don't support adding this to the ups.status. For
> the operation of upsmon, a battery test and runtime calibration are the
> same thing - you'd risk a shorter than normal runtime when the mains is
> out (if the battery is not fully charged).
Perhaps this belongs in ups.test.result? Several drivers put "in
progress" here while a test is in progress.
> For now, I don't support either of these two flags.
Neither I. -- Peter
More information about the Nut-upsdev