Citeren Tom Cassimon <tom at cassimon.mine.nu>:
[...]
> Checking device (0925/1234) (007/002)
> - VendorID: 0925
> - ProductID: 1234
> - Manufacturer: ?
> - Product: UPS USB MON V1.4
> - Serial Number: unknown
> - Bus: 007
> Trying to match device
> Device matches
OK, at least the device matching seems to work.
> send: (4 bytes) => 01 00 00 30
> read: Resource temporarily unavailable
> do_command: Resource temporarily unavailable
And from here, that's it. No response at all. Maybe this is because
the driver expects the query to be sent as a HID_REPORT_TYPE_INPUT
instead of the HID_REPORT_TYPE_FEATURE that usb->set_report uses.
Could you try again with the latest version (r1604) from the trunk? If
that fails, we also have 'lakeview_usb', which might be worth trying
out.
[...]
> I use the -u root option because the udev system doesn't seem to change the
> permissions of the device.
I know, this udev rules will be generated automatically in the future
(and the driver is already setup to support that), but this isn't
activate yet. For now I have modified this too.
Best regards, Arjen
--