Hi,
I managed to find another Liebert UPS, this time a Liebert NXe 20KVA unit,
so I can help with the driver again.
This one has 2 serial ports, one gets disabled if you connect the ethernet
module. The other port is @9600bps. The 9600 is the one I use.
I applied Richard's patch with the bit correction, and tried the driver
(after changing the bitrate), but it failed at startup because Liebert NXe
doesn't provide its Serial Number. It seems when trying to read the initial
UPS model,SN etc, the UPS replies an invalid 5-byte reply instead of the
usual 8-byte one. I attach a debug output (hex)  from my upsesp2.c for
comparison. Look at line 109 of dbg_hex.txt.
The solution is to replace
        for (i = 0; i < 37; i++) {
with
        for (i = 0; i < 15; i++) {
to just check for MODEL_NAME
As for the CHARGED, it seems that in my case the battery BATTERY_CHARGED is
always NO perhaps because the UPS uses a percentage battery charge indicator
(BATTERY_CAPACITY). I'm not sure I follow your logic with ANDing with the OL
flag. The Charging could probably be deducted from the BATTERY_CURRENT
value.This could be negative if the battery is charging, but I cannot test
it right now.
./liebertgxt2 -a nxe -DD
Network UPS Tools - Liebert GXT2 serial UPS driver 0.02 (2.4.3-2420)
Warning: This is an experimental driver.
Some features may not function correctly.
   0.000000     debug level is '2'
   0.000737     send: (6 bytes) => 01 88 02 01 04 90
   0.072087     read: (8 bytes) => 01 88 04 01 04 69 4c 47
   0.072216     send: (6 bytes) => 01 88 02 01 05 91
   0.136206     read: (8 bytes) => 01 88 04 01 05 62 65 5a
   0.136343     send: (6 bytes) => 01 88 02 01 06 92
   0.202086     read: (8 bytes) => 01 88 04 01 06 72 65 6b
   0.202209     send: (6 bytes) => 01 88 02 01 07 93
   0.266083     read: (8 bytes) => 01 88 04 01 07 20 74 29
   0.266205     send: (6 bytes) => 01 88 02 01 08 94
   0.328099     read: (8 bytes) => 01 88 04 01 08 58 4e 3c
   0.328222     send: (6 bytes) => 01 88 02 01 09 95
   0.402090     read: (8 bytes) => 01 88 04 01 09 00 20 b7
   0.402212     send: (6 bytes) => 01 88 02 01 0a 96
   0.468096     read: (8 bytes) => 01 88 04 01 0a 00 00 98
   0.468220     send: (6 bytes) => 01 88 02 01 0b 97
   0.559082     read: (8 bytes) => 01 88 04 01 0b 00 00 99
   0.559205     send: (6 bytes) => 01 88 02 01 0c 98
   0.623082     read: (8 bytes) => 01 88 04 01 0c 00 00 9a
   0.623204     send: (6 bytes) => 01 88 02 01 0d 99
   0.687179     read: (8 bytes) => 01 88 04 01 0d 00 00 9b
   0.687316     send: (6 bytes) => 01 88 02 01 0e 9a
   0.753149     read: (8 bytes) => 01 88 04 01 0e 00 00 9c
   0.753285     send: (6 bytes) => 01 88 02 01 0f 9b
   0.818205     read: (8 bytes) => 01 88 04 01 0f 00 00 9d
   0.818342     send: (6 bytes) => 01 88 02 01 10 9c
   0.880087     read: (8 bytes) => 01 88 04 01 10 00 00 9e
   0.880210     send: (6 bytes) => 01 88 02 01 11 9d
   0.972080     read: (8 bytes) => 01 88 04 01 11 00 00 9f
   0.972203     send: (6 bytes) => 01 88 02 01 12 9e
   1.052085     read: (8 bytes) => 01 88 04 01 12 00 00 a0
   1.052211     send: (6 bytes) => 01 88 02 01 13 9f
   1.116147     read: (8 bytes) => 01 88 04 01 13 31 49 1b
   1.116283     send: (6 bytes) => 01 88 02 01 14 a0
   1.180087     read: (8 bytes) => 01 88 04 01 14 30 37 09
   1.180210     send: (6 bytes) => 01 88 02 01 15 a1
   1.263082     read: (8 bytes) => 01 88 04 01 15 31 52 26
   1.263205     send: (6 bytes) => 01 88 02 01 16 a2
   1.329086     read: (8 bytes) => 01 88 04 01 16 30 35 09
   1.329210     send: (6 bytes) => 01 88 02 01 17 a3
   1.395086     read: (8 bytes) => 01 88 04 01 17 32 4d 24
   1.395208     send: (6 bytes) => 01 88 02 01 18 a4
   1.469080     read: (8 bytes) => 01 88 04 01 18 30 36 0c
   1.469202     send: (6 bytes) => 01 88 02 01 19 a5
   1.533086     read: (8 bytes) => 01 88 04 01 19 00 00 a7
   1.533209     send: (6 bytes) => 01 88 02 01 1a a6
   1.597114     read: (8 bytes) => 01 88 04 01 1a 00 00 a8
   1.597239     send: (6 bytes) => 01 88 02 01 1b a7
   1.662085     read: truncated: (5 bytes) => 01 37 01 04 3d
   1.662194     GTX2 capable UPS not detected
On Tue, Apr 6, 2010 at 4:32 PM, Richard Gregory
<R.Gregory at liverpool.ac.uk>wrote:
> Hi All,
>
> There were other byte swap issues with the driver, making all the bit field
> flags wrong. Have swapped them and can confirm the OL, OB and CHRG flags
> work. CHaRGing is not the inverse of Liebert's BATTERY_CHARGED flag as that
> means CHRG is set when the UPS is on battery. Is it reasonable to correct
> for this by ANDing with the OL flag?
>
> Byte swapping patch attached.
>
>
> Richard
>
> +--                               --+
> |  Biological Sciences, Room 231    |
> |  http://www.csc.liv.ac.uk/~greg <http://www.csc.liv.ac.uk/%7Egreg>   |
> +--                               --+
>
> Arjen de Korte wrote:
>
>> Citeren Robert Jobbagy <jobbagy.robert at gmail.com>:
>>
>>  The trouble  was in the command reply buffer use.
>>> You compute the value that value = reply[6]*256+reply[5]  <- it's wrong
>>>
>>> The right solution: value = reply[5] * 256 + reply[6];
>>>
>>
>> Thanks for this patch. I just committed it to the development version.
>>  But please note that this is an experimental driver. Most of the  functions
>> are untested (since nobody took the time to try it out and  post the results
>> back to the mailing list).
>>
>>  And other bug,
>>>
>>> battery.runtime compute, you divide this value 60 <- it's wrong
>>>
>>> right value: divide 1.0
>>>
>>
>> Probably not. Per the NUT standard, the 'battery.runtime' value is
>>  reported in seconds. As far as I understand, the UPS reports runtime
>>  remaining in minutes, so we need to multiply by 60 here. See
>>  'docs/new-names.txt' for a listing of (almost) all variables supported  in
>> NUT.
>>
>>  I continue the work on this driver,and I will write if I make a something
>>> new.
>>>
>>
>> Please do. It should be trivial to add additional commands and  variables
>> to the existing ones.
>>
>> Best regards, Arjen
>>
>
> _______________________________________________
> Nut-upsdev mailing list
> Nut-upsdev at lists.alioth.debian.org
> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsdev/attachments/20100407/57f60bbf/attachment-0001.htm>
-------------- next part --------------
SendingM: 001,095,002,001,001,09A       BATTERY_TIME_REMAIN,bit/divider:1
READ    : 001,095,004,001,001,000,0E9,085
BATTERY_TIME_REMAIN: 233.0
SendingM: 001,095,002,001,002,09B       BATTERY_VOLTAGE,bit/divider:10
READ    : 001,095,004,001,002,015,021,0D3
BATTERY_VOLTAGE: 540.9
SendingM: 001,0A1,002,001,00D,0B2       BATTERY_VOLTAGE_NOMINAL,bit/divider:10
READ    : 001,0A1,004,001,00D,000,000,0B4
BATTERY_VOLTAGE_NOMINAL: 0.0
SendingM: 001,095,002,001,003,09C       BATTERY_CURRENT,bit/divider:1
READ    : 001,095,004,001,003,000,000,09E
BATTERY_CURRENT: 0.0
SendingM: 001,095,002,001,004,09D       BATTERY_CAPACITY,bit/divider:1
READ    : 001,095,004,001,004,000,05E,0FD
BATTERY_CAPACITY: 94.0
SendingM: 001,090,002,001,001,095       BYPASS_VOLTAGE,bit/divider:10
READ    : 001,090,004,001,001,009,040,0E0
BYPASS_VOLTAGE: 236.8
SendingM: 001,0A1,002,001,008,0AD       MAX_LOAD,bit/divider:1
READ    : 001,0A1,004,001,008,000,0C8,077
MAX_LOAD: 200.0
SendingM: 001,095,002,001,005,09E       LOAD_WATTS,bit/divider:1
READ    : 001,095,004,001,005,000,000,0A0
LOAD_WATTS: 0.0
SendingM: 001,095,002,001,006,09F       LOAD_VA,bit/divider:1
READ    : 001,095,004,001,006,000,000,0A1
LOAD_VA: 0.0
SendingM: 001,095,002,001,007,0A0       LOAD_PERCENT,bit/divider:1
READ    : 001,095,004,001,007,000,000,0A2
LOAD_PERCENT: 0.0
SendingM: 001,095,002,001,008,0A1       INPUT_FREQUENCY,bit/divider:10
READ    : 001,095,004,001,008,013,086,03C
INPUT_FREQUENCY: 499.8
SendingM: 001,095,002,001,009,0A2       OUTPUT_FREQUENCY,bit/divider:10
READ    : 001,095,004,001,009,013,082,039
OUTPUT_FREQUENCY: 499.4
SendingM: 001,095,002,001,00A,0A3       BYPASS_FREQUENCY,bit/divider:10
READ    : 001,095,004,001,00A,013,082,03A
BYPASS_FREQUENCY: 499.4
SendingM: 001,095,002,001,00B,0A4       INVERTER_TEMP,bit/divider:10
READ    : 001,095,004,001,00B,000,000,0A6
INVERTER_TEMP: 0.0
SendingM: 001,095,002,001,00C,0A5       BATTERY_TEMP,bit/divider:10
READ    : 001,095,004,001,00C,000,0C8,06F
BATTERY_TEMP: 20.0
SendingM: 001,095,002,001,00D,0A6       PFC_TEMP,bit/divider:10
READ    : 001,095,004,001,00D,000,000,0A8
PFC_TEMP: 0.0
SendingM: 001,095,002,001,00E,0A7       AMBIENT_TEMP,bit/divider:10
READ    : 001,095,004,001,00E,000,0FA,0A3
AMBIENT_TEMP: 25.0
SendingM: 001,090,002,001,003,097       OUTPUT_VOLTAGE,bit/divider:10
READ    : 001,090,004,001,003,009,007,0A9
OUTPUT_VOLTAGE: 231.1
SendingM: 001,090,002,001,004,098       OUTPUT_CURRENT,bit/divider:10
READ    : 001,090,004,001,004,000,028,0C2
OUTPUT_CURRENT: 4.0
SendingT: 001,088,002,001,004,090       MODEL_NAME,length:15
READ    : 001,088,004,001,004,069,04C,047
SendingT: 001,088,002,001,005,091       MODEL_NAME,length:14
READ    : 001,088,004,001,005,062,065,05A
SendingT: 001,088,002,001,006,092       MODEL_NAME,length:13
READ    : 001,088,004,001,006,072,065,06B
SendingT: 001,088,002,001,007,093       MODEL_NAME,length:12
READ    : 001,088,004,001,007,020,074,029
SendingT: 001,088,002,001,008,094       MODEL_NAME,length:11
READ    : 001,088,004,001,008,058,04E,03C
SendingT: 001,088,002,001,009,095       MODEL_NAME,length:10
READ    : 001,088,004,001,009,000,020,0B7
SendingT: 001,088,002,001,00A,096       MODEL_NAME,length:9
READ    : 001,088,004,001,00A,000,000,098
SendingT: 001,088,002,001,00B,097       MODEL_NAME,length:8
READ    : 001,088,004,001,00B,000,000,099
SendingT: 001,088,002,001,00C,098       MODEL_NAME,length:7
READ    : 001,088,004,001,00C,000,000,09A
SendingT: 001,088,002,001,00D,099       MODEL_NAME,length:6
READ    : 001,088,004,001,00D,000,000,09B
SendingT: 001,088,002,001,00E,09A       MODEL_NAME,length:5
READ    : 001,088,004,001,00E,000,000,09C
SendingT: 001,088,002,001,00F,09B       MODEL_NAME,length:4
READ    : 001,088,004,001,00F,000,000,09D
SendingT: 001,088,002,001,010,09C       MODEL_NAME,length:3
READ    : 001,088,004,001,010,000,000,09E
SendingT: 001,088,002,001,011,09D       MODEL_NAME,length:2
READ    : 001,088,004,001,011,000,000,09F
SendingT: 001,088,002,001,012,09E       MODEL_NAME,length:1
READ    : 001,088,004,001,012,000,000,0A0
MODEL_NAME: Liebert NX 
SendingT: 001,088,002,001,013,09F       FW_VER,length:8
READ    : 001,088,004,001,013,031,049,01B
SendingT: 001,088,002,001,014,0A0       FW_VER,length:7
READ    : 001,088,004,001,014,030,037,009
SendingT: 001,088,002,001,015,0A1       FW_VER,length:6
READ    : 001,088,004,001,015,031,052,026
SendingT: 001,088,002,001,016,0A2       FW_VER,length:5
READ    : 001,088,004,001,016,030,035,009
SendingT: 001,088,002,001,017,0A3       FW_VER,length:4
READ    : 001,088,004,001,017,032,04D,024
SendingT: 001,088,002,001,018,0A4       FW_VER,length:3
READ    : 001,088,004,001,018,030,036,00C
SendingT: 001,088,002,001,019,0A5       FW_VER,length:2
READ    : 001,088,004,001,019,000,000,0A7
SendingT: 001,088,002,001,01A,0A6       FW_VER,length:1
READ    : 001,088,004,001,01A,000,000,0A8
FW_VER: I170R150M260
SendingT: 001,088,002,001,01B,0A7       SN,length:10
READ    : 001,037,001,004,03D,000,000,000
SN: 
SendingT: 001,088,002,001,025,0B1       MANUF_DATE,length:4
READ    : 001,037,001,004,03D,000,000,000
MANUF_DATE: 
SendingM: 001,094,002,001,001,099       PFC_ON,bit/divider:0
READ    : 001,094,004,001,001,010,005,0B0
PFC_ON: YES
SendingM: 001,094,002,001,001,099       DC_DC_CONVERTER_STATE,bit/divider:1
READ    : 001,094,004,001,001,010,005,0B0
DC_DC_CONVERTER_STATE: NO
SendingM: 001,094,002,001,001,099       ON_INVERTER,bit/divider:2
READ    : 001,094,004,001,001,010,005,0B0
ON_INVERTER: YES
SendingM: 001,094,002,001,001,099       UTILITY_STATE,bit/divider:3
READ    : 001,094,004,001,001,010,005,0B0
UTILITY_STATE: NO
SendingM: 001,094,002,001,001,099       INRUSH_LIMIT_ON,bit/divider:4
READ    : 001,094,004,001,001,010,005,0B0
INRUSH_LIMIT_ON: NO
SendingM: 001,094,002,001,001,099       OVERTEMP_WARNING,bit/divider:5
READ    : 001,094,004,001,001,010,005,0B0
OVERTEMP_WARNING: NO
SendingM: 001,094,002,001,001,099       BATTERY_TEST_STATE,bit/divider:6
READ    : 001,094,004,001,001,010,005,0B0
BATTERY_TEST_STATE: NO
SendingM: 001,094,002,001,001,099       INPUT_OVERVOLTAGE,bit/divider:7
READ    : 001,094,004,001,001,010,005,0B0
INPUT_OVERVOLTAGE: NO
SendingM: 001,094,002,001,001,099       ON_BATTERY,bit/divider:8
READ    : 001,094,004,001,001,010,005,0B0
ON_BATTERY: NO
SendingM: 001,094,002,001,002,09A       ON_BYPASS,bit/divider:0
READ    : 001,094,004,001,002,000,000,09C
ON_BYPASS: NO
SendingM: 001,094,002,001,002,09A       BATTERY_CHARGED,bit/divider:1
READ    : 001,094,004,001,002,000,000,09C
BATTERY_CHARGED: NO
SendingM: 001,094,002,001,002,09A       BATTERY_LIFE_ENHANCER_ON,bit/divider:4
READ    : 001,094,004,001,002,000,000,09C
BATTERY_LIFE_ENHANCER_ON: NO
SendingM: 001,094,002,001,002,09A       REPLACE_BATTERY,bit/divider:5
READ    : 001,094,004,001,002,000,000,09C
REPLACE_BATTERY: NO
SendingM: 001,094,002,001,002,09A       BOOST_ON,bit/divider:6
READ    : 001,094,004,001,002,000,000,09C
BOOST_ON: NO
SendingM: 001,094,002,001,002,09A       DIAG_LINK_SET,bit/divider:7
READ    : 001,094,004,001,002,000,000,09C
DIAG_LINK_SET: NO
SendingM: 001,094,002,001,002,09A       BUCK_ON,bit/divider:9
READ    : 001,094,004,001,002,000,000,09C
BUCK_ON: NO
SendingM: 001,094,002,001,003,09B       UPS_OVERLOAD,bit/divider:0
READ    : 001,094,004,001,003,000,000,09D
UPS_OVERLOAD: NO
SendingM: 001,094,002,001,003,09B       BAD_INPUT_FREQ,bit/divider:1
READ    : 001,094,004,001,003,000,000,09D
BAD_INPUT_FREQ: NO
SendingM: 001,094,002,001,003,09B       SHUTDOWN_PENDING,bit/divider:2
READ    : 001,094,004,001,003,000,000,09D
SHUTDOWN_PENDING: NO
SendingM: 001,094,002,001,003,09B       CHARGER_FAIL,bit/divider:3
READ    : 001,094,004,001,003,000,000,09D
CHARGER_FAIL: NO
SendingM: 001,094,002,001,003,09B       LOW_BATTERY,bit/divider:5
READ    : 001,094,004,001,003,000,000,09D
LOW_BATTERY: NO
SendingM: 001,094,002,001,003,09B       OUTPUT_UNDERVOLTAGE,bit/divider:6
READ    : 001,094,004,001,003,000,000,09D
OUTPUT_UNDERVOLTAGE: NO
SendingM: 001,094,002,001,003,09B       OUTPUT_OVERVOLTAGE,bit/divider:7
READ    : 001,094,004,001,003,000,000,09D
OUTPUT_OVERVOLTAGE: NO
SendingM: 001,094,002,001,003,09B       BAD_BYPASS_PWR,bit/divider:8
READ    : 001,094,004,001,003,000,000,09D
BAD_BYPASS_PWR: NO
SendingM: 001,094,002,001,003,09B       CHECK_AIR_FILTER,bit/divider:10
READ    : 001,094,004,001,003,000,000,09D
CHECK_AIR_FILTER: NO
SendingM: 001,094,002,001,007,09F       AMBIENT_OVERTEMP,bit/divider:2
READ    : 001,094,004,001,007,000,000,0A1
AMBIENT_OVERTEMP: NO
SendingM: 001,094,002,001,013,0AB       MAIN_CONTROL_MODULE_FAILED,bit/divider:0
READ    : 001,094,004,001,013,000,000,0AD
MAIN_CONTROL_MODULE_FAILED: NO
SendingM: 001,094,002,001,013,0AB       REDUNDANT_CONTROL_MODULE_FAILED,bit/divider:1
READ    : 001,094,004,001,013,000,000,0AD
REDUNDANT_CONTROL_MODULE_FAILED: NO
SendingM: 001,094,002,001,013,0AB       UI_MODULE_FAILED,bit/divider:2
READ    : 001,094,004,001,013,000,000,0AD
UI_MODULE_FAILED: NO
SendingM: 001,094,002,001,013,0AB       REDUNDANT_POWER_MODULE_ALARM,bit/divider:3
READ    : 001,094,004,001,013,000,000,0AD
REDUNDANT_POWER_MODULE_ALARM: NO
SendingM: 001,094,002,001,013,0AB       REDUNDANT_BATTERY_MODULE_ALARM,bit/divider:4
READ    : 001,094,004,001,013,000,000,0AD
REDUNDANT_BATTERY_MODULE_ALARM: NO
SendingM: 001,094,002,001,013,0AB       USER_MAX_LOAD_ALARM,bit/divider:5
READ    : 001,094,004,001,013,000,000,0AD
USER_MAX_LOAD_ALARM: NO
SendingM: 001,094,002,001,013,0AB       TRANSFORMER_OVERTEMP_ALARM,bit/divider:6
READ    : 001,094,004,001,013,000,000,0AD
TRANSFORMER_OVERTEMP_ALARM: NO
SendingM: 001,094,002,001,013,0AB       INTERNAL_COMMS_LOST,bit/divider:7
READ    : 001,094,004,001,013,000,000,0AD
INTERNAL_COMMS_LOST: NO
SendingM: 001,094,002,001,013,0AB       PWR_MOD_FAILED,bit/divider:9
READ    : 001,094,004,001,013,000,000,0AD
PWR_MOD_FAILED: NO
SendingM: 001,094,002,001,013,0AB       BAT_MOD_FAILED,bit/divider:10
READ    : 001,094,004,001,013,000,000,0AD
BAT_MOD_FAILED: NO
SendingM: 001,094,002,001,014,0AC       OPTION_CARD_FAIL_1,bit/divider:0
READ    : 001,094,004,001,014,000,000,0AE
OPTION_CARD_FAIL_1: NO
SendingM: 001,094,002,001,014,0AC       OPTION_CARD_FAIL_2,bit/divider:1
READ    : 001,094,004,001,014,000,000,0AE
OPTION_CARD_FAIL_2: NO
SendingM: 001,094,002,001,014,0AC       OPTION_CARD_FAIL_3,bit/divider:2
READ    : 001,094,004,001,014,000,000,0AE
OPTION_CARD_FAIL_3: NO
SendingM: 001,094,002,001,014,0AC       OPTION_CARD_FAIL_4,bit/divider:3
READ    : 001,094,004,001,014,000,000,0AE
OPTION_CARD_FAIL_4: NO
SendingM: 001,094,002,001,014,0AC       OPTION_CARD_FAIL_5,bit/divider:4
READ    : 001,094,004,001,014,000,000,0AE
OPTION_CARD_FAIL_5: NO
SendingM: 001,094,002,001,014,0AC       OPTION_CARD_FAIL_6,bit/divider:5
READ    : 001,094,004,001,014,000,000,0AE
OPTION_CARD_FAIL_6: NO
SendingM: 001,094,002,001,014,0AC       OPTION_CARD_FAIL_7,bit/divider:6
READ    : 001,094,004,001,014,000,000,0AE
OPTION_CARD_FAIL_7: NO
SendingM: 001,094,002,001,014,0AC       OPTION_CARD_FAIL_8,bit/divider:7
READ    : 001,094,004,001,014,000,000,0AE
OPTION_CARD_FAIL_8: NO
SendingM: 001,094,002,001,016,0AE       SUMMARY_ALARM,bit/divider:0
READ    : 001,094,004,001,016,000,000,0B0
SUMMARY_ALARM: NO
SendingM: 001,094,002,001,018,0B0       RECT_UV_STARTUP_FAIL,bit/divider:0
READ    : 001,094,004,001,018,000,000,0B2
RECT_UV_STARTUP_FAIL: NO
SendingM: 001,094,002,001,018,0B0       RECT_FAULT,bit/divider:1
READ    : 001,094,004,001,018,000,000,0B2
RECT_FAULT: NO
SendingM: 001,094,002,001,018,0B0       RECT_OVER_CURRENT,bit/divider:2
READ    : 001,094,004,001,018,000,000,0B2
RECT_OVER_CURRENT: NO
SendingM: 001,094,002,001,018,0B0       RECT_OVER_TEMP,bit/divider:3
READ    : 001,094,004,001,018,000,000,0B2
RECT_OVER_TEMP: NO
SendingM: 001,094,002,001,018,0B0       RECT_INDCTR_OVER_TEMP,bit/divider:4
READ    : 001,094,004,001,018,000,000,0B2
RECT_INDCTR_OVER_TEMP: NO
SendingM: 001,094,002,001,018,0B0       RECT_COMM_FAIL,bit/divider:5
READ    : 001,094,004,001,018,000,000,0B2
RECT_COMM_FAIL: NO
SendingM: 001,094,002,001,018,0B0       INV_SHUTDOWN_LOW_DC,bit/divider:6
READ    : 001,094,004,001,018,000,000,0B2
INV_SHUTDOWN_LOW_DC: NO
SendingM: 001,094,002,001,018,0B0       INV_FAULT,bit/divider:7
READ    : 001,094,004,001,018,000,000,0B2
INV_FAULT: NO
SendingM: 001,094,002,001,018,0B0       INV_OVER_CURRENT,bit/divider:8
READ    : 001,094,004,001,018,000,000,0B2
INV_OVER_CURRENT: NO
SendingM: 001,094,002,001,018,0B0       INV_OVER_TEMP,bit/divider:9
READ    : 001,094,004,001,018,000,000,0B2
INV_OVER_TEMP: NO
SendingM: 001,094,002,001,018,0B0       INV_INDCTR_OVER_TEMP,bit/divider:10
READ    : 001,094,004,001,018,000,000,0B2
INV_INDCTR_OVER_TEMP: NO
SendingM: 001,094,002,001,018,0B0       INV_COMM_FAIL,bit/divider:11
READ    : 001,094,004,001,018,000,000,0B2
INV_COMM_FAIL: NO
SendingM: 001,094,002,001,018,0B0       INV_DC_OFFSET_OVR,bit/divider:12
READ    : 001,094,004,001,018,000,000,0B2
INV_DC_OFFSET_OVR: NO
SendingM: 001,094,002,001,018,0B0       INV_CONTACTOR_FAIL,bit/divider:13
READ    : 001,094,004,001,018,000,000,0B2
INV_CONTACTOR_FAIL: NO
SendingM: 001,094,002,001,019,0B1       BAT_FAULT,bit/divider:1
READ    : 001,094,004,001,019,080,000,033
BAT_FAULT: NO
SendingM: 001,094,002,001,019,0B1       BAT_CONTACTOR_FAIL,bit/divider:2
READ    : 001,094,004,001,019,080,000,033
BAT_CONTACTOR_FAIL: NO
SendingM: 001,094,002,001,019,0B1       CONVERTER_OVER_TEMP,bit/divider:4
READ    : 001,094,004,001,019,080,000,033
CONVERTER_OVER_TEMP: NO
SendingM: 001,094,002,001,019,0B1       CONVERTER_OVER_AMPS,bit/divider:5
READ    : 001,094,004,001,019,080,000,033
CONVERTER_OVER_AMPS: NO
SendingM: 001,094,002,001,019,0B1       CONVERTER_FAIL,bit/divider:6
READ    : 001,094,004,001,019,080,000,033
CONVERTER_FAIL: NO
SendingM: 001,094,002,001,019,0B1       BALANCER_OVER_TEMP,bit/divider:7
READ    : 001,094,004,001,019,080,000,033
BALANCER_OVER_TEMP: NO
SendingM: 001,094,002,001,019,0B1       BALANCER_FAULT,bit/divider:8
READ    : 001,094,004,001,019,080,000,033
BALANCER_FAULT: NO
SendingM: 001,094,002,001,019,0B1       BALANCER_OVER_CURRENT,bit/divider:9
READ    : 001,094,004,001,019,080,000,033
BALANCER_OVER_CURRENT: NO
SendingM: 001,094,002,001,019,0B1       BY_CB_OPEN,bit/divider:10
READ    : 001,094,004,001,019,080,000,033
BY_CB_OPEN: NO
SendingM: 001,094,002,001,019,0B1       LOAD_IMPACT_XFER,bit/divider:11
READ    : 001,094,004,001,019,080,000,033
LOAD_IMPACT_XFER: NO
SendingM: 001,094,002,001,019,0B1       OPERATION_FAULT,bit/divider:12
READ    : 001,094,004,001,019,080,000,033
OPERATION_FAULT: NO
SendingM: 001,094,002,001,019,0B1       OUT_FUSE_BLOWN,bit/divider:13
READ    : 001,094,004,001,019,080,000,033
OUT_FUSE_BLOWN: NO
SendingM: 001,094,002,001,019,0B1       ON_JOINT_MODE,bit/divider:14
READ    : 001,094,004,001,019,080,000,033
ON_JOINT_MODE: NO
SendingM: 001,094,002,001,01A,0B2       MAIN_NEUTRAL_LOST,bit/divider:4
READ    : 001,094,004,001,01A,000,003,0B7
MAIN_NEUTRAL_LOST: NO
SendingM: 001,094,002,001,01B,0B3       PARALLEL_LOW_BAT_WARN,bit/divider:4
READ    : 001,094,004,001,01B,000,001,0B6
PARALLEL_LOW_BAT_WARN: NO
SendingM: 001,094,002,001,01B,0B3       PARALLEL_LOAD_SHARE_FAULT,bit/divider:5
READ    : 001,094,004,001,01B,000,001,0B6
PARALLEL_LOAD_SHARE_FAULT: NO
SendingM: 001,094,002,001,01B,0B3       PARALLEL_FAULT,bit/divider:6
READ    : 001,094,004,001,01B,000,001,0B6
PARALLEL_FAULT: NO
SendingM: 001,094,002,001,01B,0B3       PARALLEL_CONNECT_FAULT,bit/divider:7
READ    : 001,094,004,001,01B,000,001,0B6
PARALLEL_CONNECT_FAULT: NO
SendingM: 001,094,002,001,01B,0B3       PARALLEL_COMM_FAIL,bit/divider:8
READ    : 001,094,004,001,01B,000,001,0B6
PARALLEL_COMM_FAIL: NO
SendingM: 001,094,002,001,01B,0B3       PARALLEL_SYS_OVER_LOAD,bit/divider:9
READ    : 001,094,004,001,01B,000,001,0B6
PARALLEL_SYS_OVER_LOAD: NO
SendingM: 001,094,002,001,01B,0B3       PARALLEL_SYS_XFER,bit/divider:10
READ    : 001,094,004,001,01B,000,001,0B6
PARALLEL_SYS_XFER: NO
Sleeping....
    
    
More information about the Nut-upsdev
mailing list