[Nut-upsdev] [HCL] NHS Laser Senoidal 5000VA supported by gamatronic
Charles Lepple
clepple at gmail.com
Wed Jan 6 03:47:19 UTC 2016
This is the same as https://github.com/networkupstools/nut/issues/254 , right?
(It's on my TODO list. DDL updates take a little longer than HCL updates.)
Other comments below.
> On Dec 29, 2015, at 1:55 PM, Thiago Wiezbicki - NHS <thiago.wiezbicki at nhs.com.br> wrote:
>
> Device Manufacturer: NHS
> Device Name: Laser Senoidal 5000VA
>
> upsc output when the UPS is in normal condition:
>
> battery.charge: 100
> battery.current: 0.4
> battery.date: 12292015
> battery.runtime: 00000
Does battery.runtime only get updated when on battery power, or is this with a different load?
> battery.runtime.low: 59940
> battery.temperature: 00
Is this fixed at 0, or is there a temperature option?
> battery.voltage: 163.4
> device.mfr: NHS Sistemas de Energia
> device.model: Laser Senoidal 5000VA
> device.type: ups
> driver.name: gamatronic
> driver.parameter.pollinterval: 20
> driver.parameter.port: /dev/ttyACM2
> driver.version: 2.6.3
> driver.version.internal: 0.02
> input.frequency: 59.9
> input.transfer.high: 144
> input.transfer.low: 096
> input.voltage: 127.6
> input.voltage.nominal: 120
> output.current: 0.0
> output.frequency: 60.0
> output.voltage: 119.1
> ups.firmware: LSPWM(15).55
> ups.id: ny7bd8723tbecabc
> ups.load: 000
> ups.mfr: NHS Sistemas de Energia
> ups.model: Laser Senoidal 5000VA
> ups.power.nominal: 05000
> ups.status: OL
>
>
>
> Below the "upsc" command when the UPS is on battery without input (input bad):
>
>
> battery.charge: 100
> battery.current: 0.0
> battery.date: 12292015
> battery.runtime: 00076
> battery.runtime.low: 59940
This seems rather high. This variable is supposed to represent the runtime [in seconds] below which the UPS will signal "LB", but this capture only shows "OB".
> battery.temperature: 00
> battery.voltage: 155.9
> device.mfr: NHS Sistemas de Energia
> device.model: Laser Senoidal 5000VA
> device.type: ups
> driver.name: gamatronic
> driver.parameter.pollinterval: 20
> driver.parameter.port: /dev/ttyACM2
> driver.version: 2.6.3
> driver.version.internal: 0.02
> input.frequency: 0.0
> input.transfer.high: 144
> input.transfer.low: 096
> input.voltage: 0.0
> input.voltage.nominal: 120
> output.current: 0.0
> output.frequency: 60.0
> output.voltage: 119.7
> ups.alarm: Input Bad
> ups.firmware: LSPWM(15).55
> ups.id: ny7bd8723tbecabc
> ups.load: 000
> ups.mfr: NHS Sistemas de Energia
> ups.model: Laser Senoidal 5000VA
> ups.power.nominal: 05000
> ups.status: ALARM OB
>
>
>
>
> I've tested and the shutdown occours when ups.status it's equal OB LB
Thanks for testing.
--
Charles Lepple
clepple at gmail
More information about the Nut-upsdev