[Nut-upsdev] NUT I-D: Minimum command and variable set for conformance
Manuel Wolfshant
wolfy at nobugconsulting.ro
Mon Jan 3 12:06:03 GMT 2022
On 1/3/22 13:47, Roger Price wrote:
> I received a comment calling for a minimum command and variable set to
> be supported for conformance.
>
> The proposal assumes that in the future there will be UPS units which
> natively include an Attachment Daemon and which support direct
> internet access from a Management Daemon. Something like figure 3 in
> section 3 of the I-D:
> https://www.ietf.org/archive/id/draft-rprice-ups-management-protocol-05.html#name-ups-and-attachment-daemon-i
> Such a UPS could claim to be RFC compliant, a marketing advantage, and
> the comment is that such a claim should require that at least a useful
> subset of the commands be implemented.
>
> The comment proposes as the minimum set: « Battery state
> (charging/charged), UPS on main power/UPS on inverter, battery
> percentage of charge left, and killpower (commanding the UPS to turn
> itself off) at the least. »
>
> The idea of a minimum command and variable set seems to me to be an
> interesting idea, but we need to look closely as what is involved.
>
> 1. An Informational RFC cannot lay down conformance standards, but can
> discuss a "Recommended minimum support for commands and variables"
>
> 2. The minimum set is for a consumer grade appliance. Professional use
> requires much more to manage for example unattended servers.
>
> To encourage discussion, I propose the following new subsection 9.4
> Recommended Minimum Support:
>
> 9.4 Recommended Minimum Support
>
> The features provided by current UPS units vary widely. However
> experience
> shows that a minimum feature set is needed for satisfactory use of
> the NUT
> Project software. For a full list of variables see the Recording
> Document
> (7.1).
>
> 9.4.1 Desktop PC Variables
>
> The following variables form a minimum set suitable for Desktop PC.
> It is
> expected that on public power supply failure, the PC will be halted.
> It will
> not restart automatically when power returns.
>
> battery.charge
> battery.charge.low
> device.mfr
> device.model
> ups.status with statuses OL OB LB FSD
>
> 9.4.2 Unattended servers, additional variables
>
> The following additional variables are needed in a minimum set
> suitable for an
> unattended server. It is expected that on public power supply
> failure, the
> server will be halted. It will restart automatically when power
> returns.
>
> battery.date
> device.serial
> ups.delay.shutdown
> ups.delay.start
>
> 9.4.3 All systems
>
> Satisfactory use of the NUT Project software requires support for all
> commands.
>
> All comments welcome. If the list is agreed, I will add the new
> subsection 9.4 "Recommended Minimum Support" to the I-D
>
> Roger
A few comments here
- I have not seen any low- and mid-end UPS that knows about killpower so
not including it as a requirement is a good idea
- The 3KVA Ablerex that I have handy and which powers since ... a long
time ago ( I've replaced 3-4 times the batteries, at least ) a small
size DC does not know about battery.date and since it is connected via a
Serial-to-USB adapter, I am not sure that it knows about device.serial.
It probably does, but in lsusb -v I can only see the USB adapter
wolfy