[Nut-upsdev] tripp lite smart2200RMXL2U error reading protocol
Peter Selinger
selinger at mathstat.dal.ca
Mon May 14 17:29:51 UTC 2007
This looks good.
If you get revision 901 ("svn update"), then you no longer need the -x
productid option.
-- Peter
Lance Thomas wrote:
>
> I tried the new usbhid-ups from the rev 900 of the svn and after
> creating a few links to make it work in the gentoo framework I am
> connected and receiving data from the tripp lite ups. I will be
> checking to make sure the data is correct, but here is what I received
> from upsc tripplite at localhost
>
> battery.charge: 100
> battery.charge.low: 10
> battery.charge.warning: 30
> battery.temperature: 33
> battery.type: PbAC
> battery.voltage: 5.4
> battery.voltage.nominal: 48.0
> driver.name: usbhid-ups
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 3012
> driver.version: 2.1.0
> driver.version.data: TrippLite HID 0.1 (experimental)
> driver.version.internal: 0.30
> input.frequency: 59.9
> input.transfer.high: 145.0
> input.transfer.low: 83.0
> input.voltage: 125.1
> input.voltage.nominal: 120
> output.frequency: 59.9
> output.frequency.nominal: 60
> output.voltage: 124.5
> output.voltage.nominal: 120
> ups.beeper.status: enabled
> ups.delay.reboot: -1
> ups.delay.restart: -1
> ups.delay.shutdown: -1
> ups.load: 43
> ups.mfr: Tripp Lite
> ups.model: TRIPP LITE SMART2200RMXL2U
> ups.power.nominal: 2200
> ups.productid: 3012
> ups.serial: 9550ALCSM538900110
> ups.status: OL
> ups.test.result: 0
> ups.vendorid: 09ae
>
> Thanks for all the help.
>
> >>> Peter Selinger 05/14/07 11:16 AM >>>
> OK, that is very similar to the other Tripplite-HID devices; the
> functionality of this device seems to be almost a superset of the
> OMNI1000LCD and of the SmartOnlineSU1500RTXL2ua.
>
> It should work without problems with the newhidups driver, if you just
> add the 0x3012 to the source code where Charles suggested.
>
> I have just done this in the latest SVN version (revision 901).
> Note that in SVN, the driver has been renamed to usbhid-ups from
> newhidups.
>
> -- Peter
>
>
> ____________________________________________________________________
>
> This email and any attachments may contain confidential information and is
> solely for the intended recipient(s). Email communications are not considered
> secure. If you are not the intended recipient(s) of this email you are expected
> to disregard the content, delete the message and notify the original sender.
>
> --University of Wisconsin, Department of Family Medicine--
> ____________________________________________________________________
>
> **UW DFM**
>
More information about the Nut-upsdev
mailing list