[Nut-upsdev] Patch for HP T1000 INTL

Sturle Sunde sturles at gmail.com
Thu Apr 15 12:46:35 UTC 2010


Note:  I' not on this list and discovered the reply in the list
archive.  Please Cc me if you have more questions.  The archive does
not list all headers, so this mail will break threading.  I also
noticed the patch and output from lsusb is missing in the archive.

> Thanks for this report. Can you post the output from 'upsc' for this
> UPS? Which functionality did you test (if any?)

I monitored it with nut-monitor while testing with varying load,
disconnecting, connecting again, etc, and checked that reported values
were sensible.

Power input OK:

battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 30
battery.temperature: 29.9
battery.type: PbAC
battery.voltage: 27.3
battery.voltage.nominal: 24.0
device.mfr: Hewlett Packard
device.model: T1000 INTL
device.serial: 2CJ7471183
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3-2436M
driver.version.data: TrippLite HID 0.4
driver.version.internal: 0.34
input.frequency: 49.9
input.transfer.high: 278.0
input.transfer.low: 182.0
input.voltage: 237.6
input.voltage.nominal: 230
output.frequency: 49.9
output.frequency.nominal: 50
output.voltage: 237.6
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 60
ups.mfr: Hewlett Packard
ups.model: T1000 INTL
ups.power.nominal: 1000
ups.productid: 1f08
ups.serial: 2CJ7471183
ups.status: OL
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 03f0
ups.watchdog.status: 0


Unplugged:

battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 30
battery.temperature: 29.9
battery.type: PbAC
battery.voltage: 23.9
battery.voltage.nominal: 24.0
device.mfr: Hewlett Packard
device.model: T1000 INTL
device.serial: 2CJ7471183
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3-2436M
driver.version.data: TrippLite HID 0.4
driver.version.internal: 0.34
input.frequency: 0.0
input.transfer.high: 278.0
input.transfer.low: 182.0
input.transfer.reason: input voltage out of range
input.voltage: 3.1
input.voltage.nominal: 230
output.frequency: 50.0
output.frequency.nominal: 50
output.voltage: 230.0
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 58
ups.mfr: Hewlett Packard
ups.model: T1000 INTL
ups.power.nominal: 1000
ups.productid: 1f08
ups.serial: 2CJ7471183
ups.status: OB DISCHRG
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 03f0
ups.watchdog.status: 0

-- 
Sturle
~~~~~~