Hi all!

I read this in the shutdown.txt:

Here are the steps that occur when a critical power event happens:

1. The UPS goes on battery

2. The UPS reaches low battery (a "critical" UPS)

3. The upsmon master notices and sets "FSD" - the "forced shutdown"
   flag to tell all slave systems that it will soon power down the load.


But If I use my ups with nut on Battery when UPS don't send LB event just do
Output OFF and kill PC and after itself.

I don't understand when or why called the upsdrv_shutdown function?

Please someone tell me what happens if UPS works on battery and I use NUT.

Thanks your advice.

2010/7/9 Robert Jobbagy <jobbagy.robert at gmail.com>

> Hi Arjen!
>
> I attached the wrong and correct output , please check it.
> The HEAD version liebert-esp2 driver give wrong output,but if you patch it
> with my patch it will be correct.
> In outputs.log focus on model,firmware,serial and mfr date values.
>
> And I attached my patch earlier.
>
> 2010/7/6 Arjen de Korte <nut+devel at de-korte.org <nut%2Bdevel at de-korte.org>
> >
>
> Citeren Robert Jobbagy <jobbagy.robert at gmail.com>:
>>
>>
>>  I checked out the HEAD rev and tried the liebert driver.
>>> it gave wrong model,firmware,serial, mfr date value. caused by len
>>> variable
>>> in line 97 and after
>>>
>>
>> If you provide the debug output, this will save us looking up the last
>> time you posted the results.
>>
>>
>>  I use my ups with usb -> serial converter.
>>>
>>
>> Which one?
>>
>>
>>  these patches attached
>>>
>>> Did you try the liebert-esp2 driver in ON Battery mode ?
>>>
>>
>> I don't have one, so I can't tell.
>>
>>
>>  Because If I switch my ups on battery (plugged off the input) then
>>> liebert
>>> driver force shutdown PC and shutdown UPS.
>>>
>>
>> In it's present state, the liebert-esp2 driver can't shutdown the UPS.
>>
>>
>>  Battery is full charged. UPS doesnt recieve LOW BATTERY EVENT.
>>>
>>
>> How old are the batteries? When was the last time you ran a battery test?
>> This sounds more like a bad battery than a driver problem. Worn out
>> batteries are a common cause of mishaps like these, where the batteries seem
>> to be fine when not loaded (mains present), but fail under load (mains
>> failure) within seconds.
>>
>>
>>  the shutdown function is missing from liebert-esp2 driver, this is the
>>> reason the force shutdown ?
>>>
>>
>> The driver won't be able to shutdown the UPS if the upsdrv_shutdown
>> function is not functional. If the UPS kills the output, it is not caused by
>> NUT but most likely by the battery protection.
>>
>> Best regards, Arjen
>> --
>> Please keep list traffic on the list
>>
>>
>> _______________________________________________
>> Nut-upsdev mailing list
>> Nut-upsdev at lists.alioth.debian.org
>> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
>>
>
>
>
> --
> Best Regards,
>
> Robert
>



-- 
Best Regards,

Robert