[Nut-upsdev] nutdrv_qx and Best Power equipment

Charles Lepple clepple at gmail.com
Sun Jan 18 18:12:32 UTC 2015


On Sun, Jan 18, 2015 at 1:07 PM, Charles Lepple <clepple at gmail.com> wrote:
> On Fri, Jan 2, 2015 at 7:31 PM, hyouko at gmail.com <hyouko at gmail.com> wrote:
>> Before I merge it (well.. provided that it works..), I'd like to know
>> a couple of things more:
>> 1. does the load.off command ('S00R0000') work?
>
> load.off works.
>
>> 2. does the 'C' command (mapped as shutdown.stop and load.on) turn the
>> load on if executed while the ups.delay.start time elapses after
>> having fired a shutdown.return?
>
> I only tested the following case, but yes:
>
> 1) removed power
> 2) ran shutdown.return
> 3) waited for 30-second shutdown timer; UPS turns off
> 4) reconnected power
> 5) before 180 second power-on timer elapses, run load.on
> 6) UPS turns on
>
>> 3. (OK, I lied - 3 things more) does the shutdown.stayoff command
>> ('SnR0000') work?
>
> shutdown.stayoff does not work - the UPS turns on immediately after
> its usual (~5 second) self-test.
>
> I tried it with both the default 30-second ups.delay.shutdown
> (S.5R0000), as well as 60 seconds (S01R0000).
>
> I don't think this is a regression for my model, although the docs
> suggest sending the command without the "R####":
> http://buildbot.networkupstools.org/~buildbot/cayman/docs/latest/protocols/sola.html#_shutdown_command

For completeness' sake, I should mention that this was tested against
commit 99b37b4. No surprises in the log file (-DDDDD), but I have it
in case you need it.

-- 
- Charles Lepple



More information about the Nut-upsdev mailing list