[Nut-upsdev] Liebert GXT2 NUT driver
Robert Jobbagy
jobbagy.robert at gmail.com
Wed Apr 7 10:00:51 UTC 2010
Hi Guys,
I tested this driver and I found a bug,
The wrong output:
device.serial: GXT2MR15D
ups.firmware: 12OCT04
ups.mfr.date: 0428100126AF041
ups.serial: GXT2MR15D
The right output:
device.serial: 0428100126AF041
ups.firmware: GXT2MR15D
ups.mfr.date: 12OCT04
ups.serial: 0428100126AF041
I fix it and attached the patch.
2010/4/7 Spiros Ioannou <sivann at gmail.com>
> On the battery issue:
> I did some tests:
> BATTERY_CAPACITY is always 94%, no matter its charge, probably indicating
> its decay.
> BATTERY_CHARGED is always NO for me
> BATTERY_CURRENT does actually indicate when battery is charging or
> discharging. In the case of discharging (ups on battery) a negative value is
> indicated.
> The correct value can be calculated as follows:
>
> float f;
> f=(signed short int)(256*H+L)/(float)100; //100 is the divider to convert
> value to Amperes.
>
> The actual value of BATTERY_CURRENT in Amperes need to be divided by 100:
> *CHARGING:*
> # ./upsesp2 /dev/ttyS0 BATTERY_CURRENT
> SendingM: 001,095,002,001,003,09C BATTERY_CURRENT,bit/divider:100
> READ : 001,095,004,001,003, 001,056 (001 086), 0F5 (returned values
> H,L are decimal 001 086)
> BATTERY_CURRENT: 3.4
>
> *DISCHARGING (on battery)*
> # ./upsesp2 /dev/ttyS0 BATTERY_CURRENT
> SendingM: 001,095,002,001,003,09C BATTERY_CURRENT,bit/divider:100
> READ : 001,095,004,001,003, 0FC,020 (252 032), 0BA
> BATTERY_CURRENT: -9.9
>
> -9.9 comes from (255-252)*256 + (255-032) or by casting to signed short int
> which does the same.
>
> After the power comes back on, between discharging and charging there is a
> period of no battery current (0 Amp) for a few seconds.
>
> -S
>
> On Tue, Apr 6, 2010 at 9:12 PM, Spiros Ioannou <sivann at gmail.com> wrote:
>
>> Hi,
>> I managed to find another Liebert UPS, this time a Liebert NXe 20KVA unit,
>> so I can help with the driver again.
>> This one has 2 serial ports, one gets disabled if you connect the ethernet
>> module. The other port is @9600bps. The 9600 is the one I use.
>>
>> I applied Richard's patch with the bit correction, and tried the driver
>> (after changing the bitrate), but it failed at startup because Liebert NXe
>> doesn't provide its Serial Number. It seems when trying to read the initial
>> UPS model,SN etc, the UPS replies an invalid 5-byte reply instead of the
>> usual 8-byte one. I attach a debug output (hex) from my upsesp2.c for
>> comparison. Look at line 109 of dbg_hex.txt.
>>
>> The solution is to replace
>> for (i = 0; i < 37; i++) {
>> with
>> for (i = 0; i < 15; i++) {
>>
>> to just check for MODEL_NAME
>>
>> As for the CHARGED, it seems that in my case the battery BATTERY_CHARGED
>> is always NO perhaps because the UPS uses a percentage battery charge
>> indicator (BATTERY_CAPACITY). I'm not sure I follow your logic with ANDing
>> with the OL flag. The Charging could probably be deducted from the
>> BATTERY_CURRENT value.This could be negative if the battery is charging, but
>> I cannot test it right now.
>>
>> ./liebertgxt2 -a nxe -DD
>> Network UPS Tools - Liebert GXT2 serial UPS driver 0.02 (2.4.3-2420)
>> Warning: This is an experimental driver.
>> Some features may not function correctly.
>>
>> 0.000000 debug level is '2'
>> 0.000737 send: (6 bytes) => 01 88 02 01 04 90
>> 0.072087 read: (8 bytes) => 01 88 04 01 04 69 4c 47
>> 0.072216 send: (6 bytes) => 01 88 02 01 05 91
>> 0.136206 read: (8 bytes) => 01 88 04 01 05 62 65 5a
>> 0.136343 send: (6 bytes) => 01 88 02 01 06 92
>> 0.202086 read: (8 bytes) => 01 88 04 01 06 72 65 6b
>> 0.202209 send: (6 bytes) => 01 88 02 01 07 93
>> 0.266083 read: (8 bytes) => 01 88 04 01 07 20 74 29
>> 0.266205 send: (6 bytes) => 01 88 02 01 08 94
>> 0.328099 read: (8 bytes) => 01 88 04 01 08 58 4e 3c
>> 0.328222 send: (6 bytes) => 01 88 02 01 09 95
>> 0.402090 read: (8 bytes) => 01 88 04 01 09 00 20 b7
>> 0.402212 send: (6 bytes) => 01 88 02 01 0a 96
>> 0.468096 read: (8 bytes) => 01 88 04 01 0a 00 00 98
>> 0.468220 send: (6 bytes) => 01 88 02 01 0b 97
>> 0.559082 read: (8 bytes) => 01 88 04 01 0b 00 00 99
>> 0.559205 send: (6 bytes) => 01 88 02 01 0c 98
>> 0.623082 read: (8 bytes) => 01 88 04 01 0c 00 00 9a
>> 0.623204 send: (6 bytes) => 01 88 02 01 0d 99
>> 0.687179 read: (8 bytes) => 01 88 04 01 0d 00 00 9b
>> 0.687316 send: (6 bytes) => 01 88 02 01 0e 9a
>> 0.753149 read: (8 bytes) => 01 88 04 01 0e 00 00 9c
>> 0.753285 send: (6 bytes) => 01 88 02 01 0f 9b
>> 0.818205 read: (8 bytes) => 01 88 04 01 0f 00 00 9d
>> 0.818342 send: (6 bytes) => 01 88 02 01 10 9c
>> 0.880087 read: (8 bytes) => 01 88 04 01 10 00 00 9e
>> 0.880210 send: (6 bytes) => 01 88 02 01 11 9d
>> 0.972080 read: (8 bytes) => 01 88 04 01 11 00 00 9f
>> 0.972203 send: (6 bytes) => 01 88 02 01 12 9e
>> 1.052085 read: (8 bytes) => 01 88 04 01 12 00 00 a0
>> 1.052211 send: (6 bytes) => 01 88 02 01 13 9f
>> 1.116147 read: (8 bytes) => 01 88 04 01 13 31 49 1b
>> 1.116283 send: (6 bytes) => 01 88 02 01 14 a0
>> 1.180087 read: (8 bytes) => 01 88 04 01 14 30 37 09
>> 1.180210 send: (6 bytes) => 01 88 02 01 15 a1
>> 1.263082 read: (8 bytes) => 01 88 04 01 15 31 52 26
>> 1.263205 send: (6 bytes) => 01 88 02 01 16 a2
>> 1.329086 read: (8 bytes) => 01 88 04 01 16 30 35 09
>> 1.329210 send: (6 bytes) => 01 88 02 01 17 a3
>> 1.395086 read: (8 bytes) => 01 88 04 01 17 32 4d 24
>> 1.395208 send: (6 bytes) => 01 88 02 01 18 a4
>> 1.469080 read: (8 bytes) => 01 88 04 01 18 30 36 0c
>> 1.469202 send: (6 bytes) => 01 88 02 01 19 a5
>> 1.533086 read: (8 bytes) => 01 88 04 01 19 00 00 a7
>> 1.533209 send: (6 bytes) => 01 88 02 01 1a a6
>> 1.597114 read: (8 bytes) => 01 88 04 01 1a 00 00 a8
>> 1.597239 send: (6 bytes) => 01 88 02 01 1b a7
>> 1.662085 read: truncated: (5 bytes) => 01 37 01 04 3d
>> 1.662194 GTX2 capable UPS not detected
>>
>>
>>
>> On Tue, Apr 6, 2010 at 4:32 PM, Richard Gregory <
>> R.Gregory at liverpool.ac.uk> wrote:
>>
>>> Hi All,
>>>
>>> There were other byte swap issues with the driver, making all the bit
>>> field flags wrong. Have swapped them and can confirm the OL, OB and CHRG
>>> flags work. CHaRGing is not the inverse of Liebert's BATTERY_CHARGED flag as
>>> that means CHRG is set when the UPS is on battery. Is it reasonable to
>>> correct for this by ANDing with the OL flag?
>>>
>>> Byte swapping patch attached.
>>>
>>>
>>> Richard
>>>
>>> +-- --+
>>> | Biological Sciences, Room 231 |
>>> | http://www.csc.liv.ac.uk/~greg <http://www.csc.liv.ac.uk/%7Egreg> |
>>> +-- --+
>>>
>>> Arjen de Korte wrote:
>>>
>>>> Citeren Robert Jobbagy <jobbagy.robert at gmail.com>:
>>>>
>>>> The trouble was in the command reply buffer use.
>>>>> You compute the value that value = reply[6]*256+reply[5] <- it's wrong
>>>>>
>>>>> The right solution: value = reply[5] * 256 + reply[6];
>>>>>
>>>>
>>>> Thanks for this patch. I just committed it to the development version.
>>>> But please note that this is an experimental driver. Most of the functions
>>>> are untested (since nobody took the time to try it out and post the results
>>>> back to the mailing list).
>>>>
>>>> And other bug,
>>>>>
>>>>> battery.runtime compute, you divide this value 60 <- it's wrong
>>>>>
>>>>> right value: divide 1.0
>>>>>
>>>>
>>>> Probably not. Per the NUT standard, the 'battery.runtime' value is
>>>> reported in seconds. As far as I understand, the UPS reports runtime
>>>> remaining in minutes, so we need to multiply by 60 here. See
>>>> 'docs/new-names.txt' for a listing of (almost) all variables supported in
>>>> NUT.
>>>>
>>>> I continue the work on this driver,and I will write if I make a
>>>>> something
>>>>> new.
>>>>>
>>>>
>>>> Please do. It should be trivial to add additional commands and
>>>> variables to the existing ones.
>>>>
>>>> Best regards, Arjen
>>>>
>>>
>>> _______________________________________________
>>> Nut-upsdev mailing list
>>> Nut-upsdev at lists.alioth.debian.org
>>> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
>>>
>>
>>
>
> _______________________________________________
> Nut-upsdev mailing list
> Nut-upsdev at lists.alioth.debian.org
> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
>
--
Best Regards,
Robert
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsdev/attachments/20100407/8cef8585/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: liebertgxt2_patch
Type: application/octet-stream
Size: 363 bytes
Desc: not available
URL: <http://lists.alioth.debian.org/pipermail/nut-upsdev/attachments/20100407/8cef8585/attachment-0001.obj>