Citeren Marco Chiappero <marco op absence.it>:
> Sorry but I'm getting bored with this discussion, I would prefer be
> told that you do not want to include such code (which is not a
> problem) instead of reading sometimes pointless objections. The
> subdriver solution is not going to break backward compatibility or
> something else, while the driver approach would provide almost full
> NMC support to NUT without much pain. They do both integrates quite
> correctly in the current NUT structure, even though with possible
> limitations.
Maybe I just don't understand what you're trying to do. Suppose I have
two NMC equipped UPS devices that are currently controlled through two
netxml-ups drivers (and maybe a handful of clone drivers). Both
drivers are of course running on the same machine, since that's where
the upsd server also lives.
1) Both netxml-ups drivers can't connect at the same time via NSM to
their respective NMC's. We must have two instances of the netxml-ups
driver running (to provide access to all variables in the UPS) and as
far as I can see we can only accommodate one NSM client (due to the
listening socket that is needed for the callback from the NMC's) per
host.
2) You can't make *any* changes to the clients, since we not only have
installed bases of the upsmon NUT client that we provide (and granted,
where it would be trivial to add additional functionality) but also
quite a number of third party clients (Windows for instance). So to
the clients, the individual outlets of the two UPS'es would need to
appear as completely separate devices, with their own 'ups.status'
parameter (which is basically the only thing clients that need to
shutdown a machine look at).
As far as I can see, without changing the socket protocol between
between driver and server, the subdriver approach would break due to
1) and the driver approach due to 2).
What you fail to recognize is that in the existing socket protocol,
there is one driver (one socket) per 'ups.status' variable. This isn't
trivial. If you need multiple 'ups.status' variables to be able to
deal with switchable outlets, you also need multiple virtual UPS
devices in 'ups.conf, otherwise the clients will have no real/virtual
UPS to connect to (that's why we have the clone driver) and also
multiple driver sockets. I fail to see how either the subdriver or
driver approach can ever add these.
The only way I see how to solve this without rewriting half the upsd
server and/or requiring changes to the clients, is by creating a
'netnsm-ups' listener that would connect to all NMC's, without
actually providing a real/virtual UPS and create a special kind of
clone driver, that would connect both to one of the 'netxml-ups'
drivers running and also 'netnsm-ups' (to grab the 'ups.status' line).
[nsm-clone]
driver = netnsm-ups
port.ups1 = ups1.example.com
port.ups2 = ups2.example.com
[nmc-a]
# main outlet
driver = netxml-ups
port = ups1.example.com
[nmc-a-1]
driver = newclone
port = netxml-ups-nmc-a
outlet = nsm-clone-ups1-1
[nmc-a-2]
driver = newclone
port = netxml-ups-nmc-a
outlet = nsm-clone-ups1-2
[nmc-b]
# main outlet
driver = netxml-ups
port = ups2.example.com
[nmc-b-1]
driver = newclone
port = netxml-ups-nmc-b
outlet = nsm-clone-ups2-1
[nmc-b-2]
driver = newclone
port = netxml-ups-nmc-b
outlet = nsm-clone-ups2-2
There are probably ways to automate a couple of things here, but you
get the idea.
Best regards, Arjen
--