[Nut-upsdev] [HCL] NHS Laser Senoidal 5000VA supported by gamatronic
Charles Lepple
clepple at gmail.com
Sat Jan 9 21:41:09 UTC 2016
On Jan 8, 2016, at 7:09 AM, Thiago Wiezbicki - NHS <thiago.wiezbicki at nhs.com.br> wrote:
>
>>> battery.runtime: 00076
>>> battery.runtime.low: 59940
>>
>> This seems rather high. This variable is supposed to represent the runtime [in seconds] below which the UPS will signal "LB", but this capture only shows "OB".
>
> This value is high because we don't have a load in the output of the UPS, therefore, with this load the time until the UPS achieve the low battery status is 59940 seconds.
I admit that the documentation is not clear that battery.runtime.low should be a configuration value, rather than a counter.
However, I am still confused as to why the runtime.low number is larger than runtime (which would be the time until the battery is completely empty, versus just low).
Since this might be hard to work around with the current driver, we can put a note in the DDL, but at this point I don't know what the note should say.
--
Charles Lepple
clepple at gmail