[Nut-upsdev] [HCL] <JAWAN> <JW-UPSLC02> supported by <blazer_usb>
    David Méndez 
    davigre at hotmail.com
       
    Fri Feb 20 15:20:08 UTC 2015
    
    
  
Device manufacturer: JAWAN tech
Name:JW-UPSLC02
[upsc output]
battery.charge: 100
battery.voltage: 13.60
battery.voltage.high: 13
battery.voltage.low: 10.4
battery.voltage.nominal: 12.0
device.mfr:
device.model:
device.type: ups
driver.name: blazer_usb
driver.parameter.chargetime: 43200
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 5161
driver.parameter.vendorid: 0665
driver.version: 2.7.2
driver.version.internal: 0.11
input.current.nominal: 6.0
input.frequency: 60.0
input.frequency.nominal: 60
input.voltage: 118.0
input.voltage.fault: 118.0
input.voltage.nominal: 115
output.voltage: 118.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 180
ups.firmware: B1.12_APFB
ups.load: 29
ups.mfr:
ups.model:
ups.productid: 5161
ups.status: OL
ups.temperature: 32.0
ups.type: offline / line interactive
ups.vendorid: 0665
[upscmd -l <ups> output]
beeper.toggle - Toggle the UPS beeper
load.off - Turn off the load immediately
load.on - Turn on the load immediately
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start - Start a battery test
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
    
    
More information about the Nut-upsdev
mailing list