[Nut-upsdev] HP T/R2200 G2
    Arjen de Korte 
    nut+devel at de-korte.org
       
    Fri Sep 12 06:16:20 UTC 2008
    
    
  
Citeren "James Harper" <james.harper at bendigoit.com.au>:
> I got a chance to quickly test this. upsc output is:
[...]
> input.voltage: 248.1
> input.voltage.nominal: 230
[...]
> output.voltage: 218.0
> output.voltage.nominal: 230
[...]
> ups.status: OL TRIM
> all the numbers seem reasonable. In Australia we run at 240 volts, but
> all the HP UPS's I have seen are configured by default for 230 volts,
> and I must have not set this one to 240V, which will explain why it's on
> 'TRIM'. 248 volts is a bit on the high side but still within acceptable
> limits.
You could probably change this through 'upsrw', if the subdriver would  
allow it (which it currently doesn't). I'll volunteer to do this, if  
you can send me the first 30 seconds worth of output when running the  
driver with '-DD' (debug level two, *not* higher).
Best regards, Arjen
    
    
More information about the Nut-upsdev
mailing list