Hi, I'd like to inform You that this UPS communicates well via the
serial port. I haven't tested USB, and no shutdown testing so far,
however, I hope it will run well.
HP R5000
upsc output:
ambient.temperature: 27.4
ambient.temperature.high: 45
battery.charge: 99.0
battery.runtime: 536
battery.voltage: 236.3
device.mfr: Eaton
device.model: HP R5000 5000i
device.serial: 3C81520083
device.type: ups
driver.name: bcmxcp
driver.parameter.baud_rate: 9600
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS0
driver.version: 2.4.3
driver.version.internal: 0.23
input.current: 18.1
input.frequency: 50.0
input.frequency.high: 54
input.frequency.low: 46
input.frequency.nominal: 50
input.transfer.boost.high: 202
input.transfer.high: 288
input.transfer.low: 176
input.transfer.trim.low: 257
input.voltage: 224.1
input.voltage.nominal: 230
outlet.1.delay.shutdown: -1
outlet.1.delay.start: 0
outlet.1.id: 1
outlet.1.status: On
outlet.2.delay.shutdown: 258
outlet.2.delay.start: -1
outlet.2.id: 0
outlet.2.status: Off
output.current: 16.4
output.current.nominal: 21.7
output.frequency: 50.0
output.phases: 1
output.voltage: 222.2
output.voltage.nominal: 230
ups.beeper.status: muted
ups.firmware: Cont:01.02 Inve:01.02
ups.load: 73.1
ups.mfr: Eaton
ups.model: HP R5000 5000i
ups.power: 3655.0
ups.power.nominal: 5000
ups.serial: 3C81520083
ups.status: OL
upscmd output:
Instant commands supported on UPS [hpblade]:
outlet.1.shutdown.return - Description unavailable
outlet.2.shutdown.return - Description unavailable
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
test.battery.start - Start a battery test
shutdown sequence testing results:
No testing so far. Should any take place, I'll let You know.
Quick Specs:
http://h18004.www1.hp.com/products/quickspecs/14109_na/14109_na.pdf
Sincerely
Peter
More information about the Nut-upsdev
mailing list