[Nut-upsdev] Tripplite Smart1500SLT configuration?

Arjen de Korte nut+devel at de-korte.org
Fri Jul 25 07:27:16 UTC 2008


> root at golum:# /usr/local/ups/bin/upsc tripplite at localhost
> battery.charge: 100
> battery.charge.low: 10
> battery.charge.warning: 30
> battery.temperature: 24.9
> battery.type: PbAC
> battery.voltage: 40.7
> battery.voltage.nominal: 36.0
> driver.name: usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.vendorid: 09ae
> driver.version: 2.3.0-1515
> driver.version.data: TrippLite HID 0.2 (experimental)
> driver.version.internal: 0.33
> input.frequency: 59.9
> input.transfer.high: 145.0
> input.transfer.low: 95.0
> input.voltage: 120.3
> input.voltage.nominal: 120
> output.frequency: 59.9
> output.frequency.nominal: 60
> output.voltage: 120.3
> output.voltage.nominal: 120
> ups.beeper.status: enabled
> ups.delay.shutdown: 20
> ups.delay.start: 30
> ups.load: 12
> ups.mfr: Tripp Lite
> ups.model: TRIPP LITE SMART1500SLT
> ups.power.nominal: 1500
> ups.productid: 3012
> ups.serial: 9605ALCSM538800161
> ups.status: OL
> ups.timer.reboot: -1
> ups.timer.shutdown: -1
> ups.timer.start: -1
> ups.vendorid: 09ae
> ups.watchdog.status: 0
>
> Hallelujah! At least, I think I can say that. All the ones that I can
> make sense of, look good to me.

This is all looking good. Before relying on the driver for unattended
shutdowns, you may wish to test this first. Running 'upsmon -c fsd' and if
that's successful, pulling the mains plug from the UPS and repeating this,
is essential.

> Does the rest of it make sense? If so, I believe you can add this device
> to your supported devices list. If not, I'll be glad to help figure out
> what it takes to make it so.

I will add it to the list. It should be supported by the 'usbhid-ups'
driver out of the box. Thanks for the success report.

Best regards, Arjen
-- 
Eindhoven - The Netherlands
Key fingerprint - 66 4E 03 2C 9D B5 CB 9B  7A FE 7E C1 EE 88 BC 57




More information about the Nut-upsdev mailing list