Arjen,

	I did it. With the battery half-way out, still connected, and with the
multi-meter leads securely in the connectors, I got the right data this time.
As before, when you get time for a patch, I'm more than happy to test. The data is:

"Network UPS Tools upslog 2.2.2"				
"logging status of ecstasy_ups to - (10s intervals)"

                       Volts    Volts
Time       Charge(%) indicated (actual) "Comments"

10:59:49 AM	100	20.2	13.7	
10:59:59 AM	100	20.2	13.7	
11:00:09 AM	100	20.2	13.7	"Power Loss"
11:00:19 AM	79	16.3	11.75	
11:00:29 AM	81	16.3		
11:00:39 AM	82	16.3	11.7	
11:00:49 AM	81	17.1	11.68	
11:00:59 AM	81	17.1	11.67	
11:01:09 AM	79	17.1	11.65	
11:01:19 AM	79	17.1	11.63	
11:01:29 AM	78	17.1	11.61	
11:01:39 AM	78	17.1	11.6	
11:01:49 AM	78	17	11.58	
11:01:59 AM	75	17	11.57	
11:02:09 AM	74	17	11.54	
11:02:19 AM	70	17	11.52	
11:02:29 AM	70	16.9	11.48	
11:02:39 AM	70	16.9		
11:02:49 AM	74	16.9	11.52	
11:02:59 AM	62	16.9	11.47	
11:03:09 AM	62	16.9	11.41	
11:03:19 AM	62	16.9	11.37	
11:03:29 AM	59	16.6	11.33	
11:03:39 AM	59	16.6	11.33	
11:03:49 AM	56	16.6	11.28	
11:03:59 AM	52	16.5	11.65	"Monitor off"
11:04:09 AM	58	16.5	11.71	
11:04:19 AM	58	16.5		
11:04:29 AM	57	17.1		
11:04:39 AM	47	17.1	11.34	"Monitor on"
11:04:49 AM	46	17.1	11.28	
11:04:59 AM	46	16.3	11.22	
11:05:09 AM	41	16.3	11.16	
11:05:19 AM	35	16.3	11.07	
11:05:29 AM	35	16.3	11	
11:05:39 AM	30	16.2	10.96	
11:05:49 AM	25	16.2	10.92	
11:05:59 AM	21	16.2	10.87	
11:06:09 AM	21	15.9	10.8	
11:06:19 AM	17	15.9	10.73	
11:06:29 AM	13	15.9		
11:06:39 AM	23	16.3	11.18	"Monitor off"
11:06:49 AM	23	16.3	11.16	
11:06:59 AM	23	16.3	11.15	
11:07:09 AM	23	16.3		
11:07:19 AM	22	16.3	10.57	
11:07:29 AM	9	16.3	10.51	"Monitor on"
11:07:39 AM	6	15.4	10.5	

	The .csv file is:

http://www.3111skyline.com/download/ups/CyberPower/voltages_measured-discharge.csv

	The openOffice calc file is:

http://www.3111skyline.com/download/ups/CyberPower/voltages_measured-discharge.ods