[Nut-upsdev] SNMP on HP UPS

Arjen de Korte nut+devel at de-korte.org
Mon Aug 31 18:55:23 UTC 2009


Citeren Philip Ward <p.g.ward op stir.ac.uk>

> However, it is not just unsupported OIDs that are a problem, but also
> different OIDs.
>
> output voltage is "1.3.6.1.2.1.33.1.4.4.1.2.1" on the af401a but ietf
> has it at "1.3.6.1.2.1.33.1.4.4.1.2.0"
> output current is "1.3.6.1.2.1.33.1.4.4.1.3.1" on the af401a but ietf
> has it at "1.3.6.1.2.1.33.1.4.4.1.3.0"
>
> Similarly for input.frequency, input.voltage and input.current. I'm not
> sure that there is a way around these differences without either a new
> mib, or changing the way that the driver scans the OID tree to try and
> resolve them.

Have you already checked if there are firmware updates available for  
your SNMP card? These differences may not be intentional and chances  
are that there are updates available that make it conform to the IETF  
standard.

Best regards, Arjen
-- 
Please keep list traffic on the list




More information about the Nut-upsdev mailing list