> Hi Arjen,
>
> Thanks for your note.  I'll watch for Arnaud Quette's comments.
>
> For my last cluster (U. Wisconsin - Milwaukee) we have one NUT server that
> happily controls more than 800 Linux boxes.  No obvious scaling problems
> there.
Good. Then the only problem could be the FD_SETSIZE limit, which is
limited to 1024 on some systems (or even lower than that). You could try
to redefine it to a higher value though.
> (And yes, we have tested that all the boxes shut down as they
> should.  We have also had a couple of clean shutdowns in the past year
> when power failed or was turned off without warning on campus.)
Nice to hear!
> If we do run into scaling problems, am I correct that we could have more
> than one NUT server (say one for each 500 boxes)?
You could, but that would require setting up dummy UPSes too. I don't
recommend that. Checkout the value of FD_SETSIZE on your system. If it is
larger than the number of clients you want to connect to your server, you
probably have nothing to worry about.
Best regards, Arjen
    
    