[Nut-upsdev] CyberPower PR3000E works with powerpanel driver
Arjen de Korte
nut+devel at de-korte.org
Sat Jul 11 09:32:01 UTC 2009
Citeren Laurent Léonard <laurent op open-minds.org>:
> debian:~# upsc ups
> battery.charge: 100
> battery.charge.low: 45
> driver.name: powerpanel
> driver.parameter.pollinterval: 2
> driver.parameter.port: /dev/ttyS0
> driver.version: 2.2.2
> driver.version.internal: 0.23
> input.frequency: 20.0
Working back from the driver, the UPS is reporting '50'. The
conversion the driver does (dividing by 2.5 is apparently wrong). I
was unsure about the logic behind this. A PR2200 running 120 V / 60 Hz
was showing '150'. Apparently, we need to find the correct algorithm
here.
> input.frequency.nominal: 50
> input.transfer.high: 147
Here the UPS protocol reports '0', which is an offset to the default
transfer level that is configured for this UPS. This is now table
based, but this is wrong. The UPS probably has two defaults (for 120 V
and 230 V nominal respectively).
> input.transfer.low: 88
Same as for the 'input.transfer.high'.
> input.voltage: 176
This is shown as is, so apparently we need to apply a scaling and/or
offset to get the correct reading (the protocol is only able to report
values in the 0..255 range). I suspect that it will be the first
(since this is easier to do in hardware), so this factor is likely
close to (4/3) which would result in a corrected voltage of 234 V.
> input.voltage.nominal: 230
> output.voltage: 176
Same as for the 'input.voltage'.
> output.voltage.nominal: 120
Here the UPS protocol reports '0', which is an offset to the default
output voltage that is configured for this UPS. Most likely, this
offset should be added to the 'input.voltage.nominal' value. Now it is
value from a lookup table, which is quite wrong (you can probably set
the output to 220, 230 and 240 V).
> ups.beeper.status: enabled
> ups.firmware: 1.100
> ups.load: 24
> ups.mfr: CyberPower
> ups.model: PR3000E
> ups.serial: [unknown]
> ups.start.battery: yes
> ups.status: OL
> ups.temperature: 41
All in all it doesn't look too bad. There are a couple of readings
that need correcting however, so the support status would be
'experimental' for now.
> debian:~# upsrw -s input.transfer.high=129 -u local ups
> Password:
> Unexpected response from upsd: ERR ACCESS-DENIED
> - I always get the following message when I try to use upsrw:
> Unexpected response from upsd: ERR ACCESS-DENIED
> - Tested values: "input.transfer.high" and "battery.charge.low"
This is unrelated to the driver. The user 'local' apparently has not
been given access to change variables. See 'man 5 upsd.users' and 'man
5 upsd.conf' to give the user 'local' rights to do so.
> debian:~# upscmd -u local ups test.failure.start
> Password:
> - upscmd seems to have no effect and doesn't return something...
> - Tested values: "test.failure.start" and "test.failure.stop"
Same here as the above.
> I tested manual failure test mode (directly with the button on the hardware)
> and I also simulated a line failure and everything worked as expected (master
> and slaves machines shutdown and UPS shutdown).
The above means that the driver is useable with the PR3000E but
support is basic for now.
There should be a Linux driver available from CyberPower. This would
help us in finding the correct defaults for the
'input.transfer.(high|low)'. Could you run that and post your findings
here?
Best regards, Arjen
--