Hi Arjen!
I attached the wrong and correct output , please check it.
The HEAD version liebert-esp2 driver give wrong output,but if you patch it
with my patch it will be correct.
In outputs.log focus on model,firmware,serial and mfr date values.
And I attached my patch earlier.
2010/7/6 Arjen de Korte <nut+devel at de-korte.org <nut%2Bdevel at de-korte.org>>
> Citeren Robert Jobbagy <jobbagy.robert at gmail.com>:
>
>
> I checked out the HEAD rev and tried the liebert driver.
>> it gave wrong model,firmware,serial, mfr date value. caused by len
>> variable
>> in line 97 and after
>>
>
> If you provide the debug output, this will save us looking up the last time
> you posted the results.
>
>
> I use my ups with usb -> serial converter.
>>
>
> Which one?
>
>
> these patches attached
>>
>> Did you try the liebert-esp2 driver in ON Battery mode ?
>>
>
> I don't have one, so I can't tell.
>
>
> Because If I switch my ups on battery (plugged off the input) then liebert
>> driver force shutdown PC and shutdown UPS.
>>
>
> In it's present state, the liebert-esp2 driver can't shutdown the UPS.
>
>
> Battery is full charged. UPS doesnt recieve LOW BATTERY EVENT.
>>
>
> How old are the batteries? When was the last time you ran a battery test?
> This sounds more like a bad battery than a driver problem. Worn out
> batteries are a common cause of mishaps like these, where the batteries seem
> to be fine when not loaded (mains present), but fail under load (mains
> failure) within seconds.
>
>
> the shutdown function is missing from liebert-esp2 driver, this is the
>> reason the force shutdown ?
>>
>
> The driver won't be able to shutdown the UPS if the upsdrv_shutdown
> function is not functional. If the UPS kills the output, it is not caused by
> NUT but most likely by the battery protection.
>
> Best regards, Arjen
> --
> Please keep list traffic on the list
>
>
> _______________________________________________
> Nut-upsdev mailing list
> Nut-upsdev at lists.alioth.debian.org
> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
>
--
Best Regards,
Robert
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsdev/attachments/20100709/e43b3e9f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: liebert_outputs.log
Type: text/x-log
Size: 1564 bytes
Desc: not available
URL: <http://lists.alioth.debian.org/pipermail/nut-upsdev/attachments/20100709/e43b3e9f/attachment.bin>
More information about the Nut-upsdev
mailing list