[Nut-upsdev] smart1050slt by tripp lite
chance fulton
chance.fulton at gmail.com
Mon Feb 1 01:49:08 UTC 2010
If there is anything else you want done with this I am available to test
most days.
I did not have time to capture the poweroff event, as it would take me
an hour or so to kill the ups without making too much noise :)
Added secondary load around 60
Power fail at 123
return power at 182
Load removed at 240
Hope this helps.
I can let it run much longer if required, I only stopped it for the sake
of the list.
On Sun, 2010-01-31 at 20:03 -0500, Charles Lepple wrote:
> On Jan 31, 2010, at 7:07 PM, chance fulton wrote:
>
> > The tee command is not working on my system, so I have been copying
> > the
> > output out of my terminal session. I also cannot redirect it with > or
> >>> , as the output does not end up in the file.
> >
> > If I let it run a long time, I won't be able to copy it to the
> > beginning.
> >
> > Any Ideas??
>
> Forgot to mention - you need to add '2>&1' before '|tee'.
>
> That will catch both stdout and stderr.
-------------- next part --------------
A non-text attachment was scrubbed...
Name: r2300.txt.gz
Type: application/x-gzip
Size: 24590 bytes
Desc: not available
URL: <http://lists.alioth.debian.org/pipermail/nut-upsdev/attachments/20100131/4d5e892d/attachment-0001.bin>