On Wed, 21 Jun 2017, Jim Klimov wrote:

> On June 21, 2017 5:26:47 PM GMT+02:00, Tim Dawson <tadawson at tpcsvc.com> wrote:
>> My thought of #2 require none of that . . . I have a server with two
>> supplies, and two UPS units. One supply is on each UPS, and clients are
>> distributed otherwise to balance. The main thing is to ensure that it
>> is documented accurately how to config so that the server only shuts
>> down when the *second* unit hits low battery . . .  I found the info on
>> this topic almost nonexistent at present . . .

> That example is rather simple and is covered in original NUT docs and/or 
> example config-file comments. Set up two driver sections in ups.conf, 
> and an upsmon with two MONITOR entries powering one PSU each, and a 
> single required power supply. That's about it.

I added a short chapter 3 to cover what I understand is the configuration.
http://rogerprice.org/NUT/ConfigExamples.A5.pdf#section.3

The source material was the User Manual 6.5. Typical setups for big 
servers with UPS redundancy 
http://networkupstools.org/docs/user-manual.chunked/ar01s06.html#BigServers 
and http://www.susaaland.dk/sharedoc/nut-2.0.3/docs/big-servers.txt
but I chose one UPS per server power inlet to avoid any discussion of 
cabling topology.

Roger