[Nut-upsdev] Tripp Lite USB UPS

Peter Selinger selinger at mathstat.dal.ca
Thu Mar 1 04:45:15 CET 2007


Patrick,

You are not out of luck. Although the device reports inconsistent
data, the problem is most likely in the firmware and not in the
hardware. Whatever it is, we can compensate for it in the driver.

I apologize, but I am too busy this week (and next) to be looking into
this. Please remind me again after March 15 or so!

-- Peter

Patrick Krepps wrote:
> 
> HI Peter,
> 
> I had sent this reply the other day, and hadn't heard anything back. I am 
> assuming that means we are out of luck on this device? 
> 
> On Monday 26 February 2007 20:54, you wrote:
> > Hi Peter,
> >
> > Glad I was able to provide something that helped. If I understand what you
> > are saying, the UPS is reporting that it needs replacing? Or the battery?
> > Either way that is upsetting as this UPS is just over 5 weeks old. Anything
> > else I can do to help determine the source of the problem?
> >
> > Thanks for the update and info,
> > Patrick
> >
> > PS I've trimmed my long original message to keep things from getting too
> > large.
> >
> > On Monday 26 February 2007 00:23, you wrote:
> > > Hi Patrick,
> > >
> > > the debug output you sent is useful. I think it shows that the bug is
> > > likely in the device, not the driver. I parsed the report descriptor
> > > (1028 bytes), and it defines, among other things, a report number 50
> > > (0x32) ("Feature" or "Input") with the following format:
> > >
> > > byte 0, bit 0-6: unused
> > > byte 0, bit 7:   UPS.PowerSummary.PresentStatus.InternalFailure
> > > byte 1, bit 0:   unused
> > > byte 1, bit 1:   UPS.PowerSummary.PresentStatus.ShutdownImminent
> > > byte 1, bit 2-7: unused
> > > byte 2, bit 0:   UPS.PowerSummary.PresentStatus.ACPresent
> > > byte 2, bit 1:   unused
> > > byte 2, bit 2-3: UPS.PowerSummary.PresentStatus.00850046
> > > byte 2, bit 4-7: UPS.PowerSummary.PresentStatus.NeedReplacement
> > >
> > > Bits are counted from least to most significant, i.e.: 76543210.
> > >
> > > Now during the initial data collection run, we see report 50 as
> > >
> > > follows:
> > > > Report[r]: (4 bytes) => 32 00 00 11
> > >
> > > Here the first byte is the report number (0x32 = 50). The remaining
> > > bytes are the payload data. By the above scheme, this translates to:
> > > UPS.PowerSummary.PresentStatus.InternalFailure = 0
> > > UPS.PowerSummary.PresentStatus.ShutdownImminent = 0
> > > UPS.PowerSummary.PresentStatus.ACPresent = 1
> > > UPS.PowerSummary.PresentStatus.NeedReplacement = 1 (why?)
> 