[Nut-upsdev] Syslog flooding
    Kelvin Ku 
    kelvin at telemetry-investments.com
       
    Mon Apr 26 14:08:26 UTC 2010
    
    
  
On Thu, Apr 22, 2010 at 10:45:33AM -0400, Kelvin Ku wrote:
> On Tue, Apr 20, 2010 at 03:13:07PM +0200, Arjen de Korte wrote:
> > Citeren Kelvin Ku <kelvin at telemetry-investments.com>:
> >
> >> Note that the problematic unit, upsserv7, exhibits the USB disconnect 
> >> behavior even when it's the only UPS connected to the host.
> >
> > If possible, run it in debug mode
> >
> >     /path/to/usbhid-ups -DD -a upsserv7
> >
> > and watch the output when it (re)connects. Chances are that the device  
> > is reporting different serial numbers (or none at all) depending whether 
> > this is the first connection made or a later one. We've seen such erratic 
> > behavior before on other devices. This will make it impossible for the 
> > driver to reconnect. You'll be specifically interested in lines with 
> > "Serial Number" in them (and a few lines of context before and after it).
> 
> I swapped the USB cable on upsserv7 for a new one and the connection was stable
> for a day. It started flaking out again today, though, so I tried what you
> suggested. Here's the syslog before I stopped the NUT service:
Another UPS of the same model connected to a different host is generating the
same flooding. As it stands, I can't monitor any of these Tripp Lite UPSs (I
have four of them) because of these spontaneous disconnects. Note that I
hacked in support for this model as follows:
--- nut-2.4.3/drivers/tripplite-hid.c.0 2010-03-24 10:34:10.238494000 -0400
+++ nut-2.4.3/drivers/tripplite-hid.c   2010-03-24 10:39:26.166498000 -0400
@@ -81,6 +81,9 @@
        { USB_DEVICE(TRIPPLITE_VENDORID, 0x4002), battery_scale_1dot0 },
        /* e.g. TrippLite SmartOnline SU1500RTXL2ua */
        { USB_DEVICE(TRIPPLITE_VENDORID, 0x4003), battery_scale_1dot0 },
+       /* e.g. TrippLite SmartOnline SU2200XLA */
+       { USB_DEVICE(TRIPPLITE_VENDORID, 0x4004), battery_scale_1dot0 },
+
 
        /* HP R/T 2200 INTL (like SMART2200RMXL2U) */
        { USB_DEVICE(HP_VENDORID, 0x1f0a), battery_scale_1dot0 },
[kelvin at ti94 nut-2.4.3-1.fc12.src]$ cat nut-2.4.3-tripplite.patch 
--- nut-2.4.3/scripts/udev/nut-usbups.rules.in.0        2010-03-24 10:32:35.773119000 -0400
+++ nut-2.4.3/scripts/udev/nut-usbups.rules.in  2010-03-24 10:33:21.767269000 -0400
@@ -102,6 +102,8 @@
 ATTR{idVendor}=="09ae", ATTR{idProduct}=="4002", MODE="664", GROUP="@RUN_AS_GROUP@"
 #  e.g. TrippLite SmartOnline SU1500RTXL2ua  - usbhid-ups
 ATTR{idVendor}=="09ae", ATTR{idProduct}=="4003", MODE="664", GROUP="@RUN_AS_GROUP@"
+#  e.g. TrippLite SmartOnline SU2200XLA  - usbhid-ups
+ATTR{idVendor}=="09ae", ATTR{idProduct}=="4004", RUN+="/bin/sh -c '/bin/chmod 664 /dev/bus/usb/*/*; /bin/chown root:dialout /dev/bus/usb/*/*'"
 
 # PowerCOM
 #  PowerCOM IMP - IMPERIAL Series  - usbhid-ups
--- nut-2.4.3/drivers/tripplite-hid.c.0 2010-03-24 10:34:10.238494000 -0400
+++ nut-2.4.3/drivers/tripplite-hid.c   2010-03-24 10:39:26.166498000 -0400
@@ -81,6 +81,9 @@
        { USB_DEVICE(TRIPPLITE_VENDORID, 0x4002), battery_scale_1dot0 },
        /* e.g. TrippLite SmartOnline SU1500RTXL2ua */
        { USB_DEVICE(TRIPPLITE_VENDORID, 0x4003), battery_scale_1dot0 },
+       /* e.g. TrippLite SmartOnline SU2200XLA */
+       { USB_DEVICE(TRIPPLITE_VENDORID, 0x4004), battery_scale_1dot0 },
+
 
        /* HP R/T 2200 INTL (like SMART2200RMXL2U) */
        { USB_DEVICE(HP_VENDORID, 0x1f0a), battery_scale_1dot0 },
Is it possible that tripplite_usb.c needs to be updated to work with this
model's particular quirks, or is the hardware simply too flakey to be used with
NUT?
Syslog and related output is below:
Apr 26 02:59:51 kernel: hub 2-0:1.0: port 3 disabled by hub (EMI?), re-enabling...
Apr 26 02:59:51 kernel: usb 2-3: USB disconnect, address 3
Apr 26 02:59:51 kernel: usb 2-3: new low speed USB device using ohci_hcd and address 5
Apr 26 02:59:51 kernel: usb 2-3: configuration #1 chosen from 1 choice
Apr 26 02:59:51 kernel: hiddev96: USB HID v1.11 Device [Tripp Lite       TRIPP LITE UPS  ] on usb-0000:00:02.0-3
Apr 26 02:59:53 usbhid-ups[15075]: Got disconnected by another driver: Device or resource busy
Apr 26 02:59:55 usbhid-ups[15075]: Got disconnected by another driver: Device or resource busy
Apr 26 02:59:57 usbhid-ups[15075]: Got disconnected by another driver: Device or resource busy
...
Apr 26 03:33:39 usbhid-ups[15075]: Got disconnected by another driver: Device or resource busy
Apr 26 03:33:41 usbhid-ups[15075]: Got disconnected by another driver: Device or resource busy
Apr 26 03:33:43 usbhid-ups[15075]: Got disconnected by another driver: Device or resource busy
Apr 26 03:33:45 upsd[15088]: Data for UPS [upsserv6] is stale - check driver
Apr 26 03:33:47 upsmon[15093]: Poll UPS [upsserv6 at localhost] failed - Data stale
Apr 26 03:33:47 upsmon[15093]: INFO UPS upsserv6 at localhost communications lost
Apr 26 03:33:52 upsmon[15093]: Poll UPS [upsserv6 at localhost] failed - Data stale
Apr 26 03:33:57 upsmon[15093]: Poll UPS [upsserv6 at localhost] failed - Data stale
Apr 26 03:34:02 upsmon[15093]: Poll UPS [upsserv6 at localhost] failed - Data stale
...
Apr 26 08:14:47 upsmon[15093]: Poll UPS [upsserv6 at localhost] failed - Data stale
Apr 26 08:14:52 upsmon[15093]: Poll UPS [upsserv6 at localhost] failed - Data stale
Apr 26 08:14:57 upsmon[15093]: Poll UPS [upsserv6 at localhost] failed - Data stale
Apr 26 08:14:59 upsmon[15093]: Signal 15: exiting
Apr 26 08:14:59 upsd[15088]: User upsmon at 127.0.0.1 logged out from UPS [upsserv6]
Apr 26 08:14:59 upsd[15088]: User upsmon at 127.0.0.1 logged out from UPS [upsserv5]
Apr 26 08:14:59 upsd[15088]: mainloop: Interrupted system call
Apr 26 08:14:59 upsd[15088]: Signal 15: exiting
$ sudo cat /etc/ups/ups.conf
maxstartdelay = 120
[upsserv6]
        driver = usbhid-ups
        port = auto
        serial = 9824ALCPS720000081
[upsserv5]
        driver = usbhid-ups
        port = auto
        serial = 9833DLCPS720000101
$ sudo usbhid-ups -DD -a upsserv6
Network UPS Tools - Generic HID driver 0.34 (2.4.3)
USB communication driver 0.31
   0.000000	debug level is '2'
   0.000682	upsdrv_initups...
   0.001085	Checking device (09AE/4004) (002/005)
   0.021881	- VendorID: 09ae
   0.021984	- ProductID: 4004
   0.022121	- Manufacturer: Tripp Lite      
   0.022259	- Product: TRIPP LITE UPS  
   0.022399	- Serial Number: 9824ALCPS720000081  
   0.022528	- Bus: 002
   0.022599	Trying to match device
   0.022944	Device matches
   0.030887	HID descriptor length 1082
   0.067878	Report Descriptor size = 1082
   0.068412	Using subdriver: TrippLite HID 0.4
   0.070877	libusb_get_report: No error
   0.070967	Can't retrieve Report 28: Inappropriate ioctl for device
   0.071123	Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8
   0.073874	libusb_get_report: No error
   0.073901	Can't retrieve Report 29: Inappropriate ioctl for device
   0.074034	Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8
   0.076875	libusb_get_report: No error
   0.076958	Can't retrieve Report 2b: Inappropriate ioctl for device
   0.077099	Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 0, Size: 8
   0.079875	libusb_get_report: No error
   0.079902	Can't retrieve Report 30: Inappropriate ioctl for device
   0.080104	Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8
   0.082875	libusb_get_report: No error
   0.082901	Can't retrieve Report 31: Inappropriate ioctl for device
   0.083036	Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16
   0.085875	libusb_get_report: No error
   0.085969	Can't retrieve Report 11: Inappropriate ioctl for device
   0.086110	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8
   0.088874	libusb_get_report: No error
   0.088900	Can't retrieve Report 2a: Inappropriate ioctl for device
   0.089033	Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8
   0.091874	libusb_get_report: No error
   0.091900	Can't retrieve Report 62: Inappropriate ioctl for device
   0.092031	Path: UPS.PowerSummary.iOEMInformation, Type: Feature, ReportID: 0x62, Offset: 0, Size: 8
   0.094874	libusb_get_report: No error
   0.094958	Can't retrieve Report 33: Inappropriate ioctl for device
   0.095099	Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8
   0.097874	libusb_get_report: No error
   0.097901	Can't retrieve Report 34: Inappropriate ioctl for device
   0.098034	Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8
   0.100874	libusb_get_report: No error
   0.100955	Can't retrieve Report 34: Inappropriate ioctl for device
   0.101098	Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8
   0.103874	libusb_get_report: No error
   0.103900	Can't retrieve Report 3a: Inappropriate ioctl for device
   0.104032	Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x3a, Offset: 0, Size: 8
   0.106874	libusb_get_report: No error
   0.106900	Can't retrieve Report 37: Inappropriate ioctl for device
   0.107034	Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, Offset: 0, Size: 8
   0.109873	libusb_get_report: No error
   0.109899	Can't retrieve Report 36: Inappropriate ioctl for device
   0.110032	Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8
   0.112874	libusb_get_report: No error
   0.112954	Can't retrieve Report 38: Inappropriate ioctl for device
   0.113096	Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x38, Offset: 0, Size: 8
   0.115873	libusb_get_report: No error
   0.115899	Can't retrieve Report 3b: Inappropriate ioctl for device
   0.116031	Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, ReportID: 0x3b, Offset: 0, Size: 8
   0.118873	libusb_get_report: No error
   0.118899	Can't retrieve Report 39: Inappropriate ioctl for device
   0.119031	Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, ReportID: 0x39, Offset: 0, Size: 8
   0.121874	libusb_get_report: No error
   0.121900	Can't retrieve Report 2c: Inappropriate ioctl for device
   0.122032	Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x2c, Offset: 0, Size: 8
   0.124874	libusb_get_report: No error
   0.124957	Can't retrieve Report 35: Inappropriate ioctl for device
   0.125098	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16
   0.127873	libusb_get_report: No error
   0.127899	Can't retrieve Report 35: Inappropriate ioctl for device
   0.128031	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16
   0.130873	libusb_get_report: No error
   0.130954	Can't retrieve Report 32: Inappropriate ioctl for device
   0.131095	Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x32, Offset: 7, Size: 1
   0.133874	libusb_get_report: No error
   0.133900	Can't retrieve Report 32: Inappropriate ioctl for device
   0.134035	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 9, Size: 1
   0.136874	libusb_get_report: No error
   0.136974	Can't retrieve Report 32: Inappropriate ioctl for device
   0.137126	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 16, Size: 1
   0.139874	libusb_get_report: No error
   0.139900	Can't retrieve Report 32: Inappropriate ioctl for device
   0.140033	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 18, Size: 1
   0.142873	libusb_get_report: No error
   0.142899	Can't retrieve Report 32: Inappropriate ioctl for device
   0.143032	Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 19, Size: 1
   0.145873	libusb_get_report: No error
   0.145955	Can't retrieve Report 32: Inappropriate ioctl for device
   0.146097	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 20, Size: 1
   0.148873	libusb_get_report: No error
   0.148899	Can't retrieve Report 32: Inappropriate ioctl for device
   0.149032	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 21, Size: 1
   0.151874	libusb_get_report: No error
   0.151900	Can't retrieve Report 32: Inappropriate ioctl for device
   0.152034	Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 22, Size: 1
   0.154874	libusb_get_report: No error
   0.154900	Can't retrieve Report 32: Inappropriate ioctl for device
   0.155035	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 23, Size: 1
   0.157873	libusb_get_report: No error
   0.157955	Can't retrieve Report 32: Inappropriate ioctl for device
   0.158098	Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1
   0.160874	libusb_get_report: No error
   0.160956	Can't retrieve Report 32: Inappropriate ioctl for device
   0.161098	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 9, Size: 1
   0.163873	libusb_get_report: No error
   0.163900	Can't retrieve Report 32: Inappropriate ioctl for device
   0.164036	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1
   0.166874	libusb_get_report: No error
   0.166899	Can't retrieve Report 32: Inappropriate ioctl for device
   0.167032	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1
   0.169874	libusb_get_report: No error
   0.169956	Can't retrieve Report 32: Inappropriate ioctl for device
   0.170099	Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1
   0.172873	libusb_get_report: No error
   0.172899	Can't retrieve Report 32: Inappropriate ioctl for device
   0.173065	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1
   0.175874	libusb_get_report: No error
   0.175900	Can't retrieve Report 32: Inappropriate ioctl for device
   0.176035	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1
   0.178874	libusb_get_report: No error
   0.178956	Can't retrieve Report 32: Inappropriate ioctl for device
   0.179098	Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1
   0.181874	libusb_get_report: No error
   0.181900	Can't retrieve Report 32: Inappropriate ioctl for device
   0.182036	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 23, Size: 1
   0.184873	libusb_get_report: No error
   0.184899	Can't retrieve Report 04: Inappropriate ioctl for device
   0.185033	Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16
   0.187873	libusb_get_report: No error
   0.187898	Can't retrieve Report 20: Inappropriate ioctl for device
   0.188031	Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16
   0.190872	libusb_get_report: No error
   0.190898	Can't retrieve Report 23: Inappropriate ioctl for device
   0.191031	Path: UPS.BatterySystem.Battery.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x23, Offset: 2, Size: 1
   0.193872	libusb_get_report: No error
   0.193898	Can't retrieve Report 23: Inappropriate ioctl for device
   0.194032	Path: UPS.BatterySystem.Battery.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x23, Offset: 3, Size: 1
   0.196873	libusb_get_report: No error
   0.196898	Can't retrieve Report 23: Inappropriate ioctl for device
   0.197032	Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, ReportID: 0x23, Offset: 4, Size: 1
   0.199873	libusb_get_report: No error
   0.199955	Can't retrieve Report 23: Inappropriate ioctl for device
   0.200098	Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, ReportID: 0x23, Offset: 5, Size: 1
   0.202873	libusb_get_report: No error
   0.202899	Can't retrieve Report 23: Inappropriate ioctl for device
   0.203033	Path: UPS.BatterySystem.Battery.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x23, Offset: 6, Size: 1
   0.205882	libusb_get_report: No error
   0.205908	Can't retrieve Report 23: Inappropriate ioctl for device
   0.206065	Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x23, Offset: 7, Size: 1
   0.208872	libusb_get_report: No error
   0.208897	Can't retrieve Report 21: Inappropriate ioctl for device
   0.209031	Path: UPS.BatterySystem.Battery.RemainingCapacity, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8
   0.211872	libusb_get_report: No error
   0.211898	Can't retrieve Report 10: Inappropriate ioctl for device
   0.212031	Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8
   0.214872	libusb_get_report: No error
   0.214898	Can't retrieve Report 1a: Inappropriate ioctl for device
   0.215030	Path: UPS.BatterySystem.Temperature, Type: Feature, ReportID: 0x1a, Offset: 0, Size: 16
   0.217873	libusb_get_report: No error
   0.217955	Can't retrieve Report 01: Inappropriate ioctl for device
   0.218095	Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8
   0.220873	libusb_get_report: No error
   0.220900	Can't retrieve Report 02: Inappropriate ioctl for device
   0.221049	Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8
   0.223881	Can't retrieve Report 55: Broken pipe
   0.223967	Path: UPS.Flow.ffff0097, Type: Feature, ReportID: 0x55, Offset: 0, Size: 8
   0.226873	libusb_get_report: error sending control message: Broken pipe
   0.226955	Can't retrieve Report 03: Broken pipe
...
- Kelvin
    
    
More information about the Nut-upsdev
mailing list